    How many amps at 208 volt to supply a transformer to create 480 volt 150 amp
    Power requirements using a 112.5 kva transformer
    jcaron2's Avatar
    jcaron2 Posts: 986, Reputation: 204
    Senior Member
     
    #2

    Feb 16, 2011, 05:07 PM

    The total volt-amps are the same on the primary and secondary. If the secondary is at 480V, 150A, that's a total of 72 kVA.

    Therefore, if the primary is at a voltage of 208V, the current must be 72,000/208 or about 350 Amps.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Feb 17, 2011, 03:47 AM
    I will assume this is 3 phase, in which case the calculation is for example;

    480 Volts x 150 Amps x 1.73 = 124,560 VA
    jcaron2's Avatar
    jcaron2 Posts: 986, Reputation: 204
    Senior Member
     
    #4

    Feb 17, 2011, 05:57 AM
    Comment on tkrussell's post
    Good point.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

480 volt stepdown transformer [ 1 Answers ]

I am currently working on a quote that requires me to add a step down transformer (480vac/208vac). I mostly deal with Low Voltage/Dc Power and do not have a clue about sizing the transformer. I am looking for someone who can help me size it correctly. I know that the source/line voltage is 480vac,...

480 volt transformer step down to 120 volt or 230 volt [ 1 Answers ]

AC Axial Fan: run on 120 or 230 input volts / Rated Currect .061 or .053 / Input Power 7 or 6 watts. Supply voltae 480. Need a step down transformer / 480 to 120 or 230 volts.

I have a 24 volt 10 amp water softner- will a 24 volt 20 amp transformer work [ 1 Answers ]

I have a 24 volt water softner and do not have the correct transformer. I found a 24 volt 20 amp door bell transformer. My water softner is a 24 volt 10 amp. Will this work, or will it burn the water softner up? Thanks,

Can you run a 208 volt heating panel on 240 volt electrical supply [ 1 Answers ]

I have a baseboard electric heater that is 208 volts. My power supply is 240 volts. What will happen if I try to run m y 240 volt electrical supply to my 208 volt electric baseboard heater?

480 volt transformer [ 4 Answers ]

Hi there, We are moving into a warehouse that has a 480 volt transformer. The transformer is located on the other side of our office wall. I'm wondering if there's any danger of radiation being so close to it. Thank you.