    #41

    May 16, 2009, 08:51 AM
    Quote Originally Posted by Joshdta View Post
    do you get power on both lines after you reset the trip out switch?
    If you are talking about that little reset switch on the fuse, I did try pushing that a couple of times, then tested white-yellow again... No reading.
    KenLoh's Avatar
    KenLoh Posts: 55, Reputation: 2
    Junior Member
     
    #42

    May 16, 2009, 08:57 AM

    Question: That row of terminals, R,W1,G,C on the far right inside the Air Handler... if there is power on those terminals, shouldn't there be power leading to the thermostat? Does that wire lead to the thermostat?

    When I tested those terminals last night, and saw power on them, I immediately went to the wall thermostat, removed the stat cover and tested the wires from the wall. No power there.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #43

    May 16, 2009, 09:43 AM

    If you have power on r you should have power to the stat. that reset is supposed to click back into place if it is triped, also it may have a little with mark or red showing it is out.
    KenLoh's Avatar
    KenLoh Posts: 55, Reputation: 2
    Junior Member
     
    #44

    May 16, 2009, 09:53 AM
    Quote Originally Posted by Joshdta View Post
    if you have power on r you should have power to the stat. that reset is suposed to click back into place if it is triped, aslo it may have a little with mark or red showing it is out.
    Questions:

    Does that wire from the air handler (R,W,G,C) lead directly to the thermostat?

    If Yes, and If there Is power at R,W,G,C and NO power at thermostat, does that mean there's a problem somewhere along the wire behind the walls??
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #45

    May 16, 2009, 09:56 AM

    You should have two wires hooked to the board at the air handler. 1 set to the ac unit, and 1 set to the t-stat. and yes it should go directly from the board to the stat. you have power from r to c at the board now? But not at the stat?
    KenLoh's Avatar
    KenLoh Posts: 55, Reputation: 2
    Junior Member
     
    #46

    May 16, 2009, 10:05 AM
    Quote Originally Posted by Joshdta View Post
    you should have two wires hooked to the board at the air handler. 1 set to the ac unit, and 1 set to the t-stat. and yes it should go driectly from the board to the stat. you have power from r to c at the board now? but not at the stat?
    That is correct. Power at air handler side, no power at wall for thermostat.
    Check my pics for clarity.

    Do you think I should try putting in a new tstat?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #47

    May 16, 2009, 10:09 AM

    You have 24 VAC and the transformer is good and so is the circuit breaker in your tests.

    I'm looking at the pic in post #39. It appears that you have a 3 stage heat and cool of some sort.

    There is something fishy with the three reds twisted together and the black wire connected to terminal R. That other thermostat wire going to the outside unit seems connected way wrong.

    On the strip:

    Jumping R to G should make the fan come on.
    Jumping R to W1 should make the heat come on.
    W2 and W3 are not connected and this is 2nd and third stage heat.

    R and C should have 24 VAC on them. They do, so the tstst should light up

    R is either not going to the tstat? It's also black and not red. This raises some real wiring flags.

    1. Wrong thermostat - not 3 stage heat
    2. The AC contactor coil being wired totally wrong.

    Too confused at this point.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #48

    May 16, 2009, 10:10 AM

    Not if you have no power at the stat. I would say you have a broken wire somewhere. How many volts are you getting between r and c at the board? 28 volts??
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #49

    May 16, 2009, 10:15 AM

    If you jump wires at the control board in the air handler does anything work? Fan? outdoor unit? Heat?
    KenLoh's Avatar
    KenLoh Posts: 55, Reputation: 2
    Junior Member
     
    #50

    May 16, 2009, 10:15 AM
    Quote Originally Posted by Joshdta View Post
    not if you have no power at the stat. i would say you have a broken wire somewhere. how many volts are you getting between r and c at the board? 28 volts?????
    Yes... 26-28V
    KenLoh's Avatar
    KenLoh Posts: 55, Reputation: 2
    Junior Member
     
    #51

    May 16, 2009, 10:20 AM
    Quote Originally Posted by KeepItSimpleStupid View Post
    You have 24 VAC and the transformer is good and so is the circuit breaker in your tests.

    I'm looking at the pic in post #39. It appears that you have a 3 stage heat and cool of some sort.

    There is something fishy with the three reds twisted together and the black wire connected to terminal R. That other thermostat wire going to the outside unit seems connected way wrong.

