    tt1164's Avatar
    tt1164 Posts: 4, Reputation: 1
    New Member
     
    #1

    Dec 4, 2009, 11:08 PM
    Pilot light on our Lennox G40UH(X) Series furnace won't light
    The pilot light on our Lennox G40UH(X) Series furnace won't light. We went through the steps to restart the furance. The blower turns on for a few minutes but blows cold air and the pilot light never comes on. How can I fix this?
    tt1164's Avatar
    tt1164 Posts: 4, Reputation: 1
    New Member
     
    #2

    Dec 4, 2009, 11:11 PM

    The LED lights are indicating that the primary or secondary limit switch is open (per the manual). The manual says that the limit must close within three minutes or the unit goes into a one hour watchguard. How do we correct this?
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #3

    Dec 5, 2009, 05:35 AM
    Check/replace air filter if clogged. Locate the limit devices, press/reset any with buttons. If the primary limit is stuck open, tapping the fiber plate with the butt of a screwdriver may cause it to reset.
    Attached Images
       
    tt1164's Avatar
    tt1164 Posts: 4, Reputation: 1
    New Member
     
    #4

    Dec 5, 2009, 11:51 AM
    Is it possible that one of the limit switches is bad? At first I thought that maybe we just needed to reset something but nothing seems to be working.

    When we flipped what we thought was the limit switch it gave another error about the roll out switch being open. So what we thought was the limit switch was apparently the roll out. We can't find anything else that looks like it could be the limit switch.

    I don't understand why they don't make user manuals that actually show real picutres of the system and where components are located.

    Thank you so much for your help!
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #5

    Dec 5, 2009, 01:02 PM

    Roll-out switches are typically near the main burners, and resemble the previous pics.
    tt1164's Avatar
    tt1164 Posts: 4, Reputation: 1
    New Member
     
    #6

    Dec 5, 2009, 01:20 PM

    After much googling I have finally determined where the primary limit switch is. I guess it is a flat metal plate with two wire attached to it. I saw someone post another question on another forum with the exact same problems we are experiencing and the responders suggested that the primary limit switch is stuck open and that tapping it might close it.

    We tried the restart sequence again and tapped the primary limit switch during the three minute reset period and the burners FINALLY ignited. Our furnace is working again!

    I just thought I would post this in case anybody else experiences a similar problem.
    GB1234's Avatar
    GB1234 Posts: 1, Reputation: 1
    New Member
     
    #7

    Dec 17, 2009, 09:01 PM
    Wholy Cow... this works. We found this post, tapped on the primary limit switch and the furnace started up again. So simple. Glad we didn't have to pay to get the HVAC guy out here for an emergency visit!

    Just a note... the primary limit switch on our G40UH is a red metal plate that is on vertical surface. It also has two wires coming out of it.
    furnacefixed's Avatar
    furnacefixed Posts: 1, Reputation: 1
    New Member
     
    #8

    Dec 25, 2009, 10:19 AM
    I had the same problem just now when I came back from X-mas with the in-laws. I needed a hot house and used your suggestions. It failed the first time, but then after tinkering with it, it worked for me. THANKS

    The info about the primary/secondary switches was great. I actually unscrewed the red metal plate, pulled the plate out, and tapped/cleaned the dime sized (in diameter; about the thickness of 3 dimes) metal part when just the tapping did not work. I took apart the wires and rehooked them too for a clean/fresh connection. After cleaning the dime sized object I noticed 2 more dime sized objects with others wires leading to them as well. I unscrewed, tapped, and cleaned those as well. All the wires from these 2 similar looking dime sized objects were leading to the main gas switch that I was promted to turn to off before beginning based on the user manual.

    Everything fired up nicely afterwards. The posting on the "red metal plate connected vertically" really helped me locate where the switch was. It's too bad the owner's manual does not go into more detail about this.

    Thanks for the internet as well! It's nice to find out information and do it yourself!
    webjxu123's Avatar
    webjxu123 Posts: 1, Reputation: 1
    New Member
     
    #9

    Jan 4, 2010, 07:55 PM
    I had the same problem, but I can't find it. Would any of you can work me through the procedure you did?

    We are cold to death as it is only blows but not burning.

    If you can call me to help out would be greatly appreciated.

    Please do not post phone numbers. Thank you

    John
    amsapp's Avatar
    amsapp Posts: 1, Reputation: 1
    New Member
     
    #10

    Jan 28, 2010, 07:35 AM
    Quote Originally Posted by furnacefixed View Post
    I had the same problem just now when I came back from X-mas with the in-laws. I needed a hot house and used your suggestions. It failed the first time, but then after tinkering with it, it worked for me. THANKS

    The info about the primary/secondary switches was great. I actually unscrewed the red metal plate, pulled the plate out, and tapped/cleaned the dime sized (in diameter; about the thickness of 3 dimes) metal part when just the tapping did not work. I took apart the wires and rehooked them too for a clean/fresh connection. After cleaning the dime sized object I noticed 2 more dime sized objects with others wires leading to them as well. I unscrewed, tapped, and cleaned those as well. All the wires from these 2 similar looking dime sized objects were leading to the main gas switch that I was promted to turn to off before beginning based on the user manual.

