    Hot Tub Electrical Wiring
    I am getting ready to install a Dimension One spa that the manufacture calls for using #6-3 awg wire and 240 Volt - 50 Amp with a GFCI breaker and disconnect.
    I had the house pre wired for a hot tub and 240 Volt service. They installed a 50 Amp breaker in the main box and ran about 40 feet of #8-3 G AWG Type NM-B 600V wire to a disconnect box. I know I need to change the disconnect box to a GFI at 5-10 feet from the tub and will run #6 AWG UF wiring from the GFI to the tub.

    My question, is the #8-3 wire from the main box to the GFI going to be OK? I talked with the building inspectors office and he sent me a page from the NEC which said the wire was OK for 50 amps (Table 310.16) 2002 edition.

    Would a 50 Amp breaker be installed with 8-3 wire, why not use 6-3 wire?
    omzig's Avatar
    omzig Posts: 119, Reputation: 19
    Junior Member
     
    #2

    Nov 9, 2006, 11:34 PM
    According to NEC 334.80 the ampacity of NM cable (including NM-B) is determined using the 60ºC temperature rating column of table 310.16, which would mean that #8 is 40A and #6 is 55A. So for a 50A breaker it should be #6.

    There is a lot of confusion about this subject, and this is part of the code that is often misinterpreted by a lot of people including electricians and inspectors. The confusion stems from the fact that NM-B cable's conductors are rated at 90º... but this doesn't matter, according to 334.80, the 60º column is to be used for all NM cable. I was dinged on an inspection because of this once. I thought for sure that the inspector was wrong but after I looked into it further, I found out that he wasn't. Anyone who doubts this, check out the first sentence in this document (notably what's in parentheses and the chart on page 2) from Southwire: http://appprod.southwire.com/Product...=prodcatsheet6


    Here is NEC 334.80:
    334.80 Ampacity. The ampacity of types NM, NMC, and NMS cable shall be determined in accordance with the 60ºC (140ºF) conductor temperature rating. The 90ºC (194ºF) rating shall be permitted to be used for ampacity derating purposes, provided the final derated ampacity does not exceed that for a 60º (140ºF) rated conductor...
    Don't think that because it doesn't specify NM-B that it doesn't apply. NM-B is still considered type NM and there are actually types NMC-B (aka UF, 340.80 says 60º also) and NMS-B too.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring Hot Tub and using a 50 Amp Double Pole GFCI Circiut Breaker [ 10 Answers ]

:confused: I keep getting the GFCI breaker tripping after wiring my hot tub. I wired 2 hot Red and Black to the proper terminals and the White to the neutral and the Bare Copper to the ground Post at the tub. I am using 6-3 w/G per instructions. Could the GFCI breaker be bad? When I wire...

Hot tub electrical nightmare---help [ 8 Answers ]

Does anyone know where I can find the code for wiring a hot tub in Reno, Nevada? I have an electrician taking advantage of the fact I know nothing about this topic & I could really use some help.

Electrical hot tub problem---help! [ 2 Answers ]

Does anyone know how I can find out what the code is for wiring a hot tub in Reno, Nevada? I have an electrician taking advantage of the fact I don't know this stuff & I really need help.

Hot Tub Electrical Problem [ 2 Answers ]

Our problem is with it going on standby after the tub gets up to temperature. The breaker never kicks off. The red light just starts flashing. Anyone have any ideas?! Thanks so much for your help!

Electrical Wiring [ 2 Answers ]

I currently have a 20 amp circuit for my frig outlet in the basement. I would like to install a recessed 6" IC Halo fixture on this circuit. To do so, can I use a 14/2 gauge wire or should I use a 12/2 wire which is meant for the 20 amp circuit?


View more questions Search