Ultra Member
|
|
Apr 14, 2009, 04:51 PM
|
|
Like I said 4 flashes, is usually limit switch
|
|
|
New Member
|
|
Apr 14, 2009, 04:54 PM
|
|
My filter is fine I've been changing that frequently
|
|
|
New Member
|
|
Apr 14, 2009, 04:56 PM
|
|
I got the flame sensor out and it is real dirty I'm going to clean it and put back in
|
|
|
Ultra Member
|
|
Apr 14, 2009, 04:56 PM
|
|
OK well try the flame sensor, and while you are down there look on the back of the furnace doors for the fault code chart and see if it matches what you found online. And get back too me. I am usually on here in the morning around 8 and in the evenings for a hr or so.. josh
|
|
|
New Member
|
|
Apr 14, 2009, 04:57 PM
|
|
Where's the limit switch?
|
|
|
New Member
|
|
Apr 14, 2009, 04:58 PM
|
|
Josh I'm in Ohio, my dad is an WVU alumni
Thanks Mike
|
|
|
Ultra Member
|
|
Apr 14, 2009, 05:00 PM
|
|
Nice, what town?
|
|
|
Ultra Member
|
|
Apr 14, 2009, 05:01 PM
|
|
|
|
|
Ultra Member
|
|
Apr 14, 2009, 05:02 PM
|
|
Above the gas valve and the ventor motor. Usually on the right side of the furnace
|
|
|
New Member
|
|
Apr 14, 2009, 05:04 PM
|
|
Columbus home of the Buckeyes!!
|
|
|
Ultra Member
|
|
Apr 14, 2009, 05:06 PM
|
|
Go buckeyes, any school that hates Michigan as much as wvu is OK by me. Lol
|
|
|
New Member
|
|
Apr 14, 2009, 05:10 PM
|
|
Yeah I hate to wish bad luck on anyone, but the way he left WVU and went to Mich was all wrong
|
|
|
New Member
|
|
Apr 15, 2009, 05:14 PM
|
|
Yo Josh after cleaning the flame sensor my furnace has been working fine even though the error code says the swith is open. Thanks again, you r the man
|
|
|
Ultra Member
|
|
Apr 15, 2009, 05:18 PM
|
|
Glad it works, not sure why the code is still flashing.
|
|
|
Ultra Member
|
|
Apr 15, 2009, 05:19 PM
|
|
Does your fan, blower run all the time?
|
|
|
New Member
|
|
Apr 21, 2009, 03:18 PM
|
|
The blower doesn't run all the time and the error light has stopped flashing and its been working fine since the cleaning of the flame sensor.
Thanks again
|
|
|
Ultra Member
|
|
Apr 21, 2009, 03:45 PM
|
|
Great if you have any more problems look me up.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
York Diamond 80 blowing cold air.
[ 13 Answers ]
Hi All...
Hopefully uou can help me out...
I have a york diamond 80 gas furnace. It was working fine up until a few days ago..
It began to blow out cold air when the house clearly was not even close to "requested" temp.
It turns on, starts the initial motor, the humidifer also kicks...
Error code for "open pressure switch" on York natural gas furnace
[ 6 Answers ]
I get three red flashes from the furnace after an attempt sequence when the t-stat calls for heat. The motor starts, and seems to try to light but after about thirty seconds, it quits and gives the error code.
I have removed both gray tubes from the pressure switch and made sure they are...
Inducer Motor on York Diamond 90 Keeps Running
[ 4 Answers ]
I recently had the inducer motor replaced when it burnt out but I am having issues again. The inducer motor keeps running and won't stop until the whole system shuts down.
Let me correct myself. I actually am reading about 26 V on the terminals of the pressure switch. The voltage on the...
Spill or Aux Limit switch
[ 9 Answers ]
My York Diamond 80 is not heating. When I turn it on the fan starts but flame does not attempt to ignite. The diagnostic code flashes 4 times. Sheet says 'Aux. Or Spill Limit switch'
What are these? Where are they? Can they be reset?
York Diamond 90
[ 1 Answers ]
I have a york diamond 90 and I have 4 code show what could it be