    Goodman Heater
    We have a Goodman Heater, GMT Series, that recently started to sound like it is struggling to turn on. The LED blinks three times when it is struggling and the panel says that according to the blinking, we should check venter pressure switch or vent blockage. It was eventually starting and would then go solid but the sounds continued. Since then, it has basically stopped. It will try for a while and then give up. Any ideas? Thanks.
    NorthernHeat's Avatar
    NorthernHeat Posts: 1,455, Reputation: 132
    Ultra Member
     
    #2

    Dec 3, 2006, 08:09 AM
    Not sure if GMT is 90 or 80 percent efficient. It can be a bad pressure switch, plugged flue pipes, obstruction in the draft inducer blower motor, water or foreign objust in the vacuum hose or ports. If it is 90%, it can be a plugged drain or trap.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman gas heater doesn't work [ 8 Answers ]

It's been working all right till this morning. I woke up and the room temperature was around 60 :( . All I know about it is that it is a goodman brand furnace. It doesn't have a pilot, but an automatic ignitor. We followed the instruction to reset it -- shut down the electricity, shut down the gas,...

Goodman gas heater [ 9 Answers ]

I have a modelgmpn120-5 gas heater.. today I had gas company look at it.. it runs good for a while.. then shuts down... I go down take a black vacuum hose off.. it has water in it.. I empty it.. heater runs.. today the guy from the gas company said the secodary heat exchanger was bad... how much...

Goodman Heater issue [ 6 Answers ]

Hi I have GMP075-3 model of a Goodman gas furnace. The heater would make the sounds that it was beginning to work. I could see the ignitor light but then nothing else would happen. The repair guy came and said the Burner roll-out limit was somehow tripped the other day. Possibly from a down...

Goodman GMS95 [ 2 Answers ]

Goodman GMS95 Furnace. New and sometimes does not turn on. It is a forced draft, condensing type unit. Trouble shooting light indicates bad pressure switch. Have replaced both pressure switches. When starting to remove top cover unit would start and run fine. What else could be keeping this unit...

Goodman furnace [ 2 Answers ]

My Goodman furnace will light and then go out. This will occur 3 times, then will quit running. The control board blinks 1 time and tells me to Check Gas flow, gas pressure, gas valve, and flame sensor. It seems to have gas going to the valve. Could this be a bad gas valve? Or a bad Flame...