    novice68's Avatar
    novice68 Posts: 22, Reputation: 1
    New Member
     
    #1

    Nov 11, 2008, 07:02 PM
    Gas Not kicking in on Carrier Weather Maker 8000
    I have a Carrier Weather Maker 8000 for which heating has refused to start this winter :mad: . On checking the error codes comes out to be 21 which states gas blockage. One of the suggestion was to shut off the heater and let it reset which has not helped. (Left it Off for the whole night but when started the next morning, it still did not start! :( ). The blower starts for 90 sec then the exhaust (I believe - the fan on the upper side) kicks in and the ignitor (thing that glows red) comes on but since gas fails to come, it glows for few seconds and then turns off. Any suggestion would be appreciated.

    I checked again today and from what I can gather, the error code is 12 and not 21. The error code 12 translates to "blower on after power up" or "R-W Closed". I have no idea what all this means and how R-W Closed can be reset to Open. Any help would be greatly appreciated.

    Thanks
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Nov 11, 2008, 08:53 PM
    Check this post.

    https://www.askmehelpdesk.com/heatin...-a-182116.html
    novice68's Avatar
    novice68 Posts: 22, Reputation: 1
    New Member
     
    #3

    Nov 12, 2008, 07:46 PM

    I read the answer and they following made sense to me
    "You might have a reset button at the top of the furnace near the flue pipe that you can reset by pushing in at the center of the little circular button. If not, then the pressure switch may be faulty, or more likely the vent (flue) is restricted or clogged in some way. Other more in depth tests probably need a tech to determine the cause. Unfortunately this particular furnace was noted for numerous safety features, which on occasion become stuck or malfunction. However, when they are needed, they may save your life, so we tolerate the inconvenience."

    However I am not sure what "flue" pipe is and what circular button is being described/mentioned. Is it something on the gas controls?

    Thanks,
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Nov 12, 2008, 11:22 PM
    No a reset button near the top of the furnace. It is a high limit safety control. The flue is the pipe that goes outside.
    novice68's Avatar
    novice68 Posts: 22, Reputation: 1
    New Member
     
    #5

    Nov 13, 2008, 10:05 AM

    I found (I guess) the reset button. It is a button that is sticking to the top of furnace with two wires going in and in the middle is the switch sticking out. I pressed the button couple of times before stating the furnace but it did not do any thing different. Then I pressed it during the period when the furnace started to run. It did not help either. One thing I noticed was that before starting the code indicates 12 (one small and two long blinks), however after the ignition fails the code switched to 21 (two small and one long blinks). I guess this confirm the blockage of gas. I have turned the gas control on and off just to see if that might help but to no avail.
    As far as flue is concerned, that does not seem to be the problem, I have not opened it as yet. However the blower motor seem to run fine and it does not make any sound if the passage is blocked/partially blocked.
    Any suggestion how the gas blockage can be removed.

    Thanks
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Nov 13, 2008, 10:32 AM
    Are you sure you have gas and it is turned on to the home and furnace. Stupid question but I have run into this problem before. LOL


    Use a meter and see if the gas valve is getting voltage during a unit start up. This info will help isolate the problem.
    novice68's Avatar
    novice68 Posts: 22, Reputation: 1
    New Member
     
    #7

    Nov 13, 2008, 04:12 PM

    Basically I have two units, one for upstairs and the other for downstairs. Both are being fed by the same line. (One gas line splits into two). One is working and the other one is not. Since one is working I am assuming the gas is coming to the unit that is not working.

    As for the current coming to the gas value is concerned, I have not checked that.

    There are two wires going into gas valve (gas regulator), one of these (dark green) is connected to the body of unit and the other end is going to circuit board. (Kind of makes a "V", bottom of "V" going to gas valve, one top end going to board and the other going to body). I guess I do not have to check availability of current in this wire as it seems to be a wire making the ground connection. The other light green wire is coming from the board, which I guess I need to check if any current is flowing through it. Right?

    Thanks once again.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #8

    Nov 13, 2008, 05:06 PM

    Carrier furnace will run blower motor for roughly one minute(when powered up during a call for heat) After the minute is up, the blower motor should turn off, and the combustion blower(upper motor) will come on, starting the actuall call for heat. A short time after the combustion blower(also called a draft inducer) comes on, your glow plug starts to glow, a short time after this happens, your gas valve should open, creating flame.

    Do you have one pressure switch or two? Check for votlage at the gas valve after the glow plug has began to glow, as hvac stated, you should get a reading of roughly 24v before the glow plug turns back off. Let us know what you find,
    novice68's Avatar
    novice68 Posts: 22, Reputation: 1
    New Member
     
    #9

    Nov 15, 2008, 03:08 PM

    First of all my apologies for the delayed response. I did not have had a volt meter and now I have bought one.
    By the way the wires going in the gas valve are not dark green and light green but green and blue. Green is connected to the ground and the blue is other wire.
    Here is what is happening. I am getting 24 volts going in gas value as soon as I start the heater - I checked this by disconnecting the blue wire and connecting one end of volt meter to the blue and other to the gas valve where the blue wire is suppose to be connected into gas valve. However when I connect blue wire back to the gas valve and then connect one end to volt meter and the other end to green wire, I do not get any reading.

