    Heat traps and recirc. Pumps on water heaters
    Just replaced our water heater and have been getting low hot water times at shower heads (plenty of time at sink faucets).

    If I have a recirculating pump, should there be a heat trap in the cold water supply line ? It appears from the piping method in our home that the recirculating pump supply line dumps into the cold water supply line before entering the tank. If a heat trap (our is a new whirlpool gas water heater with a black rubber washer type diaphram heat trap.

    There is no heat trap in the hot water supply side

    Question again is should it be removed if you have a recirc. Pump?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #2

    May 15, 2011, 01:48 PM

    Do you have check valves on the recirculation line and on the cold water input to the water heater line?
    mark patrick's Avatar
    mark patrick Posts: 9, Reputation: 1
    New Member
     
    #3

    May 15, 2011, 06:10 PM
    Quote Originally Posted by hkstroud View Post
    Do you have check valves on the recirculation line and on the cold water input to the water heater line?
    Thanks for the quick reply. Doesn't look like there is a check valve. I do have a gate valve in the line from the pump back into the line that feeds the cold water into the tank, and there is a gate valve between that line junction and the cold water inlet nipple of the tank.

    I did go look at the old tank and there isn't a rubber heat trap (and the metal nipples didn't have a ball bearing type heat trap either) . The replaced tank was over 15 years old so that may explain why.

    I re attached everything the way it was originally except for installing braided stainless steel hot and cold hoses for an easier replacement down the road for myself or the next home owner.

    When hot water is turned on at a faucet or shower head, the pump and its up and down stream supply lines become cold to the touch. I just felt the cold water supply line and it's hot as well. I'm guessing that's normal as hot water is being mixed with the cold back into the tank. That was why I asked about the heat trap. Seems almost like it shouldn't be there in a recirc. Pump set up.

    Sorry if I'm rambling. I'm trying to give an accurate and complete list of all the symptoms. Must be the architect in me.

    Wondering ? Can you download pictures into this forum? That might clear a lot of the confusion.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #4

    May 15, 2011, 06:55 PM

    Yes you can upload pic to this site.

    You need a check valve on the recirculation line just before it connect to the main cold water input line to keep the cold water from going through the recirculation line when you open a faucet. You need a check valve on the main cold water line just before the connection of the recirculation line to prevent hot water from going up the main cold water input line.


    =========================================



    How do I add pictures and other file types to my post?

    A. "Attach" files (including pictures) from your computer. This method puts the attached file below the text of the post.

    Click on an Ask or Answer button to ask or answer a question
    Compose your question or answer in the window.
    Under the window where you composed your question or answer is a section called Additional Options.
    Click on the Manage Attachments button: a pop-up dialog will open. NOTE: The Manage Attachments dialog lists the maximum sizes of the various types of files that may be attached.
    Click the Browse button to navigate to the image on your computer and double click the file on your computer: this will return you to the dialog window.
    Click the Upload button.
    Click the link to close the dialog window OR repeat numbers 5 & 6 to attach another image.

    B. "Embed" image(s) from the internet. This method inserts an image wherever you wish within the text of your post.

    Click the Insert Image icon above the posting window: A pop-up asking for the URL will open.
    Enter the URL of the image in the field then click the
    Attached Images
     
    mark patrick's Avatar
    mark patrick Posts: 9, Reputation: 1
    New Member
     
    #5

    May 15, 2011, 07:30 PM
    Quote Originally Posted by hkstroud View Post
    Yes you can upload pic to this site.

    You need a check valve on the recirculation line just before it connect to the main cold water input line to keep the cold water from going through the recirculation line when you open a faucet. You need a check valve on the main cold water line just before the connection of the recirculation line to prevent hot water from going up the main cold water input line.


    =========================================



    How do I add pictures and other file types to my post?

    A. "Attach" files (including pictures) from your computer. This method puts the attached file below the text of the post.

    Click on an Ask or Answer button to ask or answer a question
    Compose your question or answer in the window.
    Under the window where you composed your question or answer is a section called Additional Options.
    Click on the Manage Attachments button: a pop-up dialog will open. NOTE: The Manage Attachments dialog lists the maximum sizes of the various types of files that may be attached.
    Click the Browse button to navigate to the image on your computer and double click the file on your computer: this will return you to the dialog window.
    Click the Upload button.
    Click the link to close the dialog window OR repeat numbers 5 & 6 to attach another image.

    B. "Embed" image(s) from the internet. This method inserts an image wherever you wish within the text of your post.

    Click the Insert Image icon above the posting window: A pop-up asking for the URL will open.
    Enter the URL of the image in the field then click the
    Thanks Harold,




    So here's the current set up replaced exactly as the original install. The supply line from the pump running to the right connects into the cold water supply. The yellow gate valve handle is blocking the view of the actual connection. The hot supply is the line on the left (closest in the picture) and the cold supply is in the right (background behind the flue riser). The hose bib in the upper right hand corner stops water flow to the water heater.



    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #6

    May 15, 2011, 09:16 PM

    ..
    Attached Images
      
    mark patrick's Avatar
    mark patrick Posts: 9, Reputation: 1
    New Member
     
    #7

    May 16, 2011, 04:56 AM
    Quote Originally Posted by hkstroud View Post
    ..
    Hey Harold. The connection in question is just another gate valve in line before hot water comes back to the recirc. Pump from the loop .
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #8

    May 16, 2011, 05:04 AM

    Then you need a check valve on the recirculation line to prevent cold water from the main supply entering the recirculation line when you open a faucet.

