    If a transformer is taped from an 800A OCPD using the tap rule in article 240.21(B)(3)(1), when does article 240.21(B)(3)(2) apply.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Jun 28, 2011, 08:05 PM

    Okay,

    You need to go back and re-read the code.

    Article 240.21 - Provides for the positioning of the OCPD. Also, it tells you that these conductors cannot feed other conductors without being connected to another OCPD.

    240.21(B) Applies to feeder taps. These taps can be unprotected at their source providing that Sections (B)(1) through (B)(5) are met.

    Section 240.21(B) [feeder taps] (3) [over 25 ft. long] must supply a transformer and comply with sub sections (1) through (5) of 240.21(B)(3).

    So, it is not when to apply condition (for want of a better word) 2 or condition 1. It is a statement that say all of these conditions must apply.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Nec code on duct banks [ 0 Answers ]

NEC article pertaining to underground multiple conduit spacing in a duct bank. Conduit size 2" and smaller

NEC Code Finder [ 3 Answers ]

Greetings, I'm trying to find a book for the NEC class I'm taking. It was only mentioned once, "Finn's Fast Finder(?)" I cannot find it anywhere online. It is supposed to be a NEC Code Reference book that let's you quickly search for code articles and any articles that are referenced or...

Nec code for stapling wires from box [ 2 Answers ]

What is the code for stapling a wire after you staple from the electrical box


View more questions Search