Ask Experts Questions for FREE Help !
Ask
    mrdan3000's Avatar
    mrdan3000 Posts: 3, Reputation: 1
    New Member
     
    #1

    Jan 31, 2010, 01:30 PM
    Trane XB LED blinks 5 times and blower won't stop running, but no heat.
    Problem: Trane XB LED blinks 5 times and blower won't stop running, but no heat.

    Any ideas what the solution is? I am thinking some kind of fan control board. I can shut off power to the whole unit, but when I power back on I get the same problem. Blower runs with no heat. The thermostat can be set to "heat" or "off" but the blower still runs. The blower is in "auto." I tried resetting the ICM, but it did not fix it. This unit is only a few years old - maybe 2006. Please help! It's cold outside!
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 31, 2010, 04:35 PM
    Look on the back side of the blower access door and post the answer to your 5 blink code. Then post the complete EXACT model number of your unit.
    mrdan3000's Avatar
    mrdan3000 Posts: 3, Reputation: 1
    New Member
     
    #3

    Jan 31, 2010, 05:30 PM
    Model: tuc1b060a9361ab

    Error: flame sensed when no flame should be present

    There is definitely no flame present. I reset the unit and the blower immediately comes on even though I turn it off at the thermostat (blower is set to auto). I inspected the flame sensor but it visually looks OK.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #4

    Jan 31, 2010, 05:41 PM

    OK, I've seen this code written on many diagnostic charts, but have never actually seen the coded blinked out on the control board. Im hoping hvac1000 can shed a little lite on this situation, as I've wondered what I would do if I came across it. The way I see it, this code would come in when the gas valve stuck open. But more likely your board has malfunctioned. I was thinking you had a tripped high limit, or rollout, but the flame sensed when no flame should be present is throwing me off. Can you clear this up for us hvac1000.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Jan 31, 2010, 06:14 PM
    As per the factory (If all other components check out as OK then replace the circuit board).

    Both Trane and there sister American Standard/others have this programed into there boards. It is somewhat of a catch all code. If something fails and the board cannot figure it out it dumps it on 5.

    Now remember the magic words (If all other components check out). Make sure that all limits are reset or PROVEN good along with all other components. Check for the famous polarity problem also. In other words pull all the tricks out of the bag then if all is OK replace the circuit board.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #6

    Jan 31, 2010, 06:27 PM

    Hear you loud and clear. Thanks again. Never have been a big fan of replacing the board unless I can prove (beyond a reasonable doubt) that the board is the culprit. Can't always rely on the diagnostic code, that I've learned the hard way.
    I really appreciate your feedback hvac1000.

    PS. Nothing tickles me more than going on a furnace call, the homeowner tells me that he just replaced the board, but furnace still doenst work. Then I clean a flame senser, or clear a blockage in a vent,or condensate drain line, or etc etc etc. Always nice to see the look on the homeowners face after such an easy fix(for someone that nows what to look for and how to test the system correctly) Then they say, so I just waisted 100 bucks(or much more) on a board. And all I can say is, yep, but at least you have a spare board if the need ever arises, oh you threw it away and the garbage man came this morning, oh, I'm really sorry to hear that. Here's my card, I'm betting it will save you money in the long run. Have a nice day.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Jan 31, 2010, 07:34 PM
    That is a good way to do the biz. My guys would get fired if they ever berated a customer in person and I found out about it. Now in the shop the next morning there were always good customer tails from the day before and some were so funny they bordered on the insane.

    I can never blame a customer for trying to save some $$$ but most of the time they end up spending more than if they would just allow the pro to fix it to start with. It is like the thermostat tail which is true. As in all areas we have subdivisions where all houses are about the same and all furnaces etc are the same. One year a service Tec from my office had to install a new thermostat for a customer in one of the subdivisions. Now we all know that a thermostat that has been working all along is usually the last item you would ever replace since the dag gone thing last forever but this one needed to be replaced. Over the winter we had quite a few calls at different homes in the same subdivision and when our service Tec got there the first thing they were told is that the thermostat was replaced by the husband but the furnace still would not work. This led to the famous question of that year (Why did you replace the thermostat Mam. Our guys were instructed to use yes Mam and no Mam to be polite) and the answer was always Susie, Mary, and all the rest of the neighbors replace there thermostat whenever the furnace breaks since that is how Alice Johnson's husband fixed theirs. Rumors like this abound on the net and also in person to person communication and as we see every day all it does is cost the customer more money in the long run. I miss those stories at 6:30 AM contractor time every work day.
    Attached Images
     
    mrdan3000's Avatar
    mrdan3000 Posts: 3, Reputation: 1
    New Member
     
    #8

    Feb 1, 2010, 12:09 PM
    I replaced the board. Problem solved! Thanks for your advice.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #9

    Feb 1, 2010, 01:25 PM
    Glad you got it going.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

AC / Heat Pump inside blower fan will not stop running [ 2 Answers ]

I have a Trane XE 1000 Heat Pump the inside furnace blower fan runs non-stop. Even when you turn the thermostate to off. I replaced the thermostate with a new digital honeywell non-programable thermostate this did not fix the issue. Can someone tell me what my problem is, what I need to do to...

Goodman GMS91155DXA LED blinks 3 times [ 6 Answers ]

First a bit of history: The furnace is almost 2 years old and worked all of last winter without any problems. Based on the information in the manual and some things I gleaned online, I replaced the pressure switch. Worked great ran all of last night and then starting this morning I get the same...

Trane xr 90 led flashing 3 times [ 1 Answers ]

The LED light on my Trane XR 90 is flashing 3 times, do you know what that indicates?

Furnace do not truns on LED blinks three times [ 1 Answers ]

I have Goodman Furnace model GMT 090- 3B installed 3 years ago and it gives me constant problem I just changed Hot surface ignitor last week and it was working good and it again stop working and when I open the cover of furnace I can see there is a red LED light that blinks three times and stops...

Why does the furnace not work and LED blinks three times [ 2 Answers ]

Why does the furnace not work suddenly after one year and the LED blinks three times


View more questions Search