    My furnace. Its off but it still keeps blowing air. Reset high temperature switch?
    Ok. My old thermostat was a digital one but without batterys, and the screen didn't work (wasnt displaying anything, could not see nothing) so I went Lowe's to buy a new one just today. I turned off the furnace and the breaker when I installed it. Everything went perfectly until I went upstair to turn the furnace on. I have my heater on and its only blowing air, not cold or hot. Just air, so I went to my thermostat to turn off the furnace but nothing. The thing still keeps blowing air even when I already turned off my thermostat. The only way I can turn my furnace off is my hitting the OFF and ON switch by my furnace.

    The problem is that it did this before I replaced my old thermostat. I replaced it because I thought that was the problem but nope. Its still doing the samething as it was before. I can put it on heat or ac but the thing will still blow air out, again.. not cold nor hot. Just air. Fan is on AUTO on my thermostat.

    My house is fairly new. Not sure if that helps but here is the Model number of my furnace: Bryant MODEL 310AAV/JAV. I think it's a gas furnace.



    Oh yeah. There was a light flashing. It was flasking 3 times quickly then 3 times slowly
    (333 3 3 3) That is what it looked like.


    Here is what the code reads:

    33, LIMIT CIRCUIT FAULT - Indicates the limit, drath safeguard, flame rollout, or blocked vent switch (if used) is open or the furnace is operating in high-heat only mode due to 2 seccessive low heat limit trips. Blower will run for 4 minutes or until open switch remakes whichever is longer. If open longer then 3 minutes, code changes to lockout #13. If open less then 3 minutes status code #33 continues to flash until blower shuts off. Flame rollout switch and BVSS require manual reset Check for:
    -Recstricted vent
    -Excessive wind
    -loose blower wheel
    -proper vent dizing
    -dirty filter or restricted duct system
    -Defective blower motor or capacitor
    -defective switch or connections
    -inadequate combustion air supply (flame roll-out switch open)






    Im really thankful for the help. Being a single mother of 3, it's a bit hard to pay those high repair bills.

    Thanks. Kati.


    Oh yeah, Someone told me it could be that I need to reset high temperature switch. Anyone have an idea onto where this could be located?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #2

    Apr 23, 2009, 05:53 AM

    Sounds like a high limit problem. How is your filter?
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #3

    Apr 23, 2009, 05:54 AM
    Turn you power off to yor unit and look for this.


    http://www.hvacpartsoutlet.com/Produ...LHH12ZB220.jpg
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #4

    Apr 23, 2009, 05:55 AM
    Then with the power off tap it between the wirs with a screw driver or something gently. This limit is supposed to reset itsself but sometimes if they are over heated it will stick.
    omgnowaykati's Avatar
    omgnowaykati Posts: 23, Reputation: 1
    New Member
     
    #5

    Apr 23, 2009, 06:25 AM
    Would you happen to know where this might be located?

    Should I open the furnace doors or is it in the attic?
    omgnowaykati's Avatar
    omgnowaykati Posts: 23, Reputation: 1
    New Member
     
    #6

    Apr 23, 2009, 06:27 AM

    My filter has just been replaced yesterday. Its new. Brb while I go look for the image you showed.

    Thanks for the help.
    omgnowaykati's Avatar
    omgnowaykati Posts: 23, Reputation: 1
    New Member
     
    #7

    Apr 23, 2009, 08:25 AM

    Okay, Been looking for it for almost an hour and I think I might of found it.

    There are 2 red wires connected to it and there isn't a reset button. They are two screws to the side of out. Im not sure if I should remove the screws and pull out the part. Im not sure if it's long from the back as it shows on the picture you linked me. I found it in front of my furnace.

    Another thing is that its connect to the air vent. The blower is below. Here is a picture I found on the internet along with where I think it might be at.



    Also, There are 2 red wires connected to something where the image above says the number 7. You can see it at the buttom of the vent there is a little device.
    omgnowaykati's Avatar
    omgnowaykati Posts: 23, Reputation: 1
    New Member
     
    #8

    Apr 23, 2009, 11:38 AM

    Bryant Plus 80 Manual Here's a online guide of my furnace.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #9

    Apr 23, 2009, 01:13 PM

    That's should be the right one. In the front of your furnace right above the gas valve
    omgnowaykati's Avatar
    omgnowaykati Posts: 23, Reputation: 1
    New Member
     
    #10

    Apr 23, 2009, 01:55 PM

    Okay, I hope that was the correct thing I was tapping but now the code changed to code 13.

