    Knob & tube
    I have an old house (1865) and it has knob & tube wiring. I have a fluorescent kitchen light with an older flip switch which goes up or down. It is a three way, with a switch on each side of the kitchen, and I have to flip the switch several times for it to come on. My question is can this be dangeruos or just inconvienient? Thanks in advance
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Nov 25, 2009, 01:56 PM
    The fluorescent fixture is not working properly because the wiring does not have a equipment grounding conductor, and one is needed for any fluorescent fixture to start.

    You may notice that the fixture seems to work OK on humid days or those with high relative humidity, and will not work on days that are dry.

    All receptacles, light fixtures, and switches now and for some time are required to be grounded. Your fixture is not necessarily unsafe to operate as it is out of reach, but the lack of grounding is needed to operate properly.

    Any chance of changing the fixture to an incandescent fixture?
    mtconc's Avatar
    mtconc Posts: 119, Reputation: 9
    Junior Member
     
    #3

    Nov 25, 2009, 03:22 PM

    Not sure if we can change the fixture right now.. can I change the switch and ground the fixture or do I need something else?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #4

    Nov 25, 2009, 06:20 PM

    You said older flip switch, how old? How old is the fluorescent light fixture? Does it have "starter" (looks sort of like a small "C" size battery)? Does the same thing happen at both switches. If you turn the switch on and wait a while does the light eventually come on? Has it always done this of is this something new?
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #5

    Nov 25, 2009, 08:04 PM

    Uhh, TKRussell, he didn't say the light wasn't working correctly, he said the switch wouldn't turn the light on immediately. My first guess is that the switch is shot. I have some experience with 'no ground' wiring and know that fluorescent lights were around long before the grounding conductor came into general use. And tired switches are common.

    The most common reason a FL doesn't work correctly is end of lamp life. 2nd is dirty tubes and fixtures, although usually when that becomes a problem, end of life is not far off. 3rd reason is a bad ballast. Somewhere down the list farther is ungrounded fixture.

    Interesting note here. I have a 4' 2 tube fixture in a kitchen that has knob & tube wiring. The magnetic ballast cooked out and the fixture had to be replaced. I called a well known ballast manufacturer and asked an engineer what would be recommended for this situation, would an electronic ballast work w/o a ground or should I use a rapid start magnetic ballast fixture like the original? He immediately said I should install a ground. I said I am not ripping the plaster ceiling, fiberglas insulation, walls and doors out at this point in time just to run a ground. When he got it through his head that there was NO possibility of installing a ground, he said that an electronic ballast was the best choice in this situation. The light has been running for several years of daily use now and I have had no complaints. Now if you are starting the lamps in cold temperatures it makes much more of a difference.

    EPMiller
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Nov 27, 2009, 01:19 PM
    Uhh,EP, there are at least two switches, so the poster should be able to determine if the problem is a switch. Sure a switch can be changed as part of troubleshooting, however I am offering a popular reason for a problem with wiring that has no ground.

    Fluorescent fixtures require grounding to start. Don't discount my advice without reviewing available backup:

    Shown in this troubleshooting list:
    American Fluorescent

    And by Item 5 from Advance Ballast:

    http://www.advance.philips.com/docum...3529026841.pdf

    Includes electronic.

    They may work, then some days they may not. You have been lucky.

    Do more web search for many other sites that back up my advice.

    Mt, try an electronic ballast, keeping in mind, at least one manufacturer states grounding is needed. I have no other advice except install a grounded circuit to the fixture.
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #7

    Nov 27, 2009, 04:18 PM
    Quote Originally Posted by tkrussell View Post
    Uhh,EP, there are at least two switches, so the poster should be able to determine if the problem is a switch. Sure a switch can be changed as part of troubleshooting, however I am offering a popular reason for a problem with wiring that has no ground.
    Agreed, but I still stand by what I said. If nothing has been changed lately on the circuit and the light just recently started acting up my checks are 1) end of lamp life, 2) dirty tubes and fixture, 3) ballast, 4) power supply, 5) other things. Agreed that I jumped right to #4, but I assumed that the poster would have checked the tubes already. The age of the wiring brought a bad switch to mind. Also the use of the singular in describing what he does when turning the light on, made me think it was one of the switches. Probably bad assumption in hindsight. If it is just grounding, the problem should have been there all along.
    Fluorescent fixtures require grounding to start. Don't discount my advice without reviewing available backup: <snip web resources> Includes electronic.
    Yes, I distributed a copy of one of those, from Advance I believe, to my coworkers several years ago. I am familiar with correct procedure.
    They may work, then some days they may not. You have been lucky <snip>
    How can the original fixture in my kitchen have been just "lucky" for 40 years or so? Agreed that they will not start as easily w/o grounding, but temperature and humidity are definitely factors here.
    Mt, try an electronic ballast, keeping in mind, at least one manufacturer states grounding is needed. I have no other advice except install a grounded circuit to the fixture.
    Completely agree here. If at all possible, get a ground to that fixture. See the last paragraph of my previous post.

    No hard feelings here, just trying to explain myself.

    EPM

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Knob & Tube [ 1 Answers ]

I am currently remodeling my bathroom. Home built in the 50's with existing knob and tube. Bathroom has power coming into 1 switch that controls lighted medicine cabinet with outlet inside cabinet. Want to add 1 new light fixture, 1 GFI, and 1 ceiling fan (no light). Is there any diagram that...

Replacing Knob and Tube [ 3 Answers ]

I'm looking for a little clarification here. I'm in the process of replacing the Knob and Tube wiring in an older 1930 home. Although I trying to preserve the original look of the house the K&T prevents me from installing insulation in the attic. Originally there was only one circuit running into...

Tieing in to knob and tube [ 3 Answers ]

When tieing in 14/2 at switch box, what do you do with the neutrals?

Tieing knob and tube to 14/2 [ 1 Answers ]

Can someone please tell me how to tie knob and tube wiring into 14/2 wiring. This is a hundred plus year old house and I want to upgrade... Thank you Lou G.

Knob and Tube tie-in [ 13 Answers ]

I apologize if I missed this info elsewhere. I have an 80 YO bungelow with seemingly healthy knob and tube wiring. The house has a combination of old and new wiring depending on when past work was done. My question is what is the safest, code friendly or preferred way to mate the old K&T to new...


View more questions Search