    Electric heat in the basement
    I will start with a simple(I hope) question:

    I would like auxiliary heat in some basement rooms downstairs we are finishing.

    I am considering flush-mounted (in the wall cavity) fan driven (as opposed to convection or radiant) wall heaters, probably 1000W per room.

    All else being equal, is there a reason to choose 208V or 120V? Of course, before buying and installing I would consult with an electrician to make sure my choice is viable.

    Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 29, 2006, 01:35 PM
    Using a higher voltage will allow more load on a circuit, using small wire.

    I am curious why you mention 208 volts, and not 240. You certainly may have 208 volts if your home is a part of a large apartment or condo building. If it is a single family home the supply volts should be 240 volts.

    A 120 volt 20 amp circuit with #12 wire can handle 1920 watts.
    A 240 volt 20 amp circuit with #12 wire can handle 3840 watts.

    Same wire size at a higher voltage can handle more watts of load.

    FYI, we always derated all circuits by 80%, so this is why you see some odd wattages allowed. Or increase the circuit size by 125%, which is same ratio, but works better if we derate the standard fuse or circuit breaker rating.

    Oh, another FYI, if you are part of a multi-dwelling building, you probably are not allowed to do your own electrical work, only if a single family home, check with your local code enforcement office.
    pwd77's Avatar
    pwd77 Posts: 186, Reputation: 3
    Junior Member
     
    #3

    Nov 29, 2006, 04:26 PM
    Thanks for the response.

    In my case I will be running new wire, so have no limitation there. I was just curious if there were any other factors to consider.

    [yes it is a single detached home, so the voltage should be 240, not 208. I had been reading an old thread in which the issue was 120 vs. 208 in a condo complex.]

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electric Heat-Pump-No heat [ 2 Answers ]

I had a wall-mounted unit installed in a room in may of this summer. In the middle of the night the heat shut off and has not come back on since. It is an Amana, electric heat with heat pump unit. The cooling works, the heating setting does not blow air at all. When I remove the cover it says...

Changing from gas heat to electric heat [ 3 Answers ]

How do you change from Apollo gas heating system to electric heating system?

Alternatives to electric heat? [ 8 Answers ]

I am house searching and I've found the perfect property. *But* there is electric heat. I am in Massachusetts, and our heating season is just much too long to go through several months on electric heat($$) I was wondering... what do I do? I am interested in a corn stove, but I worry if we ever...

Electric heat [ 6 Answers ]

I recently moved to a home with electric heat. I am not familiar with it. Is the air from the registers suppose to be more cool than warm, it is not cold but cool Debbi

Baseboard electric heat [ 1 Answers ]

Does anyone have any recommendations for brands/style of baseboard heaters? Have looked at hydrosil, they claim to be efficient but are higher priced units. Are the fluid/gel filled units that much more efficient than the cheaper units? Thanks


View more questions Search