    Wiring under a Sink
    I am remodeling my kitchen and I am installing a new line for my dishwasher and disposal.
    My diswasher is 5.3 amp max according to the manufacturer and the disposal is 7.3 amps.
    1st: Is a 15 amp circuit acceptable here?
    2nd: Is a GFCI required for the under the sink outlet to be used for the dishwasher?
    3rd: The disposal is hardwired - What do I use to ancor the wire coming through the sheetrock wall? Or Do I need anything but a hole?
    Thanks, Russ
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    May 25, 2008, 04:28 PM
    A 15A circuit would be OK, a 20A is preferred.
    The disposal should NOT be hardwired. You should install a cord and plug on it.

    No, the receptacle under the sink does not need GFI protection.
    reachief's Avatar
    reachief Posts: 8, Reputation: 1
    New Member
     
    #3

    May 25, 2008, 04:41 PM
    Quote Originally Posted by stanfortyman
    A 15A circuit would be OK, a 20A is preferred.
    The disposal should NOT be hardwired. You should install a cord and plug on it.

    No, the receptacle under the sink does not need GFI protection.
    I would like to follow this question up.
    So install a 20 amp outlet, but split the outlet into 2 with one for the diswasher and the second would go to the disposal switch to turn on this portion of the outlet?
    Again thanks, Russ
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    May 25, 2008, 04:46 PM
    Sounds right.
    Use a big box, like a 4" square with a duplex receptacle "industrial" cover. This will give you enough room to make all the necessary splices.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

New bathroom sink backs up halfway, quickly drains, repeat.. no overflow in this sink [ 2 Answers ]

I just very proudly finished installing our new second floor bathroom sink drains. Two different vanities, two different walls. I ran the water steadily in both of them for 10 minutes. One works fine. The other backs up about halfway up the bowl, then suddenly quickly drains everything and...

Am trying to convert my single sink bathroom to a double sink, [ 1 Answers ]

I have a single sink in my bathroom at this point, am trying to put a double sink counter top on it. My question is if I have to put a double drain pipes or if I can put a T on the excisting one, same question for the hot, and cold water. Am just worried about the drain pipe hopefully you guys can...

Sewage smell from sink drains in main bath and kitchin sink [ 1 Answers ]

We just bought our first house they ran a new sewage line from all sinks,toilets,tubs,and washer to main line and replace main line to city main. The main bath sink is the worst it smells my sons room and hall way. Is the pipe to small main is 4in and vent is 2in. We have 2 full baths with...

Fog horn noise when using taps in bathroom sink and kitchen sink [ 1 Answers ]

There has developed, in the last week, a "fog horn" sound when we turn on the hot or cold taps in the bathroom or kitchen. It does not occur when we use the washer or dishwasher. Could anyone give some advise on what could be the cause of this?

Kitchen Sink/Laundry Sink Drain Vent Non-exist [ 3 Answers ]

The set-up from kitchen sink leading down to drain to basement: 1. Kitchen sink - (R side) - connected to a P drain I think you call it -PVC-, connected to a "metal" T, which has a Studer vent gizmo attached to the top of it, then draining into a metal pipe straight down to the drain in the...


View more questions Search