    Conduit size for MHF cable
    Hi -- What is the proper conduit size for installing 4/0-4/0-4/0-2/0 Mobile Home Feeder cable? The meter box is on a pole about 25 feet from the house. The cable is rated for direct burial, but I think I should run the whole way in conduit because of the rocky soil.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Dec 29, 2008, 05:18 AM
    I would use 3 inch Sch40 PVC conduit.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Dec 29, 2008, 07:31 AM
    3" would allow an easier pull, but 2-1/2" would work fine as well.
    Also, 3" will be harder to terminate in panels and enclosures. Most 200A equipment only has up to 2-1/2" factory knockouts.
    benaround's Avatar
    benaround Posts: 69, Reputation: 6
    Junior Member
     
    #4

    Dec 29, 2008, 04:51 PM
    Leadisheavy, You could always screen the rocks out of the soil for the bottom 6 inches!
    leadisheavy's Avatar
    leadisheavy Posts: 2, Reputation: 1
    New Member
     
    #5

    Dec 29, 2008, 11:21 PM

    Thanks for the info. I figured bigger would be better; I'll have to check on the knockout holes.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Dec 30, 2008, 11:57 AM
    Quote Originally Posted by leadisheavy View Post
    I figured bigger would be better;
    That is almost always a flawed philosophy.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wire size & conduit size for 60 am subpanel 150 from source [ 9 Answers ]

Indiana question: I want to install a 60amp subpanel 150 feet from the main panel. This is all exposed runs both inside and out in a commercial envirenement. What gauge and type of copper wire and what size conduit whould I use. How often should insert a junction box in the run. John

Cable/conduit lubricant for pulling new cable? [ 1 Answers ]

What is recommended lubricant for pulling cable through conduit?

How to size Conduit 6-3 [ 4 Answers ]

I have 2 6-3 for a 60ft run and 1 6-3 for another run. Question, what size conduit do I use. This circuit is for a tankless water heater. All will in my garage which is drywalled.

Do I need conduit to run a 220v cable through my cellar? [ 10 Answers ]

I'm running a 2-2/4 aluminum cable for a 220v circuit from my barn from the panel in my house. Once entering the home (from the 36" deep in-conduit run from the barn), I have to string the cable through the mechanical area (cellar) of the house, then through a center-home crawl space and then...


View more questions Search