    What is the wire size for a 30amp circuit at 200 feet?
    I am trying to install a 30amp sub-panel out to my barn from the house. The wire run is approximately 200 feet including the internal wire distance in both buildings. What wire size do I need to use? Will 8/3 with ground be sufficient?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Feb 17, 2010, 05:08 AM

    #4 copper will be needed to deliver 30 amps 120 volts 200 feet.
    danarh's Avatar
    danarh Posts: 2, Reputation: 1
    New Member
     
    #3

    Feb 17, 2010, 05:33 AM

    My oversight... sorry. 30 amps 240V at 200 feet. What is the required wire size?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Feb 17, 2010, 05:45 AM
    #6

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What is the wire size for a 30 amp at 50 feet [ 1 Answers ]

What is the wire size for a 30 amp wire at 50 feet long

Wire size wire & circuit breaker do I need for a 15.8 range [ 2 Answers ]

What size circuit breaker & wire size do I need rfor a 15.8 raqnge ?

Wire size for a 100 amp sub panel 200 feet away [ 8 Answers ]

I have a 200 amp main panel in my house and I just built a garage and am planning on putting a 100 amp sub panel in the garage. The garage is about 200 feet from my house and it has a 2 inch pvc stubbed out underground. I am wondering what size aluminum I would need to feed it, and if I can use a...

Gauge of Wire From Meter to house,100 amp fuses,200 feet run. [ 2 Answers ]

Hello, I am intending to replace some wire that runs for 200 feet, from my meter to my house.I live on an island, so the run is quite long ! At either end are breaker boxes with 100 amp fuses in each.Never had any trouble/ fuse blows etc. The old wire (each of the 3 strands) are a little...


View more questions Search