    Upgrading electrical service in a barn
    Hi. I'm trying to upgrade my electrical service in my barn from 120 to 240. It is 290 feet from my main service panel, and I'd like to take 50 amps out to a subpanel that's already there. I've done the calculations for voltage drop (I hope correctly) and I think what I need is #4 (copper) wire (I plan on putting it in buried PVC). Also, can't I just run three wires--two hot and one neutral--and just ground the sub panel since the main panel is already grounded? Thanks for letting me know if I've figured this out correctly.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Jul 28, 2008, 02:38 PM
    Do you only want 240 VAC only or will you actually need 120/240?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Jul 28, 2008, 02:54 PM
    My rough calculation calls for #2 AWD conductors.

    You would need 3 (120/240) #2 conductors THHWN (90 celsius) (two ungrounded and one Neutral return). I believe that you will also need a #10 ground at the Barn Panel, You cannot use the ground provided by the main panel as part of the EGS at the barn.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jul 28, 2008, 04:20 PM
    Just a few clarifications,

    The insulation is THHN/THWN.

    The green wire will need to be #8, if # 2 wire is used. The equipment ground is to be proportional to th line conductors when increased in size.

    My calcs agree with #2 copper, assuming a conservative amount of inductive load, such as motors, to arrive at less than the max recommended 3% of Vd.

    How did you arrive at #4?

    Unless there would not be a large motor load, or a welder, and a steady 50 amp load would be unlikely, and considering the cost of copper, I would not hesitate to install #2 aluminum with XHHW insulation, with a #4 equipment ground. If there is any chance the load will increase due to expansion, stick to the copper.

    By the way , the conduit will need to be min 18" deep. Not required, unless by local code, but having a warning tape 6-12 in below grade above the conduit is wise in the event digging happens there.. Using metallic tape will allow a metal detector to locate the path easy later on.
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #5

    Jul 28, 2008, 04:36 PM
    Quote Originally Posted by tkrussell
    Just a few clarifications,

    The insulation is THHN/THWN.

    The green wire will need to be #8, if # 2 wire is used. The equipment ground is to be proportional to th line conductors when increased in size.

    My calcs agree with #2 copper, assuming a conservative amount of inductive load, such as motors, to arrive at less than the max recommended 3% of Vd.

    How did you arrive at #4?

    Unless there would not be a large motor load, or a welder, and a steady 50 amp load would be unlikely, and considering the cost of copper, I would not hesitate to install #2 aluminum with XHHW insulation, with a #4 equipment ground. If there is any chance the load will increase due to expansion, stick to the copper.

    By the way , the conduit will need to be min 18" deep. Not required, unless by local code, but having a warning tape 6-12 in below grade above the conduit is wise in the event digging happens there.. Using metallic tape will allow a metal detector to locate the path easy later on.
    I agree with TK and Don---seeing that we have no idea on the load planned in your remote structure.



    To add: It would be nice to see people show how they came up with their numbers. Anyone can go to some renky dink site and use their VD calculator--- later coming on here as if they did the calculation work! :rolleyes:
    WmInChilton's Avatar
    WmInChilton Posts: 3, Reputation: 1
    New Member
     
    #6

    Jul 28, 2008, 08:03 PM
    here's how I came up with my calculations for 4 AWG wire:

    A: The formula for voltage drop is: Vd = 2K x L x I / Cm

    Vd = Voltage Drop
    I = Current in Conductor (Amperes)
    L = One way Length of Circuit
    Cm = Cross Section Area of Conductor (Circular Mils)
    K = Resistance in ohms of one circular mil foot of conductor
    K = 12.9 for Copper Conductors @ 75 degrees C
    K = 21.2 for Aluminum Conductors @ 75 degree C
    / = Divided by

    using the above formula, I came up with


    Vd = 2 x 12.9 x 290 x 50 / 41740 = 8.9 volts
    8.9 volts / 240 volts = 0.037 = 3.7%

    am I to take it from your response, that this is a rinky-dink calculation? And therefore wrong?
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #7

    Jul 28, 2008, 08:28 PM
    Strickly speaking yes and no, because you said 240V, but you really mean 120/240V.

