    genewilson's Avatar
    genewilson Posts: 6, Reputation: 1
    New Member
     
    #1

    Nov 6, 2008, 09:23 AM
    Spa wiring 4 wire with gfci confussed!
    Planning to hook up new spa with a pony or sub box as they call it, was thinking about just putting in a ground rod at the sub box for my ground and nuetral lines, that would save me from buying another 140 ft. of wire, but was reading at another site that the ground and the nuertal wire from gfci couldn't be hooked up on the same bar in the box or would trip the gfci. If I pulled all 4 wires from the main box the ground and nuetral are on the same bus bar anyway. They were saying pull all 4 wires from the main,and at the sub box bond the grounds at the sub box ,and hook gfci nuetral to nuetral bar, if the ground and the gfci nuetral were at the same bus bar then the gfci would trip. I don't understand this since in the main box the ground and nuetral wires are on the same bar anyway, so in the long run they are still connected. Can any one help I confussed??
    Thanks, Gene
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Nov 6, 2008, 12:24 PM

    I'm confused too. Don't know if you have a 240 3 pole 4 wire spa with a spa box or what you have.

    A low impeadace ground does not come from ground rods. It's primary purpose is lightning protection, but in case of a pool/spa 140' away it serves another purpose. It makes the exposed parts at an equal potential.

    Neutrals and grounds stay separate at sub panels.

    A 240 V GFCI breaker has a load neutral and a panel neutral, so it effectively has two neutral connections. One connects at the source and one is the load neutral.

    GFCI protection basically comes out in the wash because when you twist L1 and L2 in the same direction with N, the currents cancel unless there happens to be a path to ground.

    GFCI's also check for ground/neutral shorts after the initial connection at the GFCI in another way.

    For 120 ckts, it's easy to explain: A small AC current is modulated on both the neutral and hot leads. The difference is measured directly by a transformer. If any difference is found, you have a neutral to ground short because you would not be able to modulate ground.
    genewilson's Avatar
    genewilson Posts: 6, Reputation: 1
    New Member
     
    #3

    Nov 6, 2008, 12:48 PM
    It's a 240 v 50amp breaker , which consists of two hots 115v. If I run both hots , the nuetral, and ground out of the main breaker but keep the ground and nuetral separate at the sub panel , then the ground and nuetral line will come back into the main breaker on the same bus bar, and this is OK, will not trip the gfci.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #4

    Nov 6, 2008, 12:57 PM

    True.

    The GFCI breaker is in the SPA panel or main panel? I'm also assuming that the SPA panel and sub-panel are one in the same.
    genewilson's Avatar
    genewilson Posts: 6, Reputation: 1
    New Member
     
    #5

    Nov 6, 2008, 01:50 PM
    Yes , the spa panel and the sub panel are the same, and the gfci will be installed in the sub-panel
    genewilson's Avatar
    genewilson Posts: 6, Reputation: 1
    New Member
     
    #6

    Nov 6, 2008, 01:57 PM
    If I just bring the two hots from the main , and put a grounding rod next to the sub-panel and connect the rod to the bus bar in the sub for nuetral and ground wires , it wouldn't be a grounded loop and work the same as if I had pulled the neutral and ground from the main, and had kept them separate in the sub. True?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #7

    Nov 6, 2008, 02:08 PM

    Won't work. Trust me.
    genewilson's Avatar
    genewilson Posts: 6, Reputation: 1
    New Member
     
    #8

    Nov 6, 2008, 02:23 PM
    Thanks, I'll stick to pulling all 4 lines, from the main, and keep the ground and neutral seprate in the sub-panel, I should learn by now that my short cuts always cost me more in the long run (darn I hate to admit my wife is right). Thanks for your help.
    I heard from one of my old neighbors that he yanked his meter out and connected the two hots right on the paying side of the meter. Then went to has spa box 10 feet away, so I figured the only way he hooked his spa box gfci was through a grounding rod. At his spa box.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #9

    Nov 6, 2008, 03:27 PM

    Remember to tape the ends the correct wire colors and use conduit for a SPA.
    genewilson's Avatar
    genewilson Posts: 6, Reputation: 1
    New Member
     
    #10

    Nov 6, 2008, 03:28 PM
    Thanks again, keep it simple

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

GFCI breaker w/ 2-wire outlet [ 1 Answers ]

Will a GFCI breaker in the service panel protect a branch circuit without a ground wire? I recently installed a 20a GFCI breaker in my daughter's older home to protect three duplex receptacles - two in the kitchen and one outside the back door. I then discovered that the outlet outside is only a...

GFCI breakers when circuit lacks a ground wire. [ 1 Answers ]

Greetings, My home, built in the early 1950's, is wired with a 2 wire conducter lacking the ground wire. I believe it is 14 ga. My question is , would installing GFCI breakers provide protection from shock and fire, or would a more costly repair be in store? Thanks Sparky, Timashinkle

Spa GFCI wiring [ 0 Answers ]

Here is a visual. Full size it to read the print. Make sure to use correct wire size for load, distance and location conditions. Copper is not cheap, neither is safety it has a heaftier price. Find the name on hot tub "control pack", not hot tub "Brand" Some may only be three wire hook up...

Wiring a gfci [ 1 Answers ]

I need to wire a gfci breaker in my house for my hot tub can you run me through it

Spa and GFCI wiring [ 1 Answers ]

I have a 240 amp line that is powering a hot tub installed before I bought the house. The line comes off the main panel in the house through a 50 amp breaker and is routed through a 30 amp GFCI and then to the tub. Pushing the test button on the GFCI does not trip the GFCI. Likewise, manually...


View more questions Search