    slinke's Avatar
    slinke Posts: 4, Reputation: 1
    New Member
     
    #1

    Mar 3, 2009, 09:21 AM
    Is it safe to replacing a lighter gauge wire with a heavier gauge
    Hi all,

    One of my baseboard heater (240v)'s wire was broken can I replace it with a heavier gauge wire? Also can different gauge ground wires (copper wire) be connected with a wire-nut? IS THIS SAFE TO DO? OR Will this create a fire hazard?
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #2

    Mar 3, 2009, 07:59 PM

    You can replace with heavier gauge wire IF the insulation rating is the same or higher than the old. If you are working on heat, most likely the insulation will have to be rated for 105 degrees C.

    As to using a wire nut on the ground, it should be fine as long as: 1) You are not extending with lighter gauge wire. 2) You are using the correct size wire nut that is rated for that combination of wires. 3) The wire nuts are in a junction box or the wiring compartment of the heater.

    EPM
    patcolamp's Avatar
    patcolamp Posts: 16, Reputation: 1
    New Member
     
    #3

    Mar 3, 2009, 09:30 PM
    Slinke

    1. Yes, you can use a larger size wire. As long as you do not downsize the breaker size. Wire can be bigger than the breaker but the breaker can't be smaller than the rated wire size.

    2. Yes you can put a wirenut for connecting ground wires.

    I hope this helps you out.

    JP
    Patco lamp
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Mar 4, 2009, 08:02 AM

    Pat,

    Would you consider rewriting #1.

    "Wire can be bigger than the breaker but the breaker can't be smaller than the rated wire size."

    Obviously, you can put a lower amperage breaker on a higher rated conductor (30 amp breaker on a 40 amp conductor).

    What you cannot do is place a higher rated breaker on a lower rated conductor ( a 20 amp breaker on a 15 amp conductor).
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #5

    Mar 4, 2009, 09:39 AM

    What we should be asking, I think is is the proper wire size being used in the first place?

    You need to take the (total wattage)*1.25/240 to get the current and the wire has to be sized from there. The 1.25 is a derating factor that needs to be applied to space heating loads.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Mar 4, 2009, 11:18 AM

    I agree with KISS on getting the current size of the conductor.

    Please tell us what the wattage on the heater is. The information will be on the metal tag on the heater.

    From that we will be able to determine the correct size the conductors should be.

    Also, When you say. "use larger conductor" are you speaking about replacing the entire conductor run or just a small run of conductor near the break?

    If you are only replacing the broken section then you may not be doing a wise thing.
    slinke's Avatar
    slinke Posts: 4, Reputation: 1
    New Member
     
    #7

    Mar 5, 2009, 03:23 PM
    Quote Originally Posted by donf View Post
    I agree with KISS on getting the current size of the conductor.

    Please tell us what the wattage on the heater is. The information will be on the metal tag on the heater.

    From that we will be able to determine the correct size the conductors should be.

    Also, When you say. "use larger conductor" are you speaking about replacing the entire conductor run or just a small run of conductor near the break?

    If you are only replacing the broken section then you may not be doing a wise thing.
    Thanks for all the info so far... This is a fantastic forum!

    The Baseboard Heater Wattage is 1758

    Volt 230V

    Amp 7.6

    I'm just trying to replace the broken/burned RED wire that was twisted together(in a wire-nut) with the BLACK wire and wire-nut the broken ground wire with a slightly larger one.

    I've attached a picture of the baseboard.
    Attached Images
     
    slinke's Avatar
    slinke Posts: 4, Reputation: 1
    New Member
     
    #8

    Mar 5, 2009, 03:32 PM
    Quote Originally Posted by slinke View Post
    Thanks for all the info so far... This is a fantastic forum!

    The Baseboard Heater Wattage is 1758

    Volt 230V

    Amp 7.6

    I'm just trying to replace the broken/burned RED wire that was twisted together(in a wire-nut) with the BLACK wire and wire-nut the broken ground wire with a slightly larger one.

    I've attached a picture of the baseboard.
    Sorry guys... the broken/burned RED wire was twisted together with the WHITE wire not the BLACK wire.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #9

    Mar 6, 2009, 09:01 AM
    Okay,

    I must be blind because I cannot find any red wire in your picture.

    For baseboard heat, usually it is a straight 240 VAC. That means that you can actually use 14/2 (15amp).
    You would install the white wire to one input terminal and then re-identify the wire with black or red tape. Or some other permanent coloring to signify that this wire is no longer a Neutral wire. It is a live wire carrying power.

