    I need to slow down the blow on my concord furnace
    I just installed a add-on wood/coal furnace that works really good... The problem that iI am having is that the gas furnace that I added on to has too much air pressure... I need to step the fan down but I do not know how to do that... It is a newer furnace... It is a Concord 90 plus model number CG90UA125D20D-1... I have know idea where I put the darn installation manual I have been lookig for it for weeks.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Nov 18, 2008, 12:41 PM
    The problem you are going to face is that the furnace manufacturer requires a minimum of air flow across the heat exchanger in that new furnace. If you just start lowering the blower speed it could damage the furnace and no warranty will cover this damage. Try to find another solution first then if the blower speed needs to be lowered still contact a HVAC company so they can check to make sure the correct heat rise and flow requirements are met so no damage to your new furnace happens.
    painterdude2900's Avatar
    painterdude2900 Posts: 6, Reputation: 1
    New Member
     
    #3

    Nov 18, 2008, 01:00 PM

    Yes I know... I just need to slow it down because it is over powering the blower on the wood furnace... The gas furnace is not hooked to a fuel line...
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Nov 18, 2008, 05:27 PM
    Just look at the wiring diagram on the back of the blower door. It has the motor wiring on it.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #5

    Nov 18, 2008, 05:32 PM

    If your wood burner has a blower, why are you using the central system blower at all? If the central blower is overpowering the wood blower, most likely you will not be able to slow the central blower enough to remedy this problem.
    painterdude2900's Avatar
    painterdude2900 Posts: 6, Reputation: 1
    New Member
     
    #6

    Nov 19, 2008, 06:14 AM

    It is a add- on wood furnace... The blower on the wood furnace is only to get the heat to the plenum of the gas furnace... The blower on the gas furnace forces the hot air through the house.In the installation manual for the wood furnace it did say that I might have to step the blower speed to med. To low speed...
    painterdude2900's Avatar
    painterdude2900 Posts: 6, Reputation: 1
    New Member
     
    #7

    Nov 19, 2008, 06:17 AM
    Quote Originally Posted by hvac1000 View Post
    Just look at the wiring diagram on the back of the blower door. It has the motor wiring on it.
    Thank you very much!
    painterdude2900's Avatar
    painterdude2900 Posts: 6, Reputation: 1
    New Member
     
    #8

    Nov 20, 2008, 06:21 AM
    I was able to slow down the speed on the Concord furnace... Now we are getting the heat through out the house that we needed... Thank you very much!
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #9

    Nov 20, 2008, 10:26 AM
    Good deal.
    KidChaos's Avatar
    KidChaos Posts: 45, Reputation: 3
    Junior Member
     
    #10

    Sep 29, 2013, 03:19 AM
    Heat uses low speed already, Cooling is the high speed, unless you have medium speed on heat now there is no way to slow the fan down.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Concord Gas Furnace [ 2 Answers ]

I have a Concord Gas Furnace Model CG90UB... it currently is wired to run the fan on low speed which I find is not adequate to move the air around the house... I would like to know how to change the fan speed to run on medium... the manual states there are four speeds... Low, Low Medium, Medium and...

Concord 80 plus furnace [ 2 Answers ]

I have a concord 80 plus that is mounted horizontally. The pilot light turns on, the gas ignites, but will only stay lit for a few seconds. It will try this three or four times before the blower shuts off. The thermostat works fine (atleast it did for ac). Any suggestions?

Concord 80 plus gas, furnace [ 5 Answers ]

Hi, glad to find some help, I found your site by accident,or my good fortune! I have a concord 80 , the thermostat clicks and the blower comes on but the furnace does not light,all help appreciated

Concord 80 plus furnace [ 2 Answers ]

I am wondering how many BTu this furnace is? I can not find it anywhere. Thanks!

Concord furnace? [ 1 Answers ]

I have a concord furnace model # rgu90a100d14-3a and was wondering what the cfm for this unit is?


View more questions Search