 |
|
|
 |
New Member
|
|
May 17, 2009, 12:44 PM
|
|
AC Fan Runs Constantly Even if Unit is Turned Off!
I have a two story house with two air conditioning units. One for the upstairs and one for the downstairs. I rarely if ever use the upstairs unit because the master bedroom is downstairs and no one lives upstairs.
I had some company in town the other day and when we cut the air on it ran fine. The next day I noticed that the fan was still running on it and it was blowing air but not cold air. I switched the thermostat to the Off position and the fan continued to run. The only way I could get the fan to stop running was to trip the circuit breaker for the unit. I thought that the thermostat may be bad so I switched with another one I had here at the house. When I flipped the breaker back on the fan started right up just as before. I'm not sure how the fan can run like that when the thermostat is set to Off and the fan setting is set to Auto.
I went up in the attic to see if I could find some kind of reset switch on the air handler but I didn't see anything. If anyone has any ideas on what's going on that would be great! This unit is rarely used so I know its not worn out, but maybe that's part of the problem.
Thanks in advance for your help!!
|
|
 |
Heating & Air Conditioning Expert
|
|
May 17, 2009, 12:54 PM
|
|
More than likely you have a A/C fan relay that is stuck OR the contacts are burnt together. The relay is activated by 24 volts when you turn on the A/C OR fan switch activation.
|
|
 |
New Member
|
|
May 17, 2009, 04:47 PM
|
|
Thanks hvac1000! I'm pretty handy with most things around the house but I'm not an hvac technician. Is this something I can replace on my own or are special tools needed? Where exactly is the fan relay located?
The unit is a Comfortmaker Model# FBF050B12A3. MFG# NTG3050FBA3. Serial# L9909 68241.
|
|
 |
Heating & Air Conditioning Expert
|
|
May 17, 2009, 07:52 PM
|
|
Heil/ICP/Tempstar/Comfort Maker are all about the same as far as units/parts are concerned. I do not have a diagram of these units handy but if you look on the blower door there should be a wiring diagram there. Many times the fan relay will be located on the circuit board so it could be a expensive proposition. If you have to change the part after you check it to be sure it is defective I recommend you make your own wiring diagram of EXACTLY where the wires will be removed from so they can be put back at the same location on the new part.
As mentioned before I suggest you test the part to be sure it is defective before replacing. Other items like a defective/tripped limit control or a shorted thermostat wire can also cause the problem you mentioned.
|
|
 |
New Member
|
|
May 20, 2009, 03:43 PM
|
|
I attached a picture of the diagram. The capicator for the blower motor is easy to spot because its pretty big and has two brown wires going to it.
I am thinking that the fan relay is the part on the circuit board that's titled "CIR BLOWER" on the diagram with black and orange wires going to it. Its located on the circuit board and its looks like a very small black box. If this is the fan relay, should I be able to pop the top off the box to see the contacts inside? Thanks again!
|
|
 |
Plumbing Expert
|
|
May 20, 2009, 04:53 PM
|
|
Just one more simple test to try before replacing fan relay... try unhooking the thermostat wires from the airhandler.(not from the thermostat, but from the air handler itself). Let us know if the blower turns off now.
|
|
 |
New Member
|
|
May 20, 2009, 06:14 PM
|
|
I just unhooked all of the thermostat wires from the circuit board in the air handler and flipped the power back on to the unit and the blower is still running.
Does this mean the wires to the thermomstat are fine? I still don't really know how to check the fan relay. Thanks!
|
|
 |
Ultra Member
|
|
May 20, 2009, 06:41 PM
|
|
When you switch the thermostat to heat, does the exhaust fan come on? Or when you switch the thermostat to AC does the outdoor unit come on.
The reason I am asking is that if your transformer is burned up the fan will run continuously.
|
|
 |
New Member
|
|
May 20, 2009, 07:53 PM
|
|
The exhaust fan and blower run all the time. They run when the thermostat is switched to off, heat, or cool and the outside unit doesn't come on in any of the settings. The fan is always set to Auto. Ideas?
|
|
 |
Plumbing Expert
|
|
May 21, 2009, 03:17 PM
|
|
 Originally Posted by rusig
I just unhooked all of the thermostat wires from the circuit board in the air handler and flipped the power back on to the unit and the blower is still running.
Does this mean the wires to the thermomstat are fine? I still dont really know how to check the fan relay. Thanks!
Yes, this eliminates the thermostat and wires as the problem.
