    rasco847's Avatar
    rasco847 Posts: 49, Reputation: 1
    Junior Member
     
    #1

    Oct 27, 2008, 09:49 AM
    Rheem rgaa-150c-fr
    Hi my name is Omar and am having a problem w/our furnace.It's a package unit, natural gas and is 20+ yrs old When I turn it on(heat) I can hear the thermostat click but nothing turns on(burners or fan, but when I turn on the AC the fan turns on). I opened up the side panel where the gas valve and burners are and noticed the pilot is out (also I noticed some build up on thermocouple and pilot, it looks like mildew? I'm not sure if this is a concern), is this supposed to be out? I hope this is a common problem and someone could help
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Oct 27, 2008, 12:22 PM
    All problems a common at one point or the other. There should be a wiring diagram on the back side of the blower door that can help you track down the problem.

    You ned to find out if you have spark ignition or another type. Then you need to find out why it is not activating upon a call for heat

    Since the unit is 20 years old the gas valve brand and part number along with the controler/spark box brand and model number will be a help since I do not have a listing on your unit.

    Does the glow coil or sparker try to light the furnace?

    Is there power going to the spark box?
    rasco847's Avatar
    rasco847 Posts: 49, Reputation: 1
    Junior Member
     
    #3

    Oct 27, 2008, 02:17 PM

    Thanks for your response, hvac. I'll get the information on the parts when I get home(at work), but am wondering where is the spark box located? I only saw a transformer, fan limt switch, gas valve, thermocouple and pilot... I didn't know there was a diagram on the back cover, but like I said I'll get you the info when I get home... thanks again
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Oct 27, 2008, 03:41 PM
    It is possible there is no spark unit. It could just be a old fashion thermocouple safety design that you have to lite the pilot with a match.

    Sometimes the pilot orifice will get plugged up and it will have to be taken apart carefully and cleaned. If the nut is hard to turn spray with WD-40 or you will twist the aluminum tube and be buying a new one. The pilot orifice is VERY SMALL. DO NOT jam something bigger in the hole or you will need a new orifice also. A very small strand of wire should fit the hole but if not find something small to fit the hole so as not to cause damage.
    rasco847's Avatar
    rasco847 Posts: 49, Reputation: 1
    Junior Member
     
    #5

    Oct 27, 2008, 03:59 PM

    I'm starting to understand, if the pilot is not lit the thermocouple doesn't heat up and the gas valve won't open, right? But would the blower not turn on also?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #6

    Oct 27, 2008, 04:03 PM
    When the furnace gets hot a control tells the blower to come on. If this is the main air blower that is.
    rasco847's Avatar
    rasco847 Posts: 49, Reputation: 1
    Junior Member
     
    #7

    Oct 27, 2008, 09:53 PM
    Cleaned out the pilot and everything is working great... thanks a bunch :) you were a great help

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

TXV repeatedly goes bad on my Rheem [ 1 Answers ]

Hi All, I have a new Rheem unit (6 months old) and since the hot weather really started, the TXV has gone bad two times within a week. I suspect that either we have a lemon, or most likely, the people who have installed it and repaired it have not done something correctly. Could someone give...

Rheem [ 1 Answers ]

We have a rheem package unit model # rpno-037j and a hunter programmable thermostat #42999b,five wires-red,blue,white,green,yellow for contols can you tell us were these wires go on t-stat?

No gas at Burner on RHEEM [ 3 Answers ]

Ignitor Works, Furnace Cycles, Green LEDS on Board... No GAS

Rheem unit [ 2 Answers ]

Hi can anyone help me I have this rheem unit and now that I turn the heat on the heat pump outside only cames on when I go to the unit and reset the unit by pushing the red buton on the side Thank you

10-15yr rheem [ 1 Answers ]

Air or heat doesn't work. Fan blowes constently if left on at breaker. What could be the problem? 1 UNIT if I need to replace?


View more questions Search