    Mar 27, 2010, 03:20 PM
    Weathermaker 8000 troubleshooting blower
    Weathermaker 8000 control problem with blower - code #33

    The IDM runs, the HSI glows, the GV operates and the burners fire up but then no blower start and eventually the furnace shuts down on overtemp.

    I have run the test sequence and everything operates, even the blower at all speeds. I have checked all switches in the unenergized state and they are OK. I have checked all wiring and cleaned all automotive type connectors.

    Blower will run in self test but will not run if I jumper terminal R to G (continuous run).

    I called a service person and told him all this and he proceeded to change the motor until he realized that was not the problem, then said I needed a new controller for $600 and told me to call him if I wanted to do that.

    Any other ideas before I have to go that route.

    Thanks
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    Mar 27, 2010, 06:09 PM

    Sounds like the heat relay is out of the control board
    glott's Avatar
    glott Posts: 2, Reputation: 1
    New Member
     
    #3

    Mar 27, 2010, 07:41 PM

    Don't see anything on the schematic called a "heat relay" but took the cover off the board and can't see any sign of damage, no components missing and nothing lose. I can hear a relay pick up when I jumper R to G but no blower operation unless it is doing the test sequence.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Need troubleshooting guide to carrier weathermaker 8000 gas furnace [ 0 Answers ]

How do I install the inducer motor assembly in weathermaker 8000 model 58wav gas furnace

Weathermaker 8000 blower trouble. [ 1 Answers ]

I just installed a Weathermaker 8000 in my camp after converting it from natural to propane. It seems to start up fine, but the blower runs continuously-weather burners are ignited or not. Any insight to this would be greatly appreciated. Tim

Weathermaker 8000 keeps running [ 1 Answers ]

I have a weathermaker 8000 furnace and the fan motor runs constantly even when the heating cycle is done. I do not have a/c installed and I cannot locate a fan only switch. Is this normal for this unit?

Weathermaker 8000 blower not working [ 5 Answers ]

I have a Carrier Weathermaker 8000 two speed system. I went away for 4 days this week and left central air on as usual but, I also left my blower running to circulate air while I was gone. When I returned home my central air unit was froze up, which happens occasionally but also my blower was not...

Code 31 on weathermaker 8000 [ 3 Answers ]

I have a weathermaker 8000 58wav. It will startup, induction fan on, flames on, blower on for about 80 seconds. It then shuts down the flame and the induction motor. The blower will run for a short time and off. Blinks 31. Pressure switch was Ok, Flame sensor seems Ok. I checked the chimney vent...


View more questions Search