    Pvencius's Avatar
    Pvencius Posts: 6, Reputation: 1
    New Member
     
    #1

    Dec 11, 2008, 05:37 PM
    Variable speed settings
    New Goodman 95% V/S furnace s not cycling as the brochure stated. States it runs 90% of the time to circulate air. My contractor says to fun the fan on the ON position to achieve but that will make it run 100% of the time. When in the auto setting it seems to cycle similar to the old heater, on for a while then off, nowhere near the 90% like it is supposed to be engineered? Should it be set in manual vs auto and in auto should it run more often?
    MarkwithaK's Avatar
    MarkwithaK Posts: 955, Reputation: 107
    Senior Member
     
    #2

    Dec 11, 2008, 05:40 PM

    And here we go! VS motors are, in my opinion, more trouble then they are worth. I tend to shy my customers away from variable speed motors.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #3

    Dec 11, 2008, 08:42 PM

    I'm a big fan of variable speed equipment myself, and my home is equipped with such. I have seen a few failures over the years, but they were usually attributable to something external (moisture, incorrect voltage, etc.). Automatic vs. continuous operation is a matter of personal preference-if comfort is improved with continuous operation, then go with it. I do and the comfort level is much more consistent throughout my home, but this is not always the case. If you use the auto selection, the blower only runs during heating and cooling cycles. In the continuous mode the speed will ramp up during a cycle, then ramp down to a lower speed in between cycles. Variable speed motors typically convert the AC power supplied to DC, and at low speed measurable power consumption is greatly reduced. When I say measurable, I am referring to your electric meter-it is designed to measure power consumption in the form of a wide-band elliptical sine wave. Conversion to DC narrows and squares the sine wave, hence the meter doesn't recognize as much power consumption. P.S. I do not wish to discredit MarkwithaK's statements-variable speed is not necessarily for everyone, and perhaps he has seen a high failure rate in his area. Strange as it is, some things work well in some areas, not so well in others.
    Pvencius's Avatar
    Pvencius Posts: 6, Reputation: 1
    New Member
     
    #4

    Dec 12, 2008, 02:57 AM

    So the brochure "runs 90% of the time" is not correct?
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #5

    Dec 12, 2008, 04:34 AM

    Well, I would hope that the manufacturer knows their own product. They may have some quirk that varies from others, but the operating scenario I described before is pretty typical of most variable speed units. Does the brochure give any specifics on the other 10% when the blower might not run?
    Pvencius's Avatar
    Pvencius Posts: 6, Reputation: 1
    New Member
     
    #6

    Dec 12, 2008, 06:18 PM

    No
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Dec 12, 2008, 07:04 PM
    Strange as it is, some things work well in some areas, not so well in others.

    It has to do with power conditioning by the utility. Factory variable speed is junk and the price of replacement parts is out through the roof when it is out of warranty. I prefer the add on type since you just use the same standard 3-4 speed motor. Been using variable speed of the add on type for over 30 years and never lost a unit or motor because of it but the factory GE/Regal-Beloit setup that is in the variable speed units now by all the manufactures is just to expensive to repair. There is NO reason to convert to DC just for variable speed.
    MarkwithaK's Avatar
    MarkwithaK Posts: 955, Reputation: 107
    Senior Member
     
    #8

    Dec 13, 2008, 12:34 AM

    My point wasn't about the quality of VS motors but more in line with the cost of replacement/repair. I have priced a replacement VS motor from my supplier and at my cost you can damn near buy a new furnace... without a variable speed motor lol. Factor in markup and labor and that supposedly money saving device just cost you a butt load of money.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #9

    Dec 13, 2008, 12:46 AM
    Eventually there will be no savings with a factory variable speed setup. The replacement parts will take care of all that savings. LOL
    MarkwithaK's Avatar
    MarkwithaK Posts: 955, Reputation: 107
    Senior Member
     
    #10

    Dec 13, 2008, 09:50 PM

    I'm sure that sales reps will show a customer all the numbers outlining their potential energy savings but I would bet my last beer that nowhere in the companies literature do they layout the high repair costs of the units with variable speed motors.
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #11

    Dec 14, 2008, 09:23 AM

    Whoosh! What was that? Look! Up in the sky, it's.. it's... VARIABLE SPEED MAN! Yes, Variable Speed Man, defender of the virtues and benefits of variable speed HVAC equipment. Together with Bryantman, he battles the forces of skepticism and discomfort...
    Pvencius's Avatar
    Pvencius Posts: 6, Reputation: 1
    New Member
     
