    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #21

    Nov 23, 2009, 06:16 AM

    I would avoid disconnecting Neutrals at panel, unless it is positively NOT a Multi circuit. You can burn out some expensive equipment/appliances.
    Marshall132's Avatar
    Marshall132 Posts: 14, Reputation: 1
    New Member
     
    #22

    Nov 23, 2009, 08:19 AM

    Why is that?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #23

    Nov 23, 2009, 08:35 AM

    Ok, simple one. Your TV. It has a polorized plug. It should rally have a 3 prong plug. It doesn't.

    The neutral is connected to the wide prong, which in turn is connected to ground.

    Because components aren't 100% isulated, there is a small amount of leahage current present, so now that leakage current and whatever weird waveform that's present is TRYING to power all the other devices connected to the neutral.

    Since ground is used for communications in USB and TV coax, raising these groud potentions can evoke damage. There may be some info in the surge supression sticky in the Electrical & Lightng link on the top left of this page.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #24

    Nov 23, 2009, 01:34 PM

    Plus, if you have a circuit drawing 10 amps, and the other multicircuit hot has 1 light bulb on it.
    The load being very great compared to the bulb will cause the bulb to blow, can go as high as 240 volts.
    Marshall132's Avatar
    Marshall132 Posts: 14, Reputation: 1
    New Member
     
    #25

    Nov 23, 2009, 02:30 PM

    So you are saying that equipment that creates this stray current is traveling through other equipment that are tied into ground through other means than the neutral thus making it a complete circuit despite the neutral being disconnected.
    Marshall132's Avatar
    Marshall132 Posts: 14, Reputation: 1
    New Member
     
    #26

    Nov 23, 2009, 02:34 PM
    And stratmando, could you contextualize your response a little more. Where does the 240 volts come from?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #27

    Nov 23, 2009, 02:34 PM

    No, only the 2 circuits will be affected, The total voltage of the 2 circuits will equal 240 volts, without the neutral, 1 device could see 80 volts, the other would see 160 volts.
    80 + 160 equals 240.
    High or low voltages are dangerous.
    Nothing should be going through ground.
    Marshall132's Avatar
    Marshall132 Posts: 14, Reputation: 1
    New Member
     
    #28

    Nov 23, 2009, 06:01 PM

    You have completely lost me. The voltage between two different legs could be 240, though I thought it was more like 230, or 220. But you would need a short between two circuits with different legs (or the third if you have three phases, which I believe most residential electrical breakers don't) or a two pole breaker. Right? Is this what you are referring to? Or are you referring to the previously mentioned stray current and voltage?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #29

    Nov 23, 2009, 06:33 PM

    In the US voltages have been bumped up a bit. The standard single phase distribution is from a 240 volt center tapped transformer. That center tap is the ground neutral bond. Connect both ends of opposite 240 phases together, you'll get zero volts out.

    The second distribution that you'd see is 208 both in single and 3 phase. You'll also see 277 as a single phase voltage. 277 is used for lighting loads.

    I'm thinking on the second part of the question.

    Suppose we had a stove with a 4 wire connection and the sove turned on with the neutral disconnected. That neutral would se 120 V with respect to ground because it's being powered by a say a clock motor winding. Now suppose that there were 120 V outlets that used the neutral that you disconnected, say a convienience outlet. Now that 120 outlet is 240 V and limited in current by the winding of the clock motor.

    It's harder to explain the varying differences, but they are caused by RF filters which tend to connect the line to ground through various leaky devices like capacitors. This is where varying voltages come from.

    Here is a schematic of a typical filter: EP/VP Series

    Note all the interconnections. Note the leakage at 125 V is .73 mA. This low of a current may also a source with a 171K output resistance. This will skew a reading when a certain voltmeters are attached esecially those that have a Z in ohms/volt measured. A 10 Meg ohm resistor (many voltmeters) in series will act as a divider.

    The 10 meg ohm input Z meter needs 12 uA to measure 125 V, so weird voltages show. They can't deliver appreciable power, but could spark and could damage connected equipment.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #30

    Nov 23, 2009, 06:40 PM

    I'm not talking about any induced voltages, stray currents or anything, Just basically if 2 circuits sharing a neutral, and the neutral is opened and a Motor was plugged in on 1 circuit(black circuit), and you had a lamp(on red circuit/opposite phase)You can get close to Line Voltage. I see More 240 than the others.
    I was also talking about 2 Pole Breaker.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #31

    Nov 23, 2009, 06:42 PM

    Check this out:
    Weird Circuit Problem at Home?
    Marshall132's Avatar
    Marshall132 Posts: 14, Reputation: 1
    New Member
     
    #32

    Nov 23, 2009, 10:53 PM

    I get it now, I did not know what you meant by multi circuit.
    Marshall132's Avatar
    Marshall132 Posts: 14, Reputation: 1
    New Member
     
    #33

    Nov 24, 2009, 09:42 AM
    Quote Originally Posted by kiss;
    "In the US voltages have been bumped up a bit. The standard single phase distribution is from a 240 volt center tapped transformer. That center tap is the ground neutral bond. Connect both ends of opposite 240 phases together, you'll get zero volts out."
    The last sentence is confusing to me. Each phase is 120v to neutral and 240 to each other, right? Where are you getting 0v?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #34

    Nov 24, 2009, 01:07 PM
    The single phase is across the 240 volts, the 120 volt is only a center tap of a transformer, based on ratio and physical location in a coil of wire, to deliver the 120 volts.