    I hope I am doing what you are asking me to do for checking the voltage. Does it give you any idea?

    Thanks
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #10

    Nov 15, 2008, 04:03 PM

    Can you take a picture of your gas valve and the leads going to it. If you can, please post it here.
    novice68's Avatar
    novice68 Posts: 22, Reputation: 1
    New Member
     
    #11

    Nov 15, 2008, 08:12 PM

    Here are some pictures.









    Hope these help.
    MarkwithaK's Avatar
    MarkwithaK Posts: 955, Reputation: 107
    Senior Member
     
    #12

    Nov 15, 2008, 08:36 PM

    I see nothing.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #13

    Nov 15, 2008, 09:44 PM
    I see little boxes with X in the middle.
    novice68's Avatar
    novice68 Posts: 22, Reputation: 1
    New Member
     
    #14

    Nov 15, 2008, 10:18 PM

    Well, I see the real "pictures" that I added. May be since I added these, therefore I can see them. What is the normal way of adding pictures here? As I try to add pictures here, it asks for a URL for the location of picture. I have uploaded pics to my Kodak Gallery and given the link of that location. How else should I add images here?

    Thanks
    novice68's Avatar
    novice68 Posts: 22, Reputation: 1
    New Member
     
    #15

    Nov 16, 2008, 03:56 PM

    Okay, Now I do not see the pictures as well. :) So I am in the same boat as everyone else except, my boat is freezing (LOL). I will wait until morning to see if someone can guide me how I can add pictures here. So far I have not been able to find either in help or via searching the web site that would guide me to add pictures here.
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #16

    Nov 16, 2008, 05:36 PM
    If you don't get a glow from the hot surface ignitor it may be burnt out. If you have a open limit. The blower will stay on until the limit is closed. If you have a call for heat or cool from the thermostat on power up of the furnace blower will run for 90 sec. and then the call for demand will start to work
    novice68's Avatar
    novice68 Posts: 22, Reputation: 1
    New Member
     
    #17

    Nov 17, 2008, 10:33 AM

    I am not sure what you mean by open limit. When I start the heater, it indicates error code 12, the blower gets on which does go off after about a minute or so then the combution blower kicks in, the ignitor lights on but the gas refuses to come on. The ignitor glows for 10 to 15 secs and then since the gas does not come on, it switches off as well as the combustion blower switches off and at this point I get the led code 21.

    Still trying to find how I can add pictures here. :confused:
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #18

    Nov 17, 2008, 05:03 PM

    Do you have one pressure swtich or two? Pressure switches will have a small orange, white, grey, or black (roughly 1/4 inch diameter) rubber hose connected to them. Please answer this question, may be a start to solving your problem.
    novice68's Avatar
    novice68 Posts: 22, Reputation: 1
    New Member
     
    #19

    Nov 18, 2008, 09:49 AM

    I am not sure if I have any pressure switch. I do not see any rubber pipes of any color.
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #20

    Nov 18, 2008, 04:31 PM

    I would be willing to bet that you have at least one pressure switch.

    If you have two, one will most likely let the glow plug come on, and the other pressure switch will allow the gas valve to open.

    Seems like there should be three wires at gas valve. Should be 24v between hot and neutral when time for gas valve to open. The green ground is just that, a ground. Are you sure there isn't a wire that has come unhooked at gas valve. Look for any dangling wires that aren't hooked to anything.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Carrier Weather Maker 8000 Model 58ZAV [ 4 Answers ]

How can I get the LED codes for the Carrier 58ZAV? I don't have the manual. The unit won't run and is flashing a 2-4 code.

Carrier weather maker 8000 [ 6 Answers ]

Hi everyone. I am new to this forum and would like your help. I have a Carrier Weather Maker 8000 and I am having problems with it. Its keeps shutting off before it reaches the desired temperature . I made a couple of clips that I hoped would explain the problem better. The Start:...

Carrier Weather Maker 8000 Gas/2HR before Fun. Turns on set at 75 [ 6 Answers ]

Hello! Turned on furnace this year every thing was fine. Then I noticed that the temp in the house was 68 & the desired temp was set at 72. Then I set it up on 75 still did not turn on. About 2hr later the furnace turned on & shut off at 75. Every thing seemed fine. It turned on and off like was...

Carrier weather maker 8000 [ 5 Answers ]

Model # 58TUA06008 has had the main board replaced but it keeps shuting off and then will restart after four hours or if I shut the power off and turn it back on. Is this an issue with the heat sensors or something else. I known the main board has been recalled is there any other issues. Thanks G