    Everything fired up nicely afterwards. The posting on the "red metal plate connected vertically" really helped me locate where the switch was. It's too bad the owner's manual does not go into more detail about this.

    Thanks for the internet as well! It's nice to find out information and do it yourself!
    I just got my furnace up and running with this information. Thanks!
    dgushardy's Avatar
    dgushardy Posts: 2, Reputation: 1
    New Member
     
    #11

    Jan 30, 2010, 12:39 PM
    KC13 you are the PRO. THANKS>>>>>>THANKS>>>>>THANKS... soooooooooooooo much
    bmwsRus's Avatar
    bmwsRus Posts: 1, Reputation: 2
    New Member
     
    #12

    Jan 30, 2010, 03:19 PM

    Limit swich is the "red metal plate connected vertically" and has two wires (purple and blue) going to one terminal, and one wire (blue) going to the other. The two blue wires are supposed to create a closed loop through the switch, so with an ohm meter you should have continuity between the two terminals. Both blue leads originate at the circuit board, and the purple lead goes to the pressure switch (which is attached to the induced draft blower). I did just as the others states, removed the switch, disconnected leads, tapped everything on the switch with the butt of my screwdriver, and then reinstalled. Worked like a charm. Please note: the pictures at the beginning of this post are of two rollout switches, and the last smaller image of the square plate with a sensor extended from it is the actual "primary limit swich."
    Raidersmack's Avatar
    Raidersmack Posts: 1, Reputation: 2
    New Member
     
    #13

    Feb 1, 2010, 01:17 AM
    on a cold night guess what my wife noticed the heater stopped blowing hot air.So what u going to do about it well like a man I Took a look at it. Sure enough had a blowing fan running with no gas burning. She was right again. Well got on the web and read another website that told me to clean the flame sensor for what reason I don't really know but did it. Recycled the system again and the same problem. The 1st led light slow flash and 2nd led light on continuous so back inside I went trying to get an answer so lucky I found this post the exact solution to my problem. Took the reddish colored board off and unplugged one of the wires so it could be reached better. Tap Tap Tap and a little more tap just to make sure and tap again. Well installed it back and reset the system again. Turn the power back on and made sure both led lights where flashing witch means normal then turn the heater on ran outside to see what was happening well both led lights where still flashing and the heater comeback to life thanks for the solution for g40uh x combustion primary or secondary switch open.
    manhandy's Avatar
    manhandy Posts: 2, Reputation: 1
    New Member
     
    #14

    Feb 1, 2010, 08:16 PM

    How do you reset the g40uh
    manhandy's Avatar
    manhandy Posts: 2, Reputation: 1
    New Member
     
    #15

    Feb 1, 2010, 08:26 PM

    What are the steps for restarting a
    g4ouh furnace?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #16

    Feb 1, 2010, 08:34 PM
    Factory service manual for G40UH(X)

    http://0190acd.netsolhost.com/manuals/G40UH_Series.pdf
    dgushardy's Avatar
    dgushardy Posts: 2, Reputation: 1
    New Member
     
    #17

    Feb 8, 2010, 12:15 PM
    https://www.hvacpartsshop.com https://www.hvacpartsshop.com/83l90--limitcontrolprimary.aspx
    https://www.hvacpartsshop.com/17w70--ignitioncontrol24vcircuitboard.aspx
    selm7557's Avatar
    selm7557 Posts: 2, Reputation: 1
    New Member
     
    #18

    Feb 15, 2010, 06:22 PM
    I also saw this forum, I am a renter. And after my landlord/brother... who is a plumber and heating guy... looked at the furnace, he could not find the problem.. I said the heater indicates that it was the primary and secondary switch. He called another heater guy, who came out and said it was the circuit board! A week later the board came in, my brother... I mean landlord, wasn't going to be home for awhile, so I decided to look it up online, I found this forum and when I tapped on the primary it worked... I was so pissed!! I could have done that a week ago! Thanks everyone for the help!
    tp7539's Avatar
    tp7539 Posts: 1, Reputation: 2
    New Member
     
    #19

    Nov 17, 2010, 09:34 AM
    I wanted to let you know that I had the same issue... and tapping on the red plate worked like a charm. Amazing that it was that simple.
    dreamchasers's Avatar
    dreamchasers Posts: 1, Reputation: 1
    New Member
     
    #20

    Jan 13, 2011, 10:08 PM
    Thank it work!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search


Check out some similar questions!

Propane Furnace won't start no pilot light red light flashes 3 times [ 6 Answers ]

My propane furnace G6RC has no visible flame and the red light either stays on or flashes 3 times in a row and then the furnace shuts off and tries to restart

Pilot light for Lennox G1203-110-4 [ 3 Answers ]

Where does the flame go on this old Lennox model?

How do you light the pilot light of a Carrier furnace? [ 1 Answers ]

How do you light the furnace of a Carrier furnace model #58DLA110-12?