    Why is a ground wire clipped onto metal box
    I am updating my electrical outlets and switches. I noticed on many of the metal boxes there is always a ground wire clipped to the box but also one connected to the fixture. What is the purpose of the one clipped to the box? Is it necessary? A clip was broken so I removed the wire for now and am wondering if I need to get the proper equipment to repair.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Mar 21, 2010, 08:20 PM

    Insulation breakdown can energize the box. The clips help detect insulation and/or component breakdown. A hot wire that say accidentally slips out of a wirenut would touch the side of the box will blow a fuse rather than energise the fixture. You should be able to see this effect better with a light fixture.

    Suppose the box wasn't grounded and the hot touched the side of the box. The unsuspecting person would try to change a light bulb and get shocked.

    The grounding is also part of the equipotential system in the house. It will assure that plumbing fixtures, electrical fixtures and appliances are at the same voltage to one another.

    The clips are readily available. Installation can be a pain, but is typically done with a screwdriver. I install them by hitting the end of a screwdriver on the clip.

    It's difficult to guarantee that the ground on the outlet will provide a good connection to the box, hence the box must be done separately.
    forsoother's Avatar
    forsoother Posts: 11, Reputation: 1
    New Member
     
    #3

    Mar 21, 2010, 08:26 PM

    It is to protect your safety when electric circuit has short current or wire broken. The grounding line will earthing your metal box, then circuit breaker will jump to secure your safety.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

3 wire plus metal conduit as a ground for a range [ 4 Answers ]

I am installing a new range. I have a three wires coming out of a metal conduit which is properly connected to a 60 amp breaker. I have a three wire cord and a grounded surface mounted outlet. I assume that the ground will connect through the metal conduit. THis will ground the outlet. How do I...

Can I use a ground wire for a ground and live black or hot wire at the same time? [ 8 Answers ]

I only have 3 wires from my ceiling to connect to my fan/light, the black, white and bare ground. No problems setting up in this room to only one switch but I would like to have the duel fan/light switch in like in my other rooms without having to pull a wire from the ceiling down to the switch,...

How do you wire a single switch (1 black 1 white 1 ground) to a 5 wire hunter remote? [ 1 Answers ]

I have an existing ceiling fan operated off a single switch (1-black, 1-white, and ground). I am trying to install a hunter ceiling fan remote (model 27157) with 5 wires (1-black/white, 1-red, 1 black, and 2-white commons). I have tried several combinations of wiring, including the recommended...

Nec-covering of ground wire from the ground rod to the water pipecables [ 1 Answers ]

I installed a new service meter panel and ground rod. The ground rod is connected to the meter panel via a #4 copper wire to a water pipe located 10 feet away. Is is allowable to bury the #4 wire between the ground rod and water pipe to keep it from being a trip hazard and protect the wire? ...

Can you use Metal Conduit as ground to convert 2 wire to 3 wire? [ 3 Answers ]

I need to convert an old cinder block house from 2 wire outlets to 3 wire by adding a ground to all outlets. Since the entire house is cinder block, all the circuits from the basement breaker box are in flexible metal conduit and metal outlet boxes... Is it possible to use the metal conduit...


View more questions Search