    Timer and themostat work fine independently. In combination the GFCI trips.
    Timer and thermostat work fine independently and do not trip the GFCI. In combination the GFCI trips. The GFCI is in main panel and thermostat and timer are in sub-panel near sauna heater. Main panel is about 30 ft away. Neutral is capped off in sub-panel.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Jun 2, 2010, 02:14 PM

    Check the wiring of the GFCI in the main panel. The pigtail is line neutral. It MUST be connected. The load neutral terminal should feed the sub-panel.

    You might have to attach pics using "go advanced/manage attachments".
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #3

    Jun 2, 2010, 02:17 PM

    How long did it work before it started tripping?
    tkirac's Avatar
    tkirac Posts: 7, Reputation: 1
    New Member
     
    #4

    Jun 2, 2010, 02:57 PM

    Approx. 15 minutes.
    BTW, the sub-panel is not a panel. It's a connection box with the thermostat and timer mounted on the face plate.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #5

    Jun 2, 2010, 03:04 PM

    What is the raing of the GFCI and what's the draw of your unit with everything on?
    tkirac's Avatar
    tkirac Posts: 7, Reputation: 1
    New Member
     
    #6

    Jun 2, 2010, 03:47 PM

    GFCI is 30A and the sauna heater is 20A. When wired one at a time it does not trip. Peculiar.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #7

    Jun 2, 2010, 04:03 PM

    Does the faceplate have a ground bond wire? e.g. are the mounted devices grounded via a screw to the device o are they grounded via the panel to box connection?
    tkirac's Avatar
    tkirac Posts: 7, Reputation: 1
    New Member
     
    #8

    Jun 2, 2010, 04:08 PM

    The box and faceplate are solidly grounded via screwed-on ground wire from the main panel.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #9

    Jun 2, 2010, 04:22 PM

    What is the rating of the GFCI
    tkirac's Avatar
    tkirac Posts: 7, Reputation: 1
    New Member
     
    #10

    Jun 2, 2010, 04:36 PM
    30a.
    tkirac's Avatar
    tkirac Posts: 7, Reputation: 1
    New Member
     
    #11

    Jun 3, 2010, 04:03 PM

    Any ideas why when the timer and thermostat are hooked up together the GFCI trips and does not when they are separately hooked up?
    tkirac's Avatar
    tkirac Posts: 7, Reputation: 1
    New Member
     
    #12

    Jun 3, 2010, 04:12 PM

    ??
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #13

    Jun 5, 2010, 04:32 AM

    In a last ditch effort to help, can you?
    1. Post links to instruction manuals for timer and thermostat
    2. Post pics of the inside of both panels

    Taking 15 minutes to trip and work independently have little in common.

    Is one of the devices solid state and the other relay based?

    Going out on a limb have you tried:

    1. Temporarily putting like a 60 W light bulb between the timer and the thermostat?
    2. Temporarily disconnecting the heater entirely and substituting another load for the heater?

    Right now, that's all I can think of.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Gfci breaker trips when I switch it on [ 1 Answers ]

I had to install 3 x GFCI breakers in my panel to bring my kitchen up to code following a kitchen remodel (lucky for me I have 3 separate circuits in my 10x10' kitchen !). Two of the breakers switch on fine and test OK. One of the breakers trips immediately when switched on. I have tested the...

GFCI trips intermitantly [ 8 Answers ]

The GFCI trips intermitantly on my spa. The Blower was unplugged and the GFCI worked. Another Blower was installed and the GFCI trips again. I say the GFCI works and there is still something wrong in the spa. The Dealer says my GFCI is old and needs better noise suppression. They want to replace it...

3-way switch trips GFCI [ 1 Answers ]

All, I installed a GFCI in a bathroom that has 2 outlets, 2 vanity light bars controlled by a pair of 3-way switches, and a shower room with a Nutone fan/heater/light combo. I installed a GFCI in one outlet and when I turn on the lights, the GFCI trips. Both outlets have two cables in them and...

Space heater trips combination AFCI [ 3 Answers ]

I just recently did some rearranging in my home. As part of the rearranging, I put in a dedicated 20 amp circuit for my laser printer that makes the lights flicker if they're on the same circuit. Since it goes into a bedroom, I used an AFCI (my jurisdiction is on the 2002 code still). Home Depot...

Submersible pump trips gfci [ 9 Answers ]

My pond pump has been operating for over a year. Recently it tripped the gfci. I pulled it and took it apart but didn't see anything obvious. I pulled the ground wire and tried the pump and it worked. Anyone have any ideas?


View more questions Search