    Square D circuit breakers
    I have a small sub-panel with 30 amps coming into it. I have had my used air compressors motor changed to one that draws 13.5 amps. The 15 amp circuit breaker still trips though the unit was rebuilt professionally.

    There are only six 15 amp circuit breakers available to me and 5 are used. They are "Square D" and I am asking if a 20 amp breaker is the same physical size as a 15 amp breaker in the Square D. Am I correct to assume then that I would wire a receptacle with 12 gauge wire? Can I use 12 gauge wire from the circuit breaker to a regular rectangular box with a normal 3 prong plug and a normal receptacle like one sees in a house? Or does it have to be some sort of special plug and receptacle?

    Thank You, David
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Oct 25, 2008, 08:09 PM

    Yes. Just use a 20 A receptacle too.

    You might want to use 12 AWG wire on the compressor and use a 20 A plug and cordset.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Circuit breakers [ 6 Answers ]

If I have a main disconnect at the pole what kind of breaker box should I put in my quanset To replace the old fuse box,a main lug or main breaker. This is also part my shop. Thanks for any answers, can omeone please help??

Circuit breakers [ 16 Answers ]

I purchased and ready to install a new diahwasher. The instructions call for a 15 amp circuit breaker. The current breaker is a 10 amp breaker solely for the dishwasher. Can I use the 10 amp or should I change the breaker to 15 amp? How difficult would it be to change?

Circuit breakers [ 2 Answers ]

It seems so far that our kitchen is wired all on the same circuit. When we use the oven and microwave or the microwave and the toaster oven which is on the other side of the room the breaker trips. That breaker is currently 15amps. Would it be all right to change that breaker to a 25 or 30 amp for...

Circuit breakers [ 2 Answers ]

I would like to up grade the amps going to my garage so I can run my saws and power tools with out dimming my shop lights. I currently have a old style fuse box in the garge feed with 12ga uf cable run off a 20amp circuit breaker in the service panel. My plans are to replace the fuse box with a new...


View more questions Search