    Bryant Plus 80t will not ignite
    My dad had a Bryant Plus 80t gas furnace installed a couple of years ago. He's having some home improvement work done in the basement where the furnace is. The walls were bleached while the furnace was running. The fumes went throughout the house, so I turned the thermostat off and aired out the house. The next morning, the furnace would not ignite; the blower continues to run though. The LED is flashing 33 and after a couple/few minutes it changes to 13. I am not at his house at the moment to recite from the furnace panel what exactly that means but it is something along the lines of a limit circuit, draft safety, blocked vent or flame rollout is the cause. The two resettable switches have not tripped. What else can we do to troubleshoot it? We've disconnected/reconnected most of the electrical connections in case the chlorine bleach caused some corrosion in those contacts. But still no luck. Maybe the combustion blower is not kicking on to create the draft necessary before ignition?
    TerryTerrific's Avatar
    TerryTerrific Posts: 7, Reputation: 0
    New Member
     
    #2

    Mar 30, 2009, 08:08 AM
    When our Rheem (Criterion model) gas furnace was just blowing air, we called for a service person.

    Within five minutes he found the problem.

    A cracked HOT SURFACE IGNITER.

    I was told that this part does not last forever.

    The igniter looks like a 2 inch tall element (similar to what is inside an incandescent light bulb but flat, like a large paperclip) mounted on a square base that is attached to 6 inches of wrapped wires that ends in a two prong male plug.

    Hot surface igniters are very delicate and the igniter part should not be touched by human hands because the oil on our hands will damage the surface (just like a halogen bulb).

    +

    Here is the write up …

    • Service call on a Rheem 80+ furnace.

    • Found cracked hot surface igniter.

    • Replaced igniter and cleaned fame sensor.

    +

    $079.95 = service call
    $040.00 = ½ hour labor at $80.00 / hour
    $065.00 = hot surface igniter

    $184.95 = total

    +

    Terence in Brook Park, oHIo
    TerryTerrific's Avatar
    TerryTerrific Posts: 7, Reputation: 0
    New Member
     
    #3

    Mar 30, 2009, 08:21 AM
    Here is what a Rheem hot surface igniter looks like:

    The LEFT one is good.

    The RIGHT one is bad.

    http://www.myhvacparts.com/images/goodnbadignitor.jpg

    +

    Terence in Brook Park, oHIo
    jlbflower's Avatar
    jlbflower Posts: 2, Reputation: 1
    New Member
     
    #4

    Apr 1, 2009, 04:20 AM
    The service tech came and showed us that there is a 3rd resettable switch, in the flue, which is not shown on the diagram in the 8-page owner's manual. He said this is because this switch is only installed when the flue is vented to a masonry chimney, which is our case. My understanding is that switch is an additional BVSS (blocked vent safety shutoff). It tripped in our case probably because of the box fans that the contractor had going in the basement, causing a reverse flow in the chimney vent. He reset it and the furnace worked fine.

    Thanks for replying to my post. I'll check for cracked igniter in the event of future furnace problems.
    svanbschalkwyk's Avatar
    svanbschalkwyk Posts: 2, Reputation: 1
    New Member
     
    #5

    Jan 22, 2011, 10:03 AM
    What does one do when the ignitor is only getting 8VAC? Shouldn't it be 1209VAC?
    I'm getting Code 34, and I've done all the suggested bits. The only problem is the ignitor isn't glowing.
    Any ideas?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Gas Furnace will not ignite [ 9 Answers ]

I have a Goodman gas furnace, Modal no. GMP075-3. When the heat is turned on the blower motor turns on but the ignitor doesn't get hot or glow like it's getting hot. I don't think that the gas valve is opening as I have tried to light it with a open flame. Please help me, it snowed last night and...

Bryant 383KAV furnace won't ignite, fan blows cold air. [ 1 Answers ]

First we replaced the thermostat. Then we replaced the ingiter. Still only blows cold air? Any one know what the problem is? :confused

10 yr old bryant furnace doesn't always ignite smell gas [ 2 Answers ]

I have had a couple people look at my furnace and can't afford to pay the Bryant team! I replaced blower motor 2 years ago, furnace seems to run great once on, but when it kicks on sometimes I smell gas before and after cycles! I had to replace the inducer cooling fan, 3 weeks ago, now the smell...

Bryant Gas Furnace fails to ignite [ 3 Answers ]

My Bryant Gas Furnace occasionally fails to ignite. When this happens, I can reset it by turning the switch by the furnace off and on. It will then ignite after sparking for 30 seconds or so. The furnace has a pilot that is on and becomes large when the thermostat directs it to, but after sparking...