    I would like to design stair pressurisation & lobby pressurisation fans for a 24 storey residential building.I would like to get the help of some body to make design calculation for the capacity of fans asper NFPA standards.
    Quantum's Avatar
    Quantum Posts: 38, Reputation: 2
    Junior Member
     
    #2

    Apr 25, 2009, 04:27 AM
    He Gopikn



    a- For High Storey Building: Assuming 2 door opening.

    Area of open door ( A ) = 2 x 0.9 = 1.8 m2

    Egrees velocity ( Ve ) = 0.75 m/s ( across open door )
    Total Air Flow (Qs ) = Ve x n x A / 0.6 = 4.5 m3/s = 9,534 cfm
    ( Through open door )

    b- Leakage Through Closed Doors

    Leakage area of double leaf door ( Al ) = 0.02 m2
    Total number of closed doors (nl ) = 26 Nos.
    ( K ) = 0.829
    ( p ) = 50
    Total Air leakage (Ql) = K x nl x Al x p0.5 = 3.048195912 m3/s = 6,458 cfm
    Add 25%, So Ql = 8072.552734 CFM

    Select the higher of the two --- Q = 9534 CFM
    mohammad sharif's Avatar
    mohammad sharif Posts: 1, Reputation: 1
    New Member
     
    #3

    May 4, 2009, 07:09 AM

    You can check application ASHRAE standard chapter A52 of 2007 it include on a clear description on how to size preesurzation system and a very valuable data in this regard. ASHRAE data comply with NFPA recommendations.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Smoke extract system [ 1 Answers ]

I am designing a smoke extract system for a big atrium within an office building. The atrium is about 12 floors height and with skylight. Smoke extract fans shall be installed at the highest point of the atrium, which will work as a heat relief as well because this project is in a very hot...

Effect of high rise buildings on earths rotation [ 3 Answers ]

Is there any effect on the earths rotation due to increase in the number of high rise building reaching to heights of nearly a mile. Especially if they are concentrated in some cities like Manhattan or Dubai.

Bryant Temp Rise Tooo High [ 3 Answers ]

My 10 year old Bryant gas forced air furnace is distributing hot air that smells HOT. This has continued beyond the early initial fall heat smell period. I measured the plenium temp at 170F after a 10 min burn time. The info plate list the Temp rise as 55-85 F; which would translate to a max outlet...


View more questions Search