    bryantfurnacer's Avatar
    bryantfurnacer Posts: 48, Reputation: 3
    Junior Member
     
    #21

    Dec 10, 2008, 10:16 PM
    OK, going to do that now. I'll be right back.
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #22

    Dec 10, 2008, 10:16 PM
    I'm going to take you through a few steps and see if we can figure it out.
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #23

    Dec 10, 2008, 10:25 PM

    Any luck?
    bryantfurnacer's Avatar
    bryantfurnacer Posts: 48, Reputation: 3
    Junior Member
     
    #24

    Dec 10, 2008, 10:37 PM

    Hey Hvac
    I did what you suggested, took the black rubber tube off the furnace, and water poured out of it, and also came out of the furnace front. It is still coming out, so I want to go back down there, I have it going into a little water bottle.
    I was surprised to see water coming out. Did I do something wrong?
    bryantfurnacer's Avatar
    bryantfurnacer Posts: 48, Reputation: 3
    Junior Member
     
    #25

    Dec 10, 2008, 10:40 PM
    At least the water is nice and warm.
    bryantfurnacer's Avatar
    bryantfurnacer Posts: 48, Reputation: 3
    Junior Member
     
    #26

    Dec 10, 2008, 10:45 PM

    OK, I think it is done draining. I think at least 3 cups of water came out of the front of the furnace.
    Do I plug it back in now?
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #27

    Dec 10, 2008, 10:45 PM

    No,you unhooked the drain not the pressure switch tube,but that's OK
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #28

    Dec 10, 2008, 10:47 PM
    Try blowing through the tube you have unhooked,is it restricted?
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #29

    Dec 10, 2008, 10:48 PM
    The pressure switch tube is about a 1/4 inch rubber tube. Lets skip the pressure switch for now. Hook the drain back up.
    bryantfurnacer's Avatar
    bryantfurnacer Posts: 48, Reputation: 3
    Junior Member
     
    #30

    Dec 10, 2008, 10:48 PM

    Oh,
    I tried to blow through it. I heard a tiny pop, then nothing. I can't blow through it.
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #31

    Dec 10, 2008, 10:50 PM

    What is the other end connected to?
    bryantfurnacer's Avatar
    bryantfurnacer Posts: 48, Reputation: 3
    Junior Member
     
    #32

    Dec 10, 2008, 10:51 PM

    It comes out the back of the pressure switch and goes into the front of the furnace right at the bottom of the main compartment, it goes into a flat black plastic plate that is on the front of the furnace.
    I didn't see another tube that went from the pressure switches to the front of the furnace. Maybe I'm not understanding what you mean.
    bryantfurnacer's Avatar
    bryantfurnacer Posts: 48, Reputation: 3
    Junior Member
     
    #33

    Dec 10, 2008, 10:56 PM
    I'm looking at my diagram of the furnace. The tube come sout of the back of the pressure switch, goes to the side of the heat exchanger I think it is and plugs into the wall that is at the front of the furnace, right at the bottom, inside the main compartment. I wish I could upload a picture so I could show you.
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #34

    Dec 10, 2008, 10:57 PM

    Do you see the inducer fan? Located in the top compartment of the furnace.
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #35

    Dec 10, 2008, 10:58 PM
    You can upload a photo,that may help.
    bryantfurnacer's Avatar
    bryantfurnacer Posts: 48, Reputation: 3
    Junior Member
     
    #36

    Dec 10, 2008, 10:58 PM

    Is that the big round plastic cover right behind the inducer motor? I see it
    bryantfurnacer's Avatar
    bryantfurnacer Posts: 48, Reputation: 3
    Junior Member
     
    #37

    Dec 10, 2008, 11:00 PM
    OK, let me geta good photo, b right back
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #38

    Dec 10, 2008, 11:01 PM

    Do you see any small tubes going to the inducer fan?
    bryantfurnacer's Avatar
    bryantfurnacer Posts: 48, Reputation: 3
    Junior Member
     
    #39

    Dec 10, 2008, 11:13 PM

    Hi,
    I have my photo, don't see how to upload it. Let me go look at the inducer fan again. I don't remember a little tube.
    hvacservicetech_07's Avatar
    hvacservicetech_07 Posts: 1,083, Reputation: 75
    Ultra Member
     
    #40

    Dec 10, 2008, 11:19 PM

    Hit the go advanced button at the bottom, you cadd attachments

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bryant Plus 80 Error code 33 [ 3 Answers ]

Hello! I'm new on here so bear with me. I found a similuar post on the Bryant 80 but I believe I have a different model... not sure how much that matters. The only model number I could find on the unit was CK5AXA036017AAAA The Error code is 33 Limit or flame roll out switch is open. The furnace...

Bryant plus 80 code 33 and cycles [ 8 Answers ]

Hi, I've got a ten year old bryant plus 80 furnace that, reads a code 33 while it cools, it is a solid while fired up but it constantly cycles. I've checed the condenser it looks clean on both top and bottom , filter is clean, all returns are open. Would making anouther return somewhere in the...

Bryant Plus 80 Code 33 [ 10 Answers ]

I have a Bryant Plus 80 that is throwing a error of 33 (limit or flame roll out switch is open). The last time this happened was because the hot surface igniter was broken (frequent problem as my furnace has a tendency to short-cycle). I had picked up a couple extra ones so I had them on hand to...

Still have error code on Bryant gaspac 8 flashes [ 6 Answers ]

For Northernheat Still getting code of 8 led flashes. Have checked the flame sensor not cracked or touching anything and is in the flame. The only time that it seems to happen is when the temp gets colder like 32/34 after being 38/40. The LED error code states Internal control fault ...

Bryant 383KAV error code 34 [ 1 Answers ]

After reading a couple of posts, I cleaned the flame sensor. When that didn't work, I bought a new one and installed it. I am still getting the same code. The burner lights for approximately 3-5 seconds, then cuts off. The thermostat is calling for heat. What am I missing?


View more questions Search