    Cold gas pipes=System lockout?
    I am having the following issues with my forced air gas furnace. It has a White Rodgers 50A55-843 board. The valve has "36E03 205" on it, along with a logo which looks like a "C" with an "A" inside of it.

    The majority of the time the furnace works. However some days in the morning I wake up and the furance is shut down. I got a blink code, but I'm not sure if it is either a "1" or a "Continuos Flash" blink code. Per the legend on the board, that means either "1: System Lockout" or "Continuos Flash: Flame sensed, 5 seconds without gas valve." Anyone know how to tell the difference?

    What I think is going on is that the basement gets cold, causing a loss of pressure at the gas valve.

    While testing it when it goes off in the morning, the forced draft motor starts, then the ignitor glows, then I hear a click at the board, followed by a 1 second pause, then a softer click, then an approximate 3 second pause, then one last click. The furnace will cycle like this 3 times before shutting off with the blink code described above.

    This morning I warmed the pipes going into the valve by just wrapping my hand around them. They were noticeably cold, and after about five minutes of "warming" the furnace is now lit and blowing hot air. I opened up the basement vent, and hopefully that will solve the problem. I had a technician come out a couple weeks ago and he said everything looked fine, replaced the air filter, and gave me a bill for $70.00.

    While testing, I also noticed a brown spot on the back of the control board. I replaced the control board last year due to a dark spot, but now I'm thinking it was a pressure issue all along. Are brown spots on the back of control boards a normal occurrence? It is not mounted, just hanging on the side supported by wires.

    Could it also be the flame sensor? I have 4 wires going into the heat exchanger. 3 wires go to the board, and 1 goes to the valve. The 3 that go to the board are black and white and yellow. I believe black and white are for the ignitor and yellow is for the flame sensor. The wire that goes to the valve is shiny and ductile, almost like solder. Are flame sensor's intermittent? If so, what is the proper way to get a voltage reading? Strip the wire and hook up a multimeter, then splice and tape?

    Thanks for looking. Any advice would help. I am contacting the technician again to look at the flame sensor and take a gas pressure reading into the valve, and also clean out the blower and look at the evaporator coil. However if his estimate is high, or if I think he is not taking a serious look at the problem like the last time I wouldn't mind doing it myself.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 4, 2009, 08:28 AM
    Is this natural gas or propane?
    citizum's Avatar
    citizum Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 24, 2009, 06:55 AM

    It's natural gas. The furnace is off again this morning. I am by the great lakes region of the northeastern part of the US, and we just had a warm front followed by a cold front. The basement seems warm, and the natural gas is working on my stove, and I'm getting the same blink code.

    I called up the owner of the HVAC company who sent the tech out here. He pointed out that there should be another flue for the forced draft motor going to the outside, and the technician who performed the original work put the wrong filter in the furnace. Does that have anything to do with the problem I'm seeing, which looks flame sensor or gas pressure related?

    Thanks.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jan 24, 2009, 07:05 AM
    work put the wrong filter in the furnance

    Should not make a difference with the problem you are having.

    He pointed out that there should be another flue for the forced draft motor going to the outside

    Usually the are 2 plastic PVC pipes intake and exhaust of the 90+ furnaces but as long as the exhaust is going outside all should be OK.

    Try cleaning the flame sensor with steel wool,Scotch Pad or sandpaper. Easy di=oes it if located around the ignitor since they break easy. Do not touch ignitor with your fingers. What is the exact brand and model of your furnace?
    Attached Images
      

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace codes--system lockout /check line clarity? [ 2 Answers ]

Our furnace is only blowing cold air and the blower will not shut off with the thermostat. The indicator light flashes 2 times-and the code thing says it means system lockout -check line clarity.:confused: The ignitors try to light but go out right away. Now it is flashing constantly meaning...

Low cold water pressure/how to flush pipes [ 5 Answers ]

I have a 7 year old house with two separate electric water heaters (both in attic) that service their respective sides of the house. One side of the house seems to have adequate hot/cold pressure and duration. The other has limited hot duration and next to no cold water pressure--hot pressure is...

Hot water in cold pipes and leaking pressure relief. [ 4 Answers ]

Hello, I have a problem with hot water coming out of the cold water lines. The problem is twofold. I have a recirculation pump that recirculates hot water back to the tank for instant hot water at all taps. About 6 months ago the pressure relief valve started leaking around a gallon of water over 2...

Hot and Cold Pipes Connected? [ 9 Answers ]

I am trying to replace an old sink in my bathroom. I shut off the cold water supply. What I thought was the hot water shutoff, however, did not shut the water off to the sink but shut off the hot water line at the point it connected to the COLD water line (after the line branched off to the...

Hot water comes out of cold for several seconds how do I trace pipes? [ 7 Answers ]

When I turn on the cold water in the kitchen sink, the first 30 seconds or so the water is hot. I believe there is a cross connection somewhere. Our home is only 2 years old. No plumbing has been changed since the initial construction. How do I trace the hot and cold water pipes in the basement...


View more questions Search