    Black would be connected to the other terminal of the heating element.

    BTW - The term, "De rating" applies to the reducing of the electricity flow in the circuit. It does not apply to the increasing of the electrical flow.
    slinke's Avatar
    slinke Posts: 4, Reputation: 1
    New Member
     
    #10

    Mar 14, 2009, 02:38 PM
    Quote Originally Posted by donf View Post
    Okay,

    I must be blind because I cannot find any red wire in your picture.

    For baseboard heat, usually it is a straight 240 VAC. That means that you can actually use 14/2 (15amp).
    You would install the white wire to one input terminal and then re-identify the wire with black or red tape. Or some other permanent coloring to signify that this wire is no longer a Neutral wire. It is a live wire carrying power.

    Black would be connected to the other terminal of the heating element.

    BTW - The term, "De rating" applies to the reducing of the electricity flow in the circuit. It does not apply to the increasing of the electrical flow.
    Eh... the RED wire is the missing burned/broken one which I'm trying to replace with a AWG 10 / AWM 600 volts vw1/ ANCE 90"C/194 F wire.

    Do you or anyone know if wires rated 194F is a safe replacement wire for baseboard heater?
    EPMiller's Avatar
    EPMiller Posts: 624, Reputation: 37
    Senior Member
     
    #11

    Mar 16, 2009, 02:15 PM
    Quote Originally Posted by slinke View Post
    eh... the RED wire is the missing burned/broken one which I'm trying to replace with a AWG 10 / AWM 600 volts vw1/ ANCE 90"C/194 F wire.

    Do you or anyone know if wires rated 194F is a safe replacement wire for baseboard heater?
    I think in this case you should get wire rated for at LEAST 105C (221F). 194F wire is 90C. Those heaters can get up around those temperatures. I know if it was mine I would use wire from the burners on an electric range. I don't know the exact temp rating, but you can't burn it with a torch. And if you are connecting it within a couple of inches of the heating element, use a ceramic wire nut.

    EPM
    AMPERE's Avatar
    AMPERE Posts: 4, Reputation: 1
    New Member
     
    #12

    Jan 17, 2013, 12:43 AM
    My rule is I never mix different gauge wires because of the national electrical code. Now to your question.

    Go to the breaker panel and carefully with one hand open the door and locate the breaker that serves this circuit. Please be careful because electricity is very dangerous.DO NOT REMOVE THE PANEL COVER. Just find the breaker that serves the circuit.

    The amps on the breaker will determine the size gauge wire to use on this circuit.
    If you can understand the nec and have one, the tables will show you the correct wire size according to the ampacity of the wire; otherwise, call an electrician. I do not write this to be unkind but only to be helpful. And if you should decide to work on this circuit, turn off the breaker and test the circuit.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What gauge wire do I use? [ 5 Answers ]

I'm wanting to run power from a 20amp breaker from my house to a small storage building 100ft away. All I want to run on this line is a fluorescent light and a small hand drill or small shop vac. What gauge wire do I use? 12 or 10ga?

Connecting 12 gauge and 14 gauge wire [ 4 Answers ]

Is it ever acceptable to attach 14 gauge to 12 gauge wire? I have a remodel situation where I have a 20 amp/12 gauge wired circuit powering outlets only. I want to tap off the end-of-run outlet to power an electric-venting skylight. The skylight comes with 14/2 wire. Can I tap off the 20 amp...

Wire Gauge? [ 7 Answers ]

I've been looking for 2 days for an online wire gauge calculator. I'm going to relocate my meter to the side of my house (converting from overhead to underground service), then I'm going to remove the existing electrical panel (from the outside of the house) and install a breaker panel on the...

Connecting 14 gauge wire and 12 gauge wires in the same blue box. [ 2 Answers ]

I am wiring my basement. All the outlets are running off 2 independent 20 amp circuit breakers connected to each other by 12/2 wire. I wanted to run some stubs off my 12/2 outlets. All each stub would do is run to a small light (max 180 watts) and of course a light switch. Since I ran out...

Gauge of wire? [ 1 Answers ]

Thank you for responding. I would like to know what size of wire I need to run a circuit 125 amp, 240V to a sub panel 244 feet away? Or, what size of wire I need to run a circuit 60 amp, 240V to a sub panel 244 feew away? Thank you in advance


View more questions Search