    13 LIMIT CIRCUIT LOCKUT - Lockout occurs if the limit, draft safeguard, flameroll out, ore blocked vent switch (if used) is open longer than 3 minutes or 10 seccessive limit trips occurred durning high heat.
    -Control will auto reset after three hours
    -Refer to #33,
    omgnowaykati's Avatar
    omgnowaykati Posts: 23, Reputation: 1
    New Member
     
    #11

    Apr 23, 2009, 01:58 PM
    Maybe I wasn't tapping the correct thing? Hmm, Its right behind the gas valve.
    omgnowaykati's Avatar
    omgnowaykati Posts: 23, Reputation: 1
    New Member
     
    #12

    Apr 23, 2009, 02:31 PM

    OK, I went back and heard a clicking sound if I moved each wire connected to the High limit control switch up and down glently. If it helps I can take some photos of my furnace all around.


    Im REALLY grateful for all the help and thanks for hanging in there with me. Lol :)
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #13

    Apr 23, 2009, 04:59 PM

    OK sometimes the conectons there get coroted may be they just need cleaned. Also there are lots of small limmits with red reset bottons in the middle of them. Check to see if any of them are out just press them back in the will click.
    omgnowaykati's Avatar
    omgnowaykati Posts: 23, Reputation: 1
    New Member
     
    #14

    Apr 24, 2009, 03:07 PM

    Hmm, there is just 1 that I see and its connected to nothing, Just connected to the side of a steel plate, I tried to push it in but it doesn't click or anything. Let me take some pictures.
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #15

    Apr 24, 2009, 03:17 PM

    OK lets try something else and you tell me what happens
    Joshdta's Avatar
    Joshdta Posts: 2,549, Reputation: 45
    Ultra Member
     
    #16

    Apr 24, 2009, 03:18 PM
    I will give you the order of operation and you tell me what step does not work OK
    omgnowaykati's Avatar
    omgnowaykati Posts: 23, Reputation: 1
    New Member
     
    #17

    Apr 24, 2009, 03:43 PM



    <a href="http://s605.photobucket.com/albums/tt137/omwnowaykati/Furnace/?action=view&current=DSCF4283.jpg" target="_blank"><img src="http://i605.photobucket.com/albums/tt137/omwnowaykati/Furnace/DSCF4283.jpg" border="0" alt="Photobucket"></a>
    omgnowaykati's Avatar
    omgnowaykati Posts: 23, Reputation: 1
    New Member
     
    #18

    Apr 24, 2009, 03:45 PM

    omgnowaykati's Avatar
    omgnowaykati Posts: 23, Reputation: 1
    New Member
     
    #19

    Apr 24, 2009, 03:47 PM










    omgnowaykati's Avatar
    omgnowaykati Posts: 23, Reputation: 1
    New Member
     
    #20

    Apr 24, 2009, 03:50 PM
    On the 3rd picture, That is the only reset switch I can see but it doesn't click or no anything but go in and out really.


    All the other red circles is the place where I was banging with a screw driver.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Troubleshooting 4 flashing lights - open high temperature limit switch [ 7 Answers ]

Thanks for your input. I finally was able to reverse the wiring and got it squared away. While I was in the attic I thought I would replace the motor which drives the fly wheel. I thought I was a hero till I put everything together and discover 4 flashing lights. The lights indicate "open high...

Furnace won't light without a furnace switch reset [ 15 Answers ]

Hello I have a Tempstar/Keeprite furnace model HGF120NE-1, Serial number 8464124770. (the exterior of the furnace has Tempstar logo and interior of furnace has Keeprite logo.) This furnace has an intermittent pilot light system. At times, especially in the morning after allowing a...

Gas furnace still not blowing warm air after reset [ 2 Answers ]

We have the Carrier 9200 gas heat/cool unit (indoor). We followed the reset instructions and the fan is blowing but we're still getting cool air. What causes it to blow out only cool air and not warm? What else can we do. Again, our home is mainly gas and our oven works fine. I tested the Air...

Trane xe 80 open high temperature limit switch [ 1 Answers ]

Furnace is about 13 years old... we just replaced the ignighter in it last night because it was running through all the steps to run except ignighting. It fired right up and ran for about 7-8 hours... now it won't ignite at all (it is running through all the steps it needs to except for...


View more questions Search