    Burner lights, but fan won't blow
    Day & Night gas (NG) furnace
    Carrier 800-19A on stamped ID plate
    Forced air

    We just moved in. The furnace has worked just fine several times. We keep the thermostat on the lowest setting, manually cranking it up for those few times that we need heat here in southern California.

    This morning, I turned up the thermostat, heard it click, but the furnace did not turn on. I verified that it 1) had power, and 2) the pilot light was properly lit. After futzing around a bit (I really didn't DO anything), the burners kicked on. GREAT!

    After a couple of minutes, the burners just turned off. The fan/blower never kicked on.

    With the thermostat all the way up, the furnace cycles through the same [incomplete] process. Why won't the blower kick in?

    Thanks.
    cursor's Avatar
    cursor Posts: 3, Reputation: 1
    New Member
     
    #2

    Dec 13, 2006, 11:25 AM
    I tried it again this morning and experienced the same. The blower simply doesn't turn on. What determines exactly when the blower's motor kicks in gear? Might the motor be burned out?

    Correction: The unit is a Carrier 80U-19A, not an 800-19A.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #3

    Dec 13, 2006, 10:52 PM
    There is a blower control located in the furnace. More than likely it is the problem.
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #4

    Dec 14, 2006, 04:21 AM
    If you just bought the house, the seller is obligated to have things like the furnace in operating shape. Call them and let them pay to have a service man. Wouldn't hurt to have the furnace inspected for other defects such as a cracked heat exchanger.

    On older furnaces the blower started after a limit switch heated up. Newer ones it is a timed delay on the circuit board. In either case, the switching is done by a relay when the coil is activated. Yes the blower motor could be burned out. Before replacing it, make sure it doesn't run when it has power to it. It is much cheaper to identify the bad component, and replace it first. Replacing the wrong thing first wastes money and doesn't solve the problem.

    To do simple checks like this you do need some tools. A test light, a meter, or a voltage detector might be the best place to start with. I came across the niftiest gadget for trouble shooting, a voltage detector. They work through the insulation of wires. There are several brands. I have a GB Instruments GVD-505A, less than $15 at Home Depot. Touch it to a hot wire, and the end glows red. Find the doodad that lights it on one side, and not the other, and you have the culprit. You do not have to open up housings and expose electrical contacts. You are looking at where your hand is, not where the meter is. Most people are capable of doing repairs and will get it going and not get hurt if they use a little sense. The voltage detector makes it even easier.
    cursor's Avatar
    cursor Posts: 3, Reputation: 1
    New Member
     
    #5

    Dec 15, 2006, 08:38 AM
    Thanks to both of you for your quality feedback. It looks like we're covered by a formal home warranty program that was part of the purchase deal. I'll be placing a phone call today to see what can be done about fixing the furnace.

    ( = c h e e r s =)

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Hampton bay ceiling fan lights & fan not operating [ 17 Answers ]

Hello, appreciate any help. It just stop working can't honestly say what stop working first or if it happened at the same time. The switch at the wall is working. So I'm assuming it is getting power? I took the bulbs out and disconneted the lower unit by glance everything appears to be fine. I...

Four ceiling fan lights [ 3 Answers ]

Hello. Big dummy here. I took the light fixture down to tighten up the four light fixtures attached thereon and didn't write down the way it was wired up before I unwired it. :o So. Here I sit with four groups of wires, one black and one white for each light, on the lower half and hanging from...

Lights do not work on the ceiling fan [ 3 Answers ]

The fan will come on when using the fan switch, but when I use the light switch the lights will not come on. Is this a wiring problem or a switch problem? I would like to fix it myself if possible. The ceiling fan was put in with lights attached below in 1995 and the lights quit working about 2...

Central ac fan won't blow [ 1 Answers ]

My ac unit in the house works fine, but is no tblowing cold air... I went outside and heard a buzzing/hummimg sound. When I removed the top the fan rotates by hand. I tried reseting my ac circuit breaker but no luck. Do I have a bad fan? Is there something else I can do to troubleshoot? Please...

Ceiling fan and lights go off and on [ 1 Answers ]

I have 2 20 AMP circuits to my bathroom running off same circuit breaker. One circuit powers a ground fault receptacle and vanity lights. Other circuit powers ceiling fan, ceiling fan light, a ground fault receptacle and shower light. This circuit goes on and off but GF or breaker do not kick off....


View more questions Search