I was under the impression that you just had a air handler. But now it sounds like you have a forced air furnace with ac, correct? If so, you may have a bad high limit, or a flame rollout switch that has tripped. Either of these could cause draft inducer and blower to run nonstop.
|
|
 |
New Member
|
|
May 21, 2009, 10:26 PM
|
|
You are correct, it is a forced air natural gas furnace with AC. What is the best way to check they high limit and flame rollout switch? Could it still be the fan relay?
|
|
 |
Plumbing Expert
|
|
May 22, 2009, 03:41 PM
|
|
Best way to test limit and rollout is to take the two wires off them and connect the wires together. If this solves your problem, don't run unit (other than for trouble shooting) this way. I think for us to help any further, we will need a make and model of the furnace. Pics of the inside controls of furnace would help also. Let us know what you find.
|
|
 |
Heating & Air Conditioning Expert
|
|
May 22, 2009, 05:27 PM
|
|
A roll out in action. This usually wipes out the parts you are going to test.
|
|
 |
New Member
|
|
May 22, 2009, 06:00 PM
|
|
Here are some pictures of the Comfort Maker unit, the full wiring diagram, and the model #s. In the picture of the unit you can see three sets of red wires all running to sensors and three sets of blue wires running to sensors. Two sets of the blue wires run to seņors on the top and bottom of the blower motor in the back and the other set runs to a sensor right above the exhaust motor. Let me know if you need better pictures of the sensors. Are these the right switches/sensors to be testing? Thanks.
|
|
 |
Ultra Member
|
|
May 22, 2009, 06:34 PM
|
|
Sounds to me like you either have a bad control board, or a pressure switch stuck closed.
|
|
 |
Plumbing Expert
|
|
May 24, 2009, 10:50 AM
|
|
 Originally Posted by mygirlsdad77
Best way to test limit and rollout is to take the two wires off of them and connect the wires together.
Sorry this was incorrect info. I should have said, the easiest way to check these limits if you don't have a multimeter is to jump the switch. The actuall best way to test the switch is to shut power off to furnace, remove wires from switch(limit) and do a continuity test acress switch to see if switch is open or closed. YOu can do this test on your pressure switch as well. (to see if its stuck closed). Hope this is all making sense.
|
|
 |
Plumbing Expert
|
|
May 24, 2009, 10:54 AM
|
|
Your rollout switch has the red wires going to it and is located at top side of burner area, there should be a little reset button in the middle of it, try pusing this button and see if it clicks. The high limit also has red wires going to it, it is located on the heat exchanger wall behind the gas valve. It has the bluish green sticker on it. Your model may also have a limit mounted on the blower fan housing, it should have red wires going to it also if you have one.
|
|
 |
New Member
|
|
May 25, 2009, 03:13 PM
|
|
I had the same problem with my unit. The fan would not go off unless I turned off the circuit breaker. I replaced the RELAY Switch/board (cost about $15) and that fixed it.
|
|
 |
New Member
|
|
May 28, 2009, 02:16 PM
|
|
Gentlemen, it looks like I may have the unit up and going again. Mygirlsdad, I did as you instructed and checked the rollout switch resets and sure enough one of them was tripped. You would have never known it by looking at it. Thank you all for your help!!
|
|
 |
Plumbing Expert
|
|
May 28, 2009, 03:40 PM
|
|
Glad you got it going. Please let us know if it trips again. Good job.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Rheem Central A/C Unit -- Outside Fan Runs Constantly
[ 7 Answers ]
Our unit is a RHEEM Classic and was manufactured in 2000. Model #RAMB-048-JAZ
The outside fan never turns off. The inside unit runs as it should and cycles on and off appropriately and the A/C cools great. The problem is that we have to go out and remove the disconnect (breaker) outside in order...
Gas furnace runs constantly
[ 3 Answers ]
This relates to a problem I'm having with my gas furnace. I took a power hit and ever since then the blower on my furnace continually runs when I have the thermostate set at off and fan on auto. I repalced the thermostate no help. I did notice the fan runs slightly faster when I switch it from auto...
Fan runs constantly
[ 3 Answers ]
The fan on my Carrier runs non-stop. The burner kicks on from time-to-time, but the fan is a constant. It never did this until a few weeks ago (settings didn't change). I put new batteries in the thermostat to see if that would help - it didn't. Any ideas to get the fan to shut off?
AC fan runs constantly
[ 4 Answers ]
Just bought a new home last fall and noticed that the AC fan was running constantly. Replaced the old thermostat with a programmable version. Didn't really use the air much after that but it has been working the heat pump all winter with no problems. Now we are starting to use the AC again and...
View more questions
Search
|