    On the strip:

    Jumping R to G should make the fan come on.
    Jumping R to W1 should make the heat come on.
    W2 and W3 are not connected and this is 2nd and third stage heat.

    R and C should have 24 VAC on them. They do, so the tstst should light up

    R is either not going to the tstat? It's also black and not red. This raises some real wiring flags.

    1. Wrong thermostat - not 3 stage heat
    2. The AC contactor coil being wired totally wrong.

    Too confused at this point.
    It's not likely the issue with the wiring or how it's set up, (although I understand, sometimes things are not set up the way it should be!) as everything has been running fine since I bought the house end of 2002, so the house is about 6-1/2yrs now. This issue just popped up now.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #52

    May 16, 2009, 10:20 AM

    You need to check for 28 volts between the 3 buged red wires and C at the board
    KenLoh's Avatar
    KenLoh Posts: 55, Reputation: 2
    Junior Member
     
    #53

    May 16, 2009, 10:27 AM
    Quote Originally Posted by Joshdta View Post
    if you jump wires at the control board in the air handler does anything work? fan?, outdoor unit? heat?
    Nope... I put the green(G) to black(R)... nothing happened.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #54

    May 16, 2009, 10:28 AM

    Is that black tied in with the 3 red? I can not see it from the pic?
    KenLoh's Avatar
    KenLoh Posts: 55, Reputation: 2
    Junior Member
     
    #55

    May 16, 2009, 10:31 AM
    Quote Originally Posted by Joshdta View Post
    you need to check for 28 volts between the 3 buged red wires and and C at the board
    You mean check for 28V between the 3 red wires in the wirenut, and the blue wire at C?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #56

    May 16, 2009, 10:33 AM

    Yes, and where does the black go that is hooked to r on the board, and where doe that blue go that is hooked to r on the board?
    KenLoh's Avatar
    KenLoh Posts: 55, Reputation: 2
    Junior Member
     
    #57

    May 16, 2009, 10:41 AM
    Quote Originally Posted by KenLoh View Post
    You mean check for 28V between the 3 red wires in the wirenut, and the blue wire at C?
    3 Red wirenutted wires to C shows no power
    To G or W1 - same thing - no power

    To R - 26V
    To W2 or W3 (even though empty) - 26V
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #58

    May 16, 2009, 10:43 AM

    This is why your stat is not lighting up 1 of the 3 red wires sends power up to the stat, and it has no power. The other one goes to the outdoor unit? Where is the 3rd one going??
    KenLoh's Avatar
    KenLoh Posts: 55, Reputation: 2
    Junior Member
     
    #59

    May 16, 2009, 11:03 AM
    Quote Originally Posted by Joshdta View Post
    yes, and where does the black go that is hooked to r on the board, and where doe that blue go that is hooked to r on the board?
    The black on R goes into that brown jacket wire. Also on that brown wire, you can see a single red wirenutted to the other 2 reds. Okay, this brown wire with the black and red leads to 2 thin black wires that goes into a white pvc pipe that goes into the ground of the garage floor. I am thinking it leads to the back to the AC condenser.

    The blue at the rear row of R, that gets capped (clear plastic cap) with the darker blue that leads to the transformer (red coil).
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #60

    May 16, 2009, 11:14 AM

    Ok where is the third red wire going? From the wire bug?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

No power to thermostat [ 19 Answers ]

Hi, I was trying to replace my old stat with a new programmble one. I had turned off the furnace before installing new one. But the new one didn't work and so, I put the old one back on. But the old one does not power now and display on the old stat does not come up. Can any one help me here...

No power to Thermostat [ 11 Answers ]

I have no power to my ac/heat digital stat, Ive replaced breakers and unit fuses, power noted to unit at fuses.. not sure what to test next... this happened after night of storms

Getting power to my thermostat [ 2 Answers ]

I am trying to hook up a new furnace, and I am having trouble getting power to the thermostat, any help would be greatly app.

No power out to my thermostat [ 10 Answers ]

Hi Can anyone help I replaced a thermostat (ruud) because the power was always on The fan kept blowing even when the unit have been turn to the off position and the fan was on the auto position Now nothing comes on I checked the trasformer where it has 120 coming in but no power coming out...

No power on thermostat [ 1 Answers ]

Help!! This morning we woke up to a freezing second floor. It is on a second unit, and when I went upstairs, the thermostat has no reading at all... no power. I checked the breaker and all was fine there. Is there an exterior switch on the unit that could need to be powered up?


View more questions Search