    Bryant 376c control board self test: blower motor not running?
    Bryant 376C (installed 1990)problem:
    The heat turned on as scheduled after 20 minutes the blower stopped. The inducer motor kept running (thermostat set temp was not reached, no ignition, no gas valve opening.

    Here my attempts to locate the problem:

    I used the self test procedure on the control board with these results:
    - inducer motor starts 10s OK
    - hot surface ignitor 15s OK
    - humidifier relay 10s ? I can hear clicking of a relay

    - blower motor cooling speed: clicking yes, no motor action
    - blower motor heating speed: clicking yes, no motor action

    Next I will measure voltage at the relay connecting to the blower motor.

    My question:
    - is the blower motor dead?
    - is the relay for the blower motor dead?
    - any problems with the control board?
    -... what else am I missing.

    Any help would be greatly appreciated.

    Greetings

    Chris
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #2

    Feb 24, 2011, 07:45 PM
    Do you have 115v on the relay in test mode? If yes you have a bad blower or run capacitor. If no you have a bad control board. New board # CES011057-02. Blower size depends on the BTU of your model.
    jcgolim's Avatar
    jcgolim Posts: 2, Reputation: 1
    New Member
     
    #3

    Feb 24, 2011, 10:11 PM
    Thanks for your feedback.

    I measured the Voltage at the relay output (red/white/black cable connecting to the blower motor, I assume it is a three phase motor?). I checked the voltage "red to white" and "red to black"
    In the test mode it only showed 2V AC (between red and black, L1 and L2 I assume).

    Based on your comments I assume that the control board is bad, is there a way to fix the board? Is the relay bad or does an IC need to be replaced?

    Greetings

    Chris
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #4

    Feb 25, 2011, 05:49 PM
    It's a single phase system. White wire-- common, Black wire-- cooling speed, Red wire-- heating speed. Check for voltage from white to red heating, white to black cooling.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can a Control Board cause a Blower Motor to cease/burn working ? [ 0 Answers ]

My technician went to this house to replace a tstat, once on scene he had trouble with the wiring, he cause the control board to stop working, but when another company arrived to replace the board they discovered that the blower motor has also stopped working, now is this a coincidence or can a...

45692-001 blower control board will not turn blower on in either heat or cooling mode [ 2 Answers ]

Armstrong G1N80 furnace blower control board will not turn on fan at all. Not in heat or cooling mode. I can hear a click when fan should be energized, but no fan startup. Pigtailed the fan hot and neutral,and fan works fine. Is this just a blower control board problem, or something else? We had...

Bryant furnace blower motor running, but not firing [ 3 Answers ]

What should I check to see why my gas furnace is not firing. I replaced the blower motor, which it is working also reset and then wired around the limit switch on the blower housing. Was working and firing furnace producing heat. Within one hour. Then the blower motor comes on, but the...

Bryant 90+ control board relocation [ 2 Answers ]

Hello, I am replacing the control board in my 10 yr old Bryant 350MAV furnace. I was given a kit to relocate the control board "into the blower area" I can't believe I'm suppose to install next to the main blower. Let's face it, even with a regular new filter, it's dirty in there and there is no...


View more questions Search