    Make sure you have good ground.
    mwatersjr's Avatar
    mwatersjr Posts: 23, Reputation: 0
    New Member
     
    #22

    Jan 3, 2009, 05:55 PM

    Just ran a separate ground to the unit and it still does it.
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #23

    Jan 3, 2009, 09:07 PM

    Its 10 days later,, I hope its fixed by now, if not someone had a cold Christmas
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #24

    Jan 3, 2009, 09:14 PM
    Try this: disconnect and insulate the wire connected to "G" on the circuit board (probably green). If problem stops, look to thermostat.
    mwatersjr's Avatar
    mwatersjr Posts: 23, Reputation: 0
    New Member
     
    #25

    Jan 3, 2009, 09:22 PM
    KC13 - I will try that next.

    WMproop - Furnace works fine except for this weird electrical anomaly. Christmas was toasty warm in the house.
    mwatersjr's Avatar
    mwatersjr Posts: 23, Reputation: 0
    New Member
     
    #26

    Jan 3, 2009, 10:48 PM

    With "G" wire disconnected, issue still persists. The "G" wire is for the manual blower "on" signal from thermostat.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #27

    Jan 3, 2009, 11:18 PM
    You are correct, and you have eliminated one more possibility.
    wmproop's Avatar
    wmproop Posts: 3,749, Reputation: 91
    Ultra Member
     
    #28

    Jan 3, 2009, 11:30 PM
    Quote Originally Posted by mwatersjr View Post
    Have a new Goodman furnace that has a peculiar issue. The furnace will heat just fine and burners will shut off normally when set point is reached. After the burners have shut down, the blower will run for a minute or so then it seems as though it is given a signal to stop then immediately restart. The blower never stops turning and it wold be best described as someone turning off a light switch and turning it right back on again. After another minute or so the system shuts down as it should. What could be causing this electrical "bump" with the blower motor?

    Thanks,
    Mike Waters
    Lynnwood, WA
    If its new, can`t the installer help you to make things right?
    mwatersjr's Avatar
    mwatersjr Posts: 23, Reputation: 0
    New Member
     
    #29

    Jan 4, 2009, 09:56 AM
    Quote Originally Posted by wmproop View Post
    if its new,,can`t the installer help you to make things right?
    He is helping, but he is retired from the heating business and got me the furnace from the person who bought his business. He installed it for free and it cost me next to nothing. He is checking on Monday with his former business to see if they have seen anything like this with a Goodman. The tech I had come out to diagnose it said he had never seen this in 20 years.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #30

    Jan 4, 2009, 10:27 AM
    Exact model number of furnace?

    Exact brand and model of thermostat?
    mwatersjr's Avatar
    mwatersjr Posts: 23, Reputation: 0
    New Member
     
    #31

    Jan 4, 2009, 01:50 PM
    Model: Goodman GDH80904BXAC
    Thermostat: LUX 1500
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #32

    Jan 4, 2009, 02:28 PM
    Now try this. Disconnect all the thermostat wires in the furnace. Label them or mark down exactly where they go. Now use a jumper (piece of wire) and jump the W and R terminals only. This should bring on the heat. Let it run till the blower comes on then disconnect the R and W wires while it is running. The blower should shut off and stay off after the residual heat is blown out if my theory is correct if not nothing was lost or gained. If it does work I will tell you where to place a resistor.
    mwatersjr's Avatar
    mwatersjr Posts: 23, Reputation: 0
    New Member
     
    #33

    Jan 4, 2009, 03:16 PM
    Jumpered the R&W terminals like you said. Burners lit, then blower motor started. Removed jumper midstream and burners shut down. Exactly 30 seconds later, the "oddity" was once again heard. Blower continued to run for additional 2 minutes then shut down and stayed off. This has been the experience all along. Now, through this experiment, we have removed the thermostat all together from the equation as a possible bad component.
    MarkwithaK's Avatar
    MarkwithaK Posts: 955, Reputation: 107
    Senior Member
     
    #34

    Jan 4, 2009, 03:50 PM
    Quote Originally Posted by hvac1000 View Post
    If it does work I will tell you where to place a resistor.
    Voltage fluctuation in control circuit?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #35

    Jan 4, 2009, 07:15 PM
    Is that a LUX CAG1500 series thermostat OR a TX1500E Or a Smart Temp TX1500? There is no LUX 1500! Accuracy counts! If so it is one stage but your furnace is two stage but factory setup to use a one stage thermostat. Not that it makes a difference since all the wires were disconnected but two stage is good.

    For your future parts needs

    http://igate.northernplumbing.com/pa...anMfg/GDH8.pdf


    Notes:
    CFM in chart is without fi lter(s). Filters do not ship with this furnace, but must be provided by the installer.
    All furnaces ship as high-speed cooling and medium-speed heating. Installer must adjust blower cooling and heating speed as needed.
    For most applications, about 400 CFM per ton when cooling is desirable.
    INSTALLATION IS TO BE ADJUSTED TO OBTAIN TEMPERATURE RISE WITHIN THE RANGE SPECIFIED ON THE RATING PLATE.
    The chart is for information only. For satisfactory operation, external static pressure should not exceed value shown on the rating plate.
    The shaded area indicates ranges in excess of recommended maximum heating static pressure.
    The dashed (----) areas indicate a temperature rise not recommended for this model.
    The above chart is for furnaces installed at 0-2000 feet. At higher altitudes, a properly de-rated unit will have approximately the same temperature
    Rise at a particular CFM, while ESP at the CFM will be lower.