    While true 8.9 / 240 = 3.7% (taking your word here) is > 3%, so you have to try again. Last time I checked 3.7 is greater than 3.

    Second, your loads also contain some 120 V, those loads are going to get jipped a lot more than 3.7%. More like double 3.7% or 7.4%.

    If it were strickly a 240 volt load like a water heater, you can use 240V to compute the voltage drop in %.

    While it is true that N carries the difference current of the two hots, that difference will not always be zero.
    WmInChilton's Avatar
    WmInChilton Posts: 3, Reputation: 1
    New Member
     
    #8

    Jul 28, 2008, 09:12 PM
    Thank you for your response. I don't claim to be the expert. That's why I'm here. You're right. I need 120 and 240 service. I've got overhead lines now that I'm trying to get rid of. I've got to take the service 290 feet from the main service panel to the sub panel at the barn. I'd like to put it underground. What's the best way?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #9

    Jul 29, 2008, 06:57 AM
    If the only reason you want to change to underground is for aesthetic purposes, personally, I'd leave it alone.

    If the service you already have is meeting your needs, save the money you would spend. 290 ft. of copper will cost a considerable amount of dollars!
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #10

    Jul 29, 2008, 07:54 AM
    I want to address this question too:

    Quote Originally Posted by WmInChilton
    Also, can't I just run three wires--two hot and one neutral--and just ground the sub panel since the main panel is already grounded?
    The answer is no. The connection to a ground rod at the detecahed structure is for lightning protection. The ground connection to the utility is for a reference. The ground an neutral busses will remain separate and isolated from each other in the barn.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #11

    Jul 29, 2008, 08:10 AM
    See if everyone else arees:

    URD drirect burial aluminum wire. You'll have to recalculate the required conductor size with K for Aluminum. 18" depth.
    Aluminum URD Cable- 600 Volt- Quadruplex-90°C For Direct Burial on Custom Cable Corp.


    Donf:
    I believe part of the reason for the upgrade is to bring 240 into the barn.

    EDIT: Added link. Removed reference to tracer wire, but will add link here: Kris-Tech Wire Company: Why You Should Always Use The Appropriate Tracer or Locating Wire Instead of THHN for Direct Burial
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #12

    Jul 29, 2008, 11:20 AM
    Donf:

    I believe part of the reason for the upgrade is to bring 240 into the barn.

    Ron -

    The poster already has 240 to the barn, supplied via overhead. See post #8.
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #13

    Jul 29, 2008, 12:33 PM
    Donf:

    In post #1:

    Quote Originally Posted by WmInChilton
    Hi. I'm trying to upgrade my electrical service in my barn from 120 to 240.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Upgrading to 200 amp service [ 1 Answers ]

I want to upgrade from 150 to 200 Amp service. My current panel has double breakers in ever slot except where the A/C, Dryer and Range are connected. I have wired panels before but never upgraded the service. I have studied and planned the change over the last two months but I still have a question...

100 or 200 amp electrical service [ 2 Answers ]

I am building a new house and have asked for 200 amp service. What is the cost difference and what are the pros and cons of doing this?

Upgrading from 100amp service to 200 amp service [ 1 Answers ]

I have a 1994 model double wide home, and would like to change my 100 amp service to 200 amp service. ( I want to go to electric heat) I have a disconnect at the house after the meter and it say 200amp. Is the wiring from there to my breaker box able to handle 200 amp service, and if not how do I...

200 Amp Electrical Service [ 1 Answers ]

What gauge wiring does the service wire need to be to feed a 200 amp electrical service? Also - aluminum or copper?

Upgrading/Relocating my service panel [ 1 Answers ]

I'm upgrading my service panel mainly because I need more breaker space, but will eventually need more juice. I'm an electrical engineer, but not a electrician, so I am fully aware of the principals, just not the code and best practices like electricians are, though I have been studying the code...


View more questions Search