    Chiller loading
    Got this issue on cooling kW at certain ambient temperature.

    Leaving CHWT=13 deg.C

    @ 45DegC- Cooling output is 1397.1kW and compressor input is 491.1kW
    @50DegC - Cooling output is 1080.8 and Compressor is 397.4

    Is it not obvious that if temperature rises the load increases? Why is that at 45degC the load is larger than the 50degC. Can this be explained further?thanks
    KISS's Avatar
    KISS Posts: 12,510, Reputation: 839
    Uber Member
     
    #2

    Jun 10, 2008, 06:51 AM
    It's really going to depend on the temperature and humidity of the air in the secondary system. More specifically Enthalpy. e.g what temp/humidity you started from and what temperature/humidity you ended up at. Enthalpy of Moist and Humid Air

    With a large system that would become the sum of all the secondary systems.

    Another possibility which I think is remote is vibration of the equipment at a particular cooling load.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to displace the loading image with a message like "loading... "? [ 3 Answers ]

How to displace the loading image with a message like "loading"?

Chiller Selection [ 1 Answers ]

Hi , Im civil engineer and supervisor of a 8 story building with 2500 square meteres living space in 5 stories and i'm setting up some mechanical objectives too , im wondering wether i have to choose a Water-Chilled Water cooler working with electrical power or a Gas-Fuled type of these...

Who can answer about chiller [ 1 Answers ]

How can I calculate the size for chiller and AHU unit PIPE :) :) ?

Chiller pump [ 1 Answers ]

How to calculate chiller pump head

Query regarding Chiller [ 2 Answers ]

Dear Sir, We have LG Steam driven Absorption Chiller of 500 Ton with following specs 1) Chilled water flow 302 m3/hr 2) Chilled water Temp 7 to 12 C In these specs, rated or max flow requirement gainst 500 Ton is mentioned. Please tell me 1) What is the minimum flow...


View more questions Search