    Complete specs.

    http://www.heatandcool.com/v/GOODMAN...0/GMHspecs.pdf

    Warranty

    http://www.heatandcool.com/v/GOODMAN...80/GMHwarr.pdf

    This info provided so you can download to your computer for reference.

    At this point I have to say that Goodman might have a problem with there new style circuit board that is causing the motor situation.

    Contact by phone

    Goodman Manufacturing Co.
    2550 N.Loop W Ste. 400
    Houston TX 77092
    713-861-2500

    Talk to Russ Charles or Kim Zachary just do not mention me since they are private contacts within the company and I want no part of this discussion if you know what I mean. LOL You do not know exactly who I am anyway so you could not tell them I said to call. LOL

    Circuit board # 0130F00006S BOARD, IGNITION, HSI INTEGRATED, 2-STAGE

    Or PCBBF109S

    As in new numbers see link

    http://www.waroosevelt.com/dealers/s...INS/SF-020.pdf

    Goodman needs to send me checks instead of free equipment to test. LOL
    mwatersjr's Avatar
    mwatersjr Posts: 23, Reputation: 0
    New Member
     
    #36

    Jan 4, 2009, 08:32 PM

    The closest LUX I could find to what I have is the TX1500E. Mine looks an awful lot like it only the TX1500E looks newer, updated, but mine has the same buttons/switches on it. Mine literally only has printed on it the words - "Lux 1500".

    Are we sure my furnace is a two-stage and is it functioning as a two-stage? Now for the really ignorant question... what's a two-stage furnace as opposed to a single-stage one? The documentation on the TX1500E says it is not for use on a two-stage device.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #37

    Jan 4, 2009, 09:01 PM
    Your furnace is one of the newer type designs that is a two stage that is actually controlled by a one stage thermostat. When the furnace kicks on it operates on one stage then after a period of time/possible temperature pass it automatically switches to the second and final stage.

    A singel stage unit burns at one rate all the time but a two stage does not and by using the first stage most of the time it helps to save energy by having less stack/flue loss based upon the first stage lower gas consumption rate. This was developed so heating contractors would not have to pull a new thermostat wire containing a extra wire for the second stage and also the original or a cheaper one stage thermostat could be used. A pretty nifty idea if I say so myself.

    When you talk to Russ or Kim just tell them you have had a goodman service person check it out and it is still doing the motor thing. Then ask for there recommendations or advice so you can repete it to the service person. Unless they have some special posting on the factory site I could not find then I am going to guess it is circuit board time. OR if the retired HVAC guy or whoever calls them they can ask the same question but hopefully will sound more professional. They do not like to talk to homeowners that much.

    Do not worry about the thermostat at this point since we know by the disconnection of wires it is not causing this problem.
    mwatersjr's Avatar
    mwatersjr Posts: 23, Reputation: 0
    New Member
     
    #38

    Jan 7, 2009, 09:08 PM

    New furnace control board went in today and the problem did not go away. Will be calling Goodman soon to find out if this is really a design "feature". Ughh...
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #39

    Jan 8, 2009, 12:32 AM
    Your going to love the answer if they tell you it is normal. Good luck.
    mwatersjr's Avatar
    mwatersjr Posts: 23, Reputation: 0
    New Member
     
    #40

    Jan 19, 2009, 06:50 PM
    Ok, the jury has come back with a verdict. After finally getting around to consulting Goodman directly the answer is... drum roll please...

    It's normal! Tada!

    The kind gentleman explained that the sound is from the relay switching the blower motor from high speed to a lower speed during the cool down period. I even created a video of it and posted it to Youtube. Here is the link if you are interested in hearing the sound.

    Another weird thing which must be simply a matter of coincidence is that no matter when the furnace is started, and I mean no matter when, either automatically or manually by me, the main burners will always shut off when the second hand of my watch is at the quarter past the hour mark. It is most uncanny and I can't explain it even after dozens, yes dozens, of experiments trying the furnace at different times. You can see this happen in the video. Rod Serling must be involved somehow I'm convinced.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman furnace GMNT080-4 furnace runs good for a while then has to be manually reset [ 5 Answers ]

I have a Goodman GMNT080-4 (90%). I'm having the same problem As Streatherg did back in the Nov 2006 question. I reviewed his article and tried Every thing on there but seems to be doing the same thing. The furnace kicks on for about an hour then locks out and has to be manually reset threw...

Goodman furnace issue [ 5 Answers ]

Had a Goodman furnace model # GM 80903 BN installed a year ago, right from the start, the problem started with the burner not igniting when the blower moter is running continuously. I have to have the motor running continuously for the particular model of air-cleaner I have to work properly. So...

Issue with Goodman GMP series gmp 050-3 [ 18 Answers ]

Hello everyone, I have an issue with my furnace. It just recently started happening, when running the ac the unit gets to the set temperature and then the unit clicks as if where going off and clicks again and keeps running. I looked inside and didn't see the status light blink.. Any help here?

Goodman Heater issue [ 6 Answers ]

Hi I have GMP075-3 model of a Goodman gas furnace. The heater would make the sounds that it was beginning to work. I could see the ignitor light but then nothing else would happen. The repair guy came and said the Burner roll-out limit was somehow tripped the other day. Possibly from a down...

Goodman Furnace Issue - Heater won't work, no fire [ 1 Answers ]

My Goodman heater won't fire up. When I turn the heat on, the sequence of events: 1) Small fan at top section turns on. 2) Heating element turns on, bright red. The system sounds like it is trying to turn on. 3) Then the bright red goes off. The fire does not light. The fan does not start 4)...


View more questions Search