    Problem with compressor on Goodman SSZ14 Heat Pump
    In April, I had two 3.5 ton Goodman SSZ14 heat pumps installed. From the begenning, periodically the compressor fails to start and the inside circulator only blows room temperature air. The installer and the supplier have been here several times and have done the following: added a hard start to each compressor, replaced a capacitor on each compressor, checked and maybe re-connected the thermostats. The second floor unit seems to be working OK now but the ground floor unit compressor has failed to start twice in the past week.
    When the problem occurs, the inside circulator will come on and begin blowing air but the compressor never kicks in. If I switch the unit off at the thermostat and turn it back on an hour later, everything works correctly. The system may work correctly for a week before the problem happens again. I would appreciate any tips you can offer for my next visit to the installer.
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #2

    Jul 14, 2010, 07:10 PM
    Something's not right. At 3 months old they shouldn`t be needing a hard start . Tell us did they install new line sets (2 copper lines) from condenser to evaporater? Did they install new matching evaporater coils?
    JRayJones's Avatar
    JRayJones Posts: 2, Reputation: 1
    New Member
     
    #3

    Jul 14, 2010, 07:16 PM
    Comment on wmproop's post
    Yes, everything was installed new. The inside circulating unit was matched to the compressor, new line sets installed, pressure checked at compressor several times. Problem has been there since day one.2nd floor unit has worked correctly for a month.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jul 14, 2010, 08:21 PM
    Quote Originally Posted by JRayJones View Post
    In April, I had two 3.5 ton Goodman SSZ14 heat pumps installed. From the begenning, periodically the compressor fails to start and the inside circulator only blows room temperature air. The installer and the supplier have been here several times and have done the following: added a hard start to each compressor, replaced a capacitor on each compressor, checked and maybe re-connected the thermostats. The second floor unit seems to be working OK now but the ground floor unit compressor has failed to start twice in the past week.
    When the problem occurs, the inside circulator will come on and begin blowing air but the compressor never kicks in. If I switch the unit off at the thermostat and turn it back on an hour later, everything works correctly. The system may work correctly for a week before the problem happens again. I would appreciate any tips you can offer for my next visit to the installer.

    Complete service manual for your unit here.

    http://www.hvacpartsshop.com/ssx%20series.pdf


    Have the installer install a Tattle Tale device on the low voltage circuit on the contactor or other control devices in the outside unit. If he or his supplier does not know what the device is then they will need to get an education.

    Available at Johnstone
    NOTE these are ONE time use devices. Cheaper to buy but costly over time since they are one time usage then you can toss them in the garbage can.
    Johnstone part number B12-015 Diversitech TT-24 TT-24 3PK TATTLETALE

    The above is for 24 volt control circuits and will trip to show a low voltage control fault. They are also available in 120 and 240 volt models.


    Another company called Wagner makes a reusable one that is good for voltages from 24 to 460.

    TC007 Wagner TC007 Chek-It Control CheckerCosts more BUT you can use them over and over. I use these in class at the university where I teach Agratis (as in for free).

    A lifetime tool for monitoring and checking safety controls and operating controls.
    One unit for all voltages 24-460 VAC or DC without switching dials or meters. Compact, 4 oz, reliable. Saves troubleshooting.
    For normally closed controls, 007 connects in parallel with safety control. When the safety control opens in response to a problem in the system, 007 red LED turns on and remains on until reset manually.With intermittent problem, the LED remains on indicating the control is open. For operating controls, 007 verifies the status of all types indicating if there is power to the holding coil, the NC contact is open or closed, the thermostat contacts are open or closed, there is power to the contactor or starting holding coil, the overloads are open or closed, or there is a bad connection either on control or power side.

    •Features battery check and reset switch
    •Includes 9-volt battery
    •007 may be used over and over
    •U.S. Pat. No. 4,092,625

    NOTE: Make sure they installed the REAL factory hard start kit. It will have a separate relay and capacitor, Be sized for your specific units compressor, use a real 3 wire hookup NOT a 2 wire hook up like the after market ones. The style units that use 2 wire hookups can be a problem with your units model number.

    Another note: The hard start kit Goodman recommends for your unit is a CSR-U-2. This is made by an old contact of mines company. It is called a 5 2 1 Compressor saver.
    Attached Images
       
    bsharrah's Avatar
    bsharrah Posts: 1, Reputation: 1
    New Member
     
    #5

    Aug 20, 2010, 07:29 PM

    Did you ever determine the cause? I am having the same issue with my Goodman system... also recently installed.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

I have a Goodman Heat Pump (Model: CRKJ30-1AB) compressor won't come on? [ 2 Answers ]

The outside fan comes on and every few minutes the contactor makes a humming sound. The compressor is not coming on. I think that the dual capacitor is working OK. Not sure about the low pressure switch...

Heat pump outdoor fan runs not compressor voltage at compressor good. New compressor [ 1 Answers ]

Have a new compressor. Just replaced fan runs compressor does not, have voltage at the compressor plug? What could stop from coming on high side and low side equal at 100psig.

Goodman cpl t30-1a heat pump, heat not working/no compressor or fan operation [ 5 Answers ]

The thermostat is operating/clicks on when desired temperature is more that the actual, but no action at the compressor or fan. We even switch thermostats from other unit in house and both operate the other unit correctly.

Goodman Heat Pump compressor keeps running [ 1 Answers ]

In Heat mode, compressor outside continues to run even when the blower inside is not running. If I switch the thermostat switch from Heat to off, the compressor stops but sometimes kicks back on, even with the thermostat switch still in the off position. At this point, I have to cut power via the...

Heat Pump compressor fan problem [ 1 Answers ]

I have a Trane XE 1000 heat pump manuf. In 2002. Yesterday, the A/C started having a problem, I checked the units inside and out and found the compressor fan not operating. The outside unit was hot and louder than usual. I turned it off overnight and this morning turned it on to find the fan...


View more questions Search