    #12

    Dec 14, 2008, 10:15 AM

    Guys, Thanks to all for your comments but the main questions have yet to be answered as with my contractor. Are these units that new that we really don't know how they are supposed work? If the 90% run time per the MFG is supposed the be achieved in the auto setting why can't that be without running in the ON mode which again is 100% run time? The point of repair costs is appreciated but I'm beyond that now and just want the unit to run the way it is engineered.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #13

    Dec 14, 2008, 10:24 AM
    The difference between 90% and 100% is a no contest overview. Is the 10% really bothering you? The reason I say that is brochure's have been known to be wrong. Get the installers manual if you really want the strait story. Post the Real/Exact model number and I will see if I can find one on the main frame. I might get lucky and find one but no guarantee.
    Pvencius's Avatar
    Pvencius Posts: 6, Reputation: 1
    New Member
     
    #14

    Dec 14, 2008, 06:14 PM

    Thanks... GMV950704CX. Look forward to your reply.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #15

    Dec 14, 2008, 06:39 PM
    Quote Originally Posted by Pvencius View Post
    Thanks...GMV950704CX. Look forward to your reply.

    Goodman variable-speed furnace runs 90%
    of the time in the low-heat capacity on most days,
    but when the weather is very cold, ramps up to
    high-heat capacity so that your family stays
    warm and snug.
    QUIET OPERATION
    Your Goodman High-Efficiency Furnace uses
    a multi-speed induced draft blower motor and
    variable-speed circulating blower to reduce the
    noise levels common in other furnaces. Since this
    unit runs in low-heat stage 90% of the time, the
    impact of the normal high-fire sound is eliminated
    90% of the time. Add to that a fully insulated,
    heavy-gauge steel cabinet, and the result is…
    extra-quiet comfort.
    YEAR-ROUND
    ENERGY SAVINGS
    Energy efficiency

    All it states is when the unit runs it will be in the low stage heat mode 90% of the time. The blower is not to stay running 90% of the time just the furnace WHEN it has a call to run.

    Here is a link to the paper you were talking about.

    Your furnace is operating properly.

    https://www.acwholesalers.com/EasyEd...95brochure.pdf
    Pvencius's Avatar
    Pvencius Posts: 6, Reputation: 1
    New Member
     
    #16

    Dec 16, 2008, 02:42 PM

    Thanks to all!
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #17

    Dec 16, 2008, 03:07 PM
    Yep
    MarkwithaK's Avatar
    MarkwithaK Posts: 955, Reputation: 107
    Senior Member
     
    #18

    Dec 16, 2008, 07:13 PM

    So can we go back to VS motor bashing now? Lol
    KC13's Avatar
    KC13 Posts: 2,556, Reputation: 99
    Ultra Member
     
    #19

    Dec 16, 2008, 07:17 PM

    Perhaps an online roundtable debate... with mudslinging and everything!
    MarkwithaK's Avatar
    MarkwithaK Posts: 955, Reputation: 107
    Senior Member
     
    #20

    Dec 16, 2008, 07:19 PM

    No mud in NW Indiana. But w are getting a nice snow fall right about now. How about a snowball fight instead of the mudslinging?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Variable speed on York Air Handler [ 1 Answers ]

I have a york air handler (no heat pump) and I have the motor on low (just have to move a wire to change from L,M,H) I was wondering if changing the motor speed to Med or High might help move the air better and make up for better efficiency and help not to be so cold in here at night. I just...

AccuClean and variable speed [ 2 Answers ]

Hello I just had a Freedom 80 variable speed furnace installed along with a 14 SEER AC unit and opted for the AccuClean. As soon as the installer left, the red light came on my AccuClean stating that the filter is dirty. It obviously isn't since everything is brand new. I called the installer...

Variable fan will only run on low speed [ 3 Answers ]

We have a Sears air conditioning condensing unit ( model # 867816840) It was working great and then all of a sudden nothing. We have power to the unit, the fan turns on but at a very slow rate. We have power to the contactor, sounds like the compressor runs. The fan motor blade moves freely....

Variable Speed vs. Single Speed Blower [ 1 Answers ]

Questions: Getting 2 new heat pump systems installed. 1.5 ton upstairs and 4 ton downstairs. Decided on Comfortmaker. Heat Load calc performed on sizes. Going 2 stage with variable speed downstairs with Honeywell IQ Pro stat. Was going to go one stage with variable speed upstairs with...

Replace air handler with variable speed [ 1 Answers ]

I want to know if I can replace a standard air handler on a 5 ton system with a variable speed air handler without replacing the outside unit. The electronics on the air handler will be different but does the compressor work full time or not.


View more questions Search