    New Construction
    My mother in-law is building a house in Mexico. I already did the wiring in the house and we have to run the service feeds from the meter 150' away. We have a 200 amp panel and I am going to run it underground on a 2" conduit and are going to use 4/0 aluminum. My question is do I need a breaker @ the meter and @the panel? There is no way to put a breaker in the meter box so I have to put it on a junction panel of some sort. Any suggestions on the best way to do this?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 26, 2006, 07:47 AM
    Depends on the local codes, but usually a breaker is installed at the meter which will then protect the underground cable from short circuits. There are 200 amp meters socket enclousures that contain a 200 breaker all in one cabinet.

    If the meter socket is already installed, a 200 amp breaker can be added in a raintite circuit breaker enclosure made for that breaker. Or a raintite fusible 200 amp disconnect switch can be used.

    Once a main breaker is located at the meter, a breaker in or at the panel is not necessary. One can be used, does no harm, but is not needed.
    mrl8zyboy's Avatar
    mrl8zyboy Posts: 5, Reputation: 1
    New Member
     
    #3

    Nov 26, 2006, 11:41 AM
    Quote Originally Posted by tkrussell
    Depends on the local codes, but usually a breaker is installed at the meter which will then protect the underground cable from short circuits. There are 200 amp meters socket enclousures that contain a 200 breaker all in one cabinet.

    If the meter socket is already installed, a 200 amp breaker can be added in a raintite circuit breaker enclosure made for that breaker. Or a raintite fusible 200 amp disconnect switch can be used.

    Once a main breaker is located at the meter, a breaker in or at the panel is not necessary. One can be used, does no harm, but is not needed.

    So I can add two 100A breakers to the meter. Where does the ground rod have to be? Can I put it were the panel is instead of were the meter is?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Nov 26, 2006, 12:29 PM
    Yes at the load side of the meter you can then feed two 100 amp breakers, in Raintite enclosures, to feed two 100 amp panels, if you like.

    The grounding always begins at the Main Disconnect, so the ground rod, or rods, will connect to the neutral lug at the main. This is where the neutral, or grounded conductor, is grounded, by the grounding conductor, which is the wire that connects to the ground rod(s).
    mrl8zyboy's Avatar
    mrl8zyboy Posts: 5, Reputation: 1
    New Member
     
    #5

    Nov 26, 2006, 02:59 PM
    Quote Originally Posted by tkrussell
    Yes at the load side of the meter you can then feed two 100 amp breakers, in Raintite enclosures, to feed two 100 amp panels, if you like.

    The grounding always begins at the Main Disconnect, so the ground rod, or rods, will connect to the neutral lug at the main. This is where the neutral, or grounded conductor, is grounded, by the grounding conductor, which is the wire that connects to the ground rod(s).


    Do I need to run a separate a ground besides the 2 hot's and the neutral to the 200A panel?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Nov 26, 2006, 03:31 PM
    Yes, an equipment ground, either green insulated or a bare does need to go from the Main Disconnect to the panel, along with the two hot and one neutral feeder conductors.

    This will connect to the Main Neutral at the Main Disconect, along with the grounding conductor coming from the rods. At the panel, the neutral will connect to the insulated Neutral bar in the panel, and the equipment ground will connect to the equipment ground bar that will be bolted directly to the panel backbox.
    mrl8zyboy's Avatar
    mrl8zyboy Posts: 5, Reputation: 1
    New Member
     
    #7

    Nov 26, 2006, 03:50 PM
    Quote Originally Posted by tkrussell
    Yes, an equipment ground, either green insulated or a bare does need to go from the Main Disconnect to the panel, along with the two hot and one neutral feeder conductors.

    This will connect to the Main Neutral at the Main Disconect, along with the grounding conductor coming from the rods. At the panel, the neutral will connect to the insulated Neutral bar in the panel, and the equipment ground will connect to the equipment ground bar that will be bolted directly to the panel backbox.


    What size ground do you recommend? What size conduit do you recommend for the 2 hot's,neutral and the ground? I will be using 4/0 aluminum for hot's and neutral. Thanks,
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #8

    Nov 26, 2006, 04:01 PM
    For a 200 amp circuit either a #4 copper or a #2 aluminum. For a 150 foot run,I would use either 2.5" or 3" PVC, to make the wire pull easier.
    mrl8zyboy's Avatar
    mrl8zyboy Posts: 5, Reputation: 1
    New Member
     
    #9

    Nov 26, 2006, 05:13 PM
    Quote Originally Posted by tkrussell
    For a 200 amp circuit either a #4 copper or a #2 aluminum. for a 150 foot run,I would use either 2.5" or 3" PVC, to make the wire pull easier.

    Thanks for the info you've been really helpful.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

OSB used in construction [ 8 Answers ]

Can I use this type of board for walls and roof and floors for my shed if I intend to cover the exterior in sheetmetal?. if so, should I paint all of the OS.. just in case it rains while I'm building?. this is going to be a 1 man job so its going to take me awhile.. thanks for any help

Cladogram construction [ 1 Answers ]

Kindly guide me to the process of cladogram construction through an appropriate software avalilable on line. I am using morphological data for such analysis and could not find any suitable software. Your immediate help will be highly appreciated. Thank you

New construction [ 1 Answers ]

We are building a new townhouse in Virginia. Would you recommend copper or pvc piping throughout the home and why. Thank you...

New construction [ 3 Answers ]

I plan to have a house built, and circumstances (financial and otherwise) Necessitate that I assume some of the construction chores such as plumbing, Electrical, floor plan design, and contracting. I'm probably way over my Head on the plumbing task because I've had very little experience. The...

Construction [ 1 Answers ]

How much does it cost to build a parliament in a developing country?


View more questions Search