    To verify, close stop valve on recir line and see how long your shower has hot water.
    mark patrick's Avatar
    mark patrick Posts: 9, Reputation: 1
    New Member
     
    #9

    May 16, 2011, 05:47 AM
    Quote Originally Posted by hkstroud View Post
    Then you need a check valve on the recirculation line to prevent cold water from the main supply entering the recirculation line when you open a faucet.

    To verify, close stop valve on recir line and see how long your shower has hot water.
    Thanks Harold,

    I'll try that this evening. Any thoughts or comments about my thought on removing the heat trap from the cold water supply line into the tank?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #10

    May 16, 2011, 06:14 AM

    Don't see what you refer to as heat trap. Is it internal to water heater or is it part of cold water braided supply? Not a factor though, heat traps theoretically stop or reduce heat loss back up piping.
    My opinion, just something to have to periodically have to replace. Certainly don't want one on the hot water out line. Would be totally useless because you are constantly pumping hot water through the line.
    mark patrick's Avatar
    mark patrick Posts: 9, Reputation: 1
    New Member
     
    #11

    May 16, 2011, 07:43 AM
    Quote Originally Posted by hkstroud View Post
    Don't see what you refer to as heat trap. Is it internal to water heater or is it part of cold water braided supply? Not a factor though, heat traps theoretically stop or reduce heat loss back up piping.
    My opinion, just something to have to periodically have to replace. Certainly don't want one on the hot water out line. Would be totally useless because you are constantly pumping hot water through the line.
    The heat trap on this water heater is basically a black rubber washer located between the dip tube and the nipple running into the cold water supply side of the tank. It has a cross shaped slotted penetration to allow water to be forced into the tank, but the slot closes when water isn't being supplied to the tank. Some of these newer heat traps are nipples with a ball bearing that works in a similar fashion.

    Doesn't seem necessary on this tank as we're constantly feeding hot water back into the cold water supply into the tank.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #12

    May 16, 2011, 08:32 AM

    OK, agree but shouldn't hurt any thing. You said you have recirculation pump on timer. Flow will only be when pump is running. Confidant that you will find you have plenty of hot water when you close stop valve on recirculation line. Which will confirm that a check valve is needed on recirculation line. You probably have plenty of hot water when pump is running also.
    mark patrick's Avatar
    mark patrick Posts: 9, Reputation: 1
    New Member
     
    #13

    May 16, 2011, 09:12 AM
    Quote Originally Posted by hkstroud View Post
    OK, agree but shouldn't hurt any thing. You said you have recirculation pump on timer. Flow will only be when pump is running. Confidant that you will find you have plenty of hot water when you close stop valve on recirculation line. Which will confirm that a check valve is needed on recirculation line. You probably have plenty of hot water when pump is running also.
    No that's what's weird. The amount of hot water at the shower wasn't affected by the pump running or not running. It literally runs out after about 5 minutes. The old water heater allowed for pretty long showers 10-20 minutes if you needed the soak.

    What is also weird is that the pump and the lines feeding it get pretty cold once you start running a shower head. Pump running or not.

    Plumbing is a strange animal to me.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #14

    May 16, 2011, 09:47 AM
    That sounds like pump is shot. When you open faucet water flows not only from the water heater but also from the cold water input pipe. Why would pump go at this particular time? Murphy's law.
    mark patrick's Avatar
    mark patrick Posts: 9, Reputation: 1
    New Member
     
    #15

    May 16, 2011, 11:01 AM
    Quote Originally Posted by hkstroud View Post
    That sounds like pump is shot. When you open faucet water flows not only from the water heater but also from the cold water input pipe. Why would pump go at this particular time? Murphy's law.
    Like when you change the anti freeze in a car and the water pump invariably dies at the same time??

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Long time to get hot water w/recirc system [ 12 Answers ]

Hi - we have a recirculating hot water system with a dedicated return to the water heater. The spigots in the master (2 sinks, tub and shower) are taking a LONG time to get hot. The guest bathroom (next furthest) sink gets hot right away, as do other faucets in the house. I'm at a loss to explain...

Water main off, water heater vacation, leave recirc pump on winter? [ 3 Answers ]

Leaving Las Vegas house for 10 days in January - basically want to insure no pipe freeze (many in outside walls) without draining entire house. The house will remain heated to ~55Your Question Title: Please enter your question title with only 85 characters long. Describe Your Question ...

Physical mounting of hot water recirc pump [ 6 Answers ]

I purchased a grundfos recirculation pump for my hot water system and I'm planning the installation. The thing is pretty heavy and there are no attach points to mount the pump itself. I'm installing it on a wall with 16" center studs. With only 1/2" copper spanning the 16" with the pump...

Water Hammering in hot H2O recirc system [ 10 Answers ]

I built this house on a slab 5 yrs ago. Well water to a storage tank to a booster pump to a pressure tank to the house. (2 story) Plumbing was initially laid in slab for Hot H2O recirc. On finish out with hot H2O tank upstairs plumbers installed recirc line to TACO pump T'd into cold side of...

Water htr/heat traps/pipe config. [ 2 Answers ]

Some time back I installed a new water heater and it had the factory installed heat traps. The instructions say you MAY have to install one or more 90° elbows in order to make a “U” configuration in the supply pipes. It also shows the pipes running vertically from the heater. I’ve read on various...


View more questions Search