    Furnace blower constant
    When I raised thermostat, the blower immediately come on without time for heat exchanger to warm up.It is set in the auto position. The furnace is a BDP (Carrier) model 394GAW060125. Any suggestions would help before I try to replace parts or call HVAC repairperson, Thanks
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Oct 20, 2008, 02:53 PM
    There should be a delay as you are well aware of. This is usually done by the use of a fan and limit control or a perset time on the circuit board if so equipped.

    Have you replaced the thermostat lately? If you have it might be wired wrong or it might be defective sending the signal to the green blower wire. This will cause the blower to come on right away. Look for a wiring diagram on the inside of the blower motor door and see if you can locate the fan and limit control. If not your circuit board might control the fan.
    LouNY's Avatar
    LouNY Posts: 2, Reputation: 1
    New Member
     
    #3

    Oct 20, 2008, 03:29 PM

    Programmable thermostat is 10 years old you think it may need to be replaced?
    mygirlsdad77's Avatar
    mygirlsdad77 Posts: 5,713, Reputation: 339
    Plumbing Expert
     
    #4

    Oct 20, 2008, 04:06 PM

    Possible. I would start by unhooking all thermostat wires from board on furnace. Write down exactly were they are hooked up before you unhook them so you know how to hook them back up. After doing this, jump r and w on the furnace board with a piece of wire. This should start normal operation of heat cycle. If you jump r and w with all other wires disconnected, and your blower motor(not combustion blower) still comes on right away, then your problem is somewhere in the furnace and not in your thermostat or thermostat wiring. Let me know if this helps, and we can take the next step.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Goodman furnace constant blinking led. [ 6 Answers ]

I have a Goodman Model # GSM100-4 furnace that has been a pain the tail. This week I went to start it up and I am getting a constant flash on the control board. I have an old, what I thought, was a good board that I swapped out. Still the same problem, constant flashing. I tried swapping the...

Furnace blower [ 1 Answers ]

The blower to my furnace will turn on and blow cold air for like 30 seconds and then shut off and the furnace isn't running. When the furnace kicks on it runs fine.

Constant blower on when stat is connected [ 1 Answers ]

I had to replace a fan limit switch, all works correctly but if I connect the stat blower runs constant. Ireplaced stat but same problem could it be in the 2wire?

Furnace blower goes on and off [ 2 Answers ]

Hi, I Have A Ultra80 Upflow Forced Hot Air Furnace... my?? To You Is... burner Comes On... then Blower Starts-runs For About A Minute Then Shuts Off.. burners Still Running Then Blower Comes On Again And Shuts Off... the Furnace Its Self If Hot As Heck... so What Im Saying Is The Blower Cycles On...

Furnace/blower. [ 6 Answers ]

Been searching but so far I haven't found any information that really helps me. I've lived in this house for about a year and a half now, it has the original furance in it(house was built in the 70's I blelieve). Last year the furnace worked fine, and had worked fine so far this year. I live in...


View more questions Search