    I found a couple of interesting diagrams. One new and shows grounding of current systems, and another very old by the verbage and obsolete 220 volts but gets the point across, that it is still only one single phase.
    Attached Images
      
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #35

    Nov 24, 2009, 02:23 PM

    You should have 0 Volts between Neutral and Ground.
    TK's drawing shows the Ground and Neutral Tied Together.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #36

    Nov 25, 2009, 08:49 AM

    Zero volts has been defined as the reference. A reference can be anywhere. But it makes sense to make the earth the 0 volt reference point. Earth and neutral is tied to the center tap, hence that is also the zero volt reference.

    What should be confusing is that wee call this single phase, because the PRIMARY is fed by a single phase system. The secondary is sort of a two-phase system with the phases tied together. These are just 180 degrees out of phase from each other, so putting the ends of a 240 line together will result in zero volts out.
    Marshall132's Avatar
    Marshall132 Posts: 14, Reputation: 1
    New Member
     
    #37

    Nov 25, 2009, 09:11 AM

    So the two phases have a 240v difference, correct? And each 120v to the neutral/ground. So what do you mean when you say "putting the ends of a 240 line together will result in zero volts out"?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #38

    Nov 25, 2009, 10:13 AM

    The last time I put two ends of a 240 volt circuit together, there was a large flash, melted metal, and a fire, due to what is called a short circuit.

    Then there was zero volts.

    I am interested in an explanation also.

    In addition, what is "sort of a two phase"?

    It is single phase, period.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #39

    Nov 25, 2009, 10:57 AM

    My friend has two phase distribution in Philadelphia.

    Two-phase electric power - Wikipedia, the free encyclopedia

    My transformer thing was all wromg:

    Soldermans Basic Electronics: Transformers Series and Parallel Connections.

    Some electronic trabformers are supplied as dual secondaries and dual primaries. The way you iterconnect them determines the voltage of the primary and current that the primary can handle. At the lower voltage it requres twice the curret and the higher voltage half. If you so happen to connect the primary in series the wrong way, you end up with zero volts out of the secondary.

    The secondaries can be connected in various ways two. Namely series and parallel. You get an extra wire to deal with when the transformer is not center-tapped.

    Connecting the 240's volt legs together 120 with an out of phase 120 V) should give you nearly zero volts. The phases would cancel. One way you would get double the voltage and the other the voltages would subtract.

    Making the connections live and unintentensional and not with matched parts could stress out some parts.

    120 in parallel with 100 VAC is not the same as 120 in parallel with 120 V.
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #40

    Nov 25, 2009, 07:07 PM
    Quote Originally Posted by tkrussell View Post
    The last time I put two ends of a 240 volt circuit together, there was a large flash, melted metal, and a fire, due to what is called a short circuit.
    Then there was zero volts. <snip>
    Hahahaha. I love it. Scares the bejeebers out of you too. Best one I ever did was cut into a 20A 120v line with a linesmans pliers. Big hole burned out of the side of it.

    EPMiller

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

"Zero" between Hot and Neutral, but Hot Neutral and Hot Hot to Ground [ 2 Answers ]

Hello! Our neighbor plugged in her vacuum yesterday. It ran for a second then shut off. All circuit breakers were set (and cycled off-on just to make sure). Troubleshooting: Hot to Neutral showed 0V. Hot to Ground showed 115V. Neutral to Ground also showed 115V.. Changed out the outlet...

What happen if you connect some grounds and neutral to the neutral bus bar and the do [ 1 Answers ]

The same conect some grounds and neutrals to the ground bus bar just using whichever bus bar is closest to the breaker so the wires don't have to travel all around the breaker box is that OK and safe to connect wires like that thank you

Do I need a converter from 240 V to 120V [ 2 Answers ]

HI... Do I need for a converter from 240 Volt to 120 Volt... cuse I have some electrical equipement which is working on 240 Volt.. now I want to use this equipment in the countries with 120 Volt... Do I need for converter or NOT?? reply me on the below email address Email...

Old 120v outlet [ 1 Answers ]

I am beginning to replace some old 120v outlets when I took off the face plate I found I have 3 white wires and 3 black wires. Do I cap two of each and only attach one black and one white on new outlet on new outlet?

120v to 220v? [ 2 Answers ]

I have a boat which is 240v 50 amp and the marina can only get me two 120v 50 amp circuits to me. Can anyone tell me if I can tie two 120v 50amp circuits into one 240v 50amp circuit. It would be greatly appreciated


View more questions Search