    Finding root cause for Leaking Pressure Relief Valve
    Hi folks,

    Reading this forum has helped to explain that in many cases a leaking Watts brand PRV rated at 150psi is "just a symptom." I need your help in finding the root cause for the leak.

    I have 2 50 Gal Water heaters installed in Parallel in my garage(as I can turn off cold inlet on one heater, and still get hot water-turning off both inlets shuts down Hot water flow).

    On one of the 2 year old tanks the Pressure Relief Valve (PRV) is leaking now, which was replaced a year ago due to similar issue. Shutting the cold inlet and throwing PRV to release several times doesn't help.

    My own gauge says Water pressure is between 90-110psi range when heater is idle/fireing. Seems high to me. A year ago the city cked it and said pressure was normal, but I cannot remember the PSI then.

    I'm pretty sure I have a backflow preventer at the street meter as the neighborhood is only 10 yrs old, and confirm I have no expansion tank, nor a Water Pressure regulator (unless city installed it at the street)

    Since this is the 2nd PRV on with the leakage on the same 2 yr old heater, I'm thinking the root cause is excessive water pressure.

    So, my questions are... In order to verify the root cause, (since the PRV is just a symptom),
    1. should I have a plumber ensure there is a water pressure regulator is installed first at the street, and verify "normal" pressure at about 70psi, before I walk down the Thermal expansion tank route inside the house?

    2. OR Should I install a expans tank, and a new PRV.. or do #1 and #2-seems extreme.

    2a. If you think I should install a expansion tank, should I install 2 of them, one per water heater inlet or just a single exp tank on one of the heaters inlet?

    Thanks in advance,

    Steel
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #2

    Mar 4, 2010, 12:38 PM

    I'm pretty sure I have a backflow preventer at the street meter as the neighborhood is only 10 yrs old, and confirm I have no expansion tank,
    If you have a backflow preventer installed and no expansion tank installed to cushion the pressure spike then you have found your problem. Iinstall a expension tank and watch your leak go bye-bye.
    Good luck, Tom
    Steelgate's Avatar
    Steelgate Posts: 5, Reputation: 1
    New Member
     
    #3

    Mar 4, 2010, 12:56 PM

    Do you think a Pressure regulator is needed in addition to the Expansion tank?

    Should I get one or two expansion tanks for 2 50 gal heaters?
    speedball1's Avatar
    speedball1 Posts: 29,301, Reputation: 1939
    Eternal Plumber
     
    #4

    Mar 4, 2010, 01:18 PM
    Quote Originally Posted by ;
    My own gauge says Water pressure is between 90-110psi range
    The average house pressure runs about 45 PSwith a top PSI of 80.
    I would first install the PRV, and it installs inside your house where the service enters. It's the backflow preventer that installs next to the meter.
    Should I get one or two expansion tanks for 2 50 gal heaters?
    When you r pressure spikes it affects the system. One tank on a cold water feed should do very nicely but bringing down the house PSI with a PRV may just solve that problem. Install the PRV first and watch the T & P valve. If it still leaks then install the expansion tank. Good luck, Tom
    Steelgate's Avatar
    Steelgate Posts: 5, Reputation: 1
    New Member
     
    #5

    Mar 9, 2010, 05:12 PM

    OK, I will be replacing the Pressure Reducing Valve first... since I found I have no valve between me and the street.

    Is there a difference in quality with PRVs? I'm looking at the Honeywell cartridge type, Honeywell DS05G1085 PRV for about $100, which has a plastic bonnet. Would a plain old cast WATTS be better or same?

    Thanks,

    Steel
    Steelgate's Avatar
    Steelgate Posts: 5, Reputation: 1
    New Member
     
    #6

    Mar 9, 2010, 05:18 PM

    Here is the guy:
    Product

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Surging water pressure & leaking water heater relief valve [ 19 Answers ]

Just recently the pressure of our water in the house surges when we turn a faucet on, and the city water company verified that our pressure in the house when we open a faucet is higher than the pressure in the lines in the street, and after the water runs is at a normal pressure (meaning their...

Cold water pressure relief valve leaking [ 6 Answers ]

My pressure relief valve is leaking. This is a very small amount of water dripping to the outside of the house. Next to replacing the valve is there anyway to stop the leak. This valve is within 2 feet of the pressure regulator where the water comes into the crawl space.

Leaking pressure relief valve on h/w tank [ 4 Answers ]

The pressure relief valve keeps leaking. The h/w tank is about 9 months old. The problem started when the main line broke. The township had to turn my water off and when they fixed it and turned the water back on is when it started. Any help towards a solution is always appreciated. :)

Leaking from relief valve [ 9 Answers ]

I have a Well-Troll system, I just replaced the 75psi relief valve on the output of my tank. And it still leaks it seams that when I use water the pump (submersible) kicks on and pops the relief (spilling 3 or 4 gallons) nothing was changed or tampered with except the changing of the relief valve....

Gas Hot Water Heater Pressure Relief Valve Leaking [ 6 Answers ]

Should the pressure relief valve on my natural gas hot water heater leak out of the pressure relief valve every time the burner comes on to heat the water? It has been doing this for several months and my builder said his plumber told him it is normal.:confused: Also the temperature just...


View more questions Search