    The full load current for a three phase AC motor rated at 7.5 hp and using 208 volts
    The full load current for a three phase AC motor rated at 7.5 hp and using 208 volts
    jcaron2's Avatar
    jcaron2 Posts: 986, Reputation: 204
    Senior Member
     
    #2

    Apr 23, 2011, 08:55 PM
    It varies somewhat from motor to motor. It's usually specified on the tag on the motor. I just looked at a 7.5 HP Baldor motor, and it's full load current was spec'ed at 23 amps at 208V. I checked out an Emerson motor, and it's current was 20.6 amps at 208V. That should give you a general idea of the typical current draw of such a motor.
    ibadullah's Avatar
    ibadullah Posts: 12, Reputation: 1
    New Member
     
    #3

    Apr 30, 2011, 07:10 AM
    as u know the formula of power is P=sqt3*V*I
    1hp=746w
    7.5hp=746x7.5
    =5595w
    so 5595=208xI
    and I=5595/208x1.73
    I=15.5A
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    May 1, 2011, 06:26 AM
    While your calculation is correct to arrive at the true wattage of a motor:

    Quote Originally Posted by ibadullah View Post
    as u know the formula of power is P=sqt3*V*I
    1hp=746w
    7.5hp=746x7.5
    =5595w
    so 5595=208xI
    and I=5595/208x1.73
    I=15.5A

    However, a simple "unit conversion" will not take into account the mechanical efficiency, electrical efficiency, or power factor of the motor, and the actual amperage draw will be more that your calculation shows.
    sinnadurai's Avatar
    sinnadurai Posts: 127, Reputation: 2
    Junior Member
     
    #5

    May 1, 2011, 07:22 AM
    Calculations won't give accurate results as amp depends on number of poles or speed of the motor too
    ibadullah's Avatar
    ibadullah Posts: 12, Reputation: 1
    New Member
     
    #6

    May 1, 2011, 11:13 AM
    Comment on tkrussell's post
    Thanku yes I know that calculation is different frm the practical
    weirdwired's Avatar
    weirdwired Posts: 8, Reputation: 1
    New Member
     
    #7

    Jan 6, 2013, 09:30 PM
    Quote Originally Posted by ibadullah View Post
    thanku yes i know that calculation is different frm the practical
    please correct me if I'm wrong,
    if considering the mechanical eff, electrical eff, and power factor of the motor:-

    for example,

    7.5HP = 7.5 x 746
    = 5595W
    this is the mechanical power.

    electrical power = mechanical power / efficiency (if eff. = 0.92)
    = 5595/0.92
    = 6081.52W (at 100%)
    normal run usually 90% max = 6081.52 x 0.9
    = 5473.37W

    current flow at rated load (5595W) = electrical power / PF (if PF = 0.83)
    = 5473.37 / 0.83
    = 6594.42VA

    full-load amp = current flow / (sqt3 x V)
    = 6594.42 / (1.732 x 208)
    = 18.3A
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #8

    Jan 7, 2013, 06:33 AM
    ... another old post...
    Although after all the math wouldn't table 430.250 be just as suitable for most applications?
    sinnadurai's Avatar
    sinnadurai Posts: 127, Reputation: 2
    Junior Member
     
    #9

    Jan 7, 2013, 07:16 AM
    Also it depends on design,design code,code letter,material used,efficiency etc
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #10

    Jan 7, 2013, 08:19 AM
    All I am attempting to point out is that, academically you may be correct...
    But from a construction point of view that level of specificity is usually not required.
    weirdwired's Avatar
    weirdwired Posts: 8, Reputation: 1
    New Member
     
    #11

    Jan 7, 2013, 08:22 PM
    thanks, and I agree with both of you guys.. (sinnadurai & hfcarson). Generally I'm use this simple formula to calculate the amps for three phase.
    amps = kW / (1.732 x 415 x eff. X PF) --> where here normally using 415V system. Eff & PF referring to manufacturer details.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can you operate a light fixture rated for 240 volt, on 208 volt single phase? [ 1 Answers ]

I have an old street light that has a multi tap ballast, the only markings that I can read on the wires are 240volt. My system is 3phase 208 volt and I was told that I could get a 2 pole breaker and the fixture would work. Is this the case?

Difference between 3-phase 208 V and single phase 208 V wiring? [ 2 Answers ]

What's the difference between a single phase and a three phase 208V wiring? Does the first has 2 wire only? Can you also identify the wires as to hot, neutral, and ground? This wiring applies to installing an Air conditioning unit. Thanks.

Is it true that single phase motor takes more current than a 3 phase motor, if so why [ 2 Answers ]

A single phase air conditioner takes 8 amps, while the same with 3 phase takes only 3 amps, the billing is finally for the amps consumed right, so why not only 3 phase.

How am I going to size my 3 phase X'mer with 1 phase load using current as reference [ 3 Answers ]

Hi, I'm Peping: I have 90 pieces of single phase loads with current of 2 Amperes. This will be loaded to a 3 phase transformer, Wye connected having a line to line voltage of 220 Volts. What will be the size of the transformer required for the mentioned loads? Many thanks, Peping


View more questions Search