    twd1's Avatar
    twd1 Posts: 1, Reputation: 1
    New Member
     
    #1

    Mar 23, 2010, 08:32 AM
    Can hook up a 110v gfi breaker of one leg ogf a 220v 50 gfi
    I have a 50 amp 220 v gfi hooked up to my hot tub, I ran a 110 v 10 amp gfi off one leg for the underwater light just for extra safety, is this safe to do? I have heard on TV that you can not run 1 gfi off another. Or is this just pertaining ti wall outlets?
    manhattan42's Avatar
    manhattan42 Posts: 143, Reputation: 11
    Junior Member
     
    #2

    Mar 24, 2010, 02:13 AM

    Unless the hot tub is listed to be wired in the manner you describe, then what you did is a violation of the manufacturer's installation instructions and therefore a Code violation.

    Generally speaking, hot tubs and their associated equipment are already configured at the factory to be run from a single branch circuit conductor termination point.

    Altering the internal wiring past that conductor termination point as you have done will not only void any warranties, it can be quite dangerous.

    As for the GFCI question, the answer is that you should not run multiple GFCIs in a series under any circumstance.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Mar 24, 2010, 04:38 PM
    Quote Originally Posted by twd1 View Post
    I have a 50 amp 220 v gfi hooked up to my hot tub, I ran a 110 v 10 amp gfi off one leg for the underwater light just for extra safety, is this safe to do? I have heard on tv that you can not run 1 gfi off another. or is this just pertaining ti wall outlets?
    What you did was completely unnecessary, and I question how it was done. Something does not sound right to me.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Mar 24, 2010, 04:39 PM
    Quote Originally Posted by manhattan42 View Post

    As for the GFCI question, the answer is that you should not run multiple GFCIs in a series under any circumstance.
    This is not actually true. There is nothing wrong with this other than redundancy.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bathroom GFI outlet trips breaker at breaker panel [ 2 Answers ]

Hello all. Our house is approximately 13 years old. Each morning when both the iron and blow dryer is plugged into two separate GFI outlets in the master bathroom, the circuit will trip the 15 amp breaker in the breaker panel. Is it possible to upgrade the breaker to a 20 amp without...

How do I run a 220v outlet from two 110v breaker switches? [ 4 Answers ]

I am a handy man but have never really messed with much electrical wiring. I need to run a 220 volt outlet to run a window unit AC. How would I go about using two existing 110 volt switches from my breaker to run a 220 volt outlet? I was told it can be done that way and it would save me from having...

Outlets on my GFI don't work but GFI is working [ 7 Answers ]

I have one plug in the garage and one out door plug that are not working. I have reset my GFI plug and the GFI plug is working however the other two plugs are still not working. Should I replace both plugs or is there something else going on? The GFI outlet itself has power. The test and reset...

OK to replace a 20A GFI with a 15A GFI? [ 1 Answers ]

I have two GFI outlets in my kitchen. I am replacing them w/another color. The new color are only available in 15A, while the ones I am replacing are 20A. The only thing I plug into them are toasters, coffee pots, and mixers... not sure if the lower amp has anything to do with the ground fault...

Replacing a circuit breaker with a GFI breaker- q on neutrals [ 1 Answers ]

In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!


View more questions Search