    Voltage drop in site lighting circuits
    How do you calculate the voltage drop for each fixture in a site lighting circuit?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Apr 9, 2008, 02:01 PM
    Due to the various lengths between each fixture, it will likely make your head hurt.
    Try this:
    Mike Holt
    The scroll to bottom to where it says "Voltage Drop Calculations"
    I would cheat on this and hook up good Voltmeter, and screw in or uncrew each bulb one by one and take readings? Good Luck
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Apr 9, 2008, 04:34 PM
    If you are designing the circuits and feeders, the simplest to do is sketch it all out on paper, laying out your circuits the shortest and/or reasonable method, and mark each light location with the total distance back to the distribution point and the total load in amps for that circuit.

    The load will reduce by one fixture but longer distance as you work you way farther from distribution.

    Start with the first fixture on the circuit, total the load and measure the distance and perform the voltage drop calcs at that point to size the feeder.

    Add the distance to the next load and deduct the first load, and do the calcs again, and again, for each difference in circuit data, until your done.

    If the variables are great, you may notice the wire size reduce quickly as you get further out. Don't reduce too quickly as to allow for future growth.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Apr 10, 2008, 06:18 AM
    I told you your head would hurt.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Voltage drop [ 5 Answers ]

I will be running wire to my shop that is aprox 250' from the main elect box at the house. I would like to have 220 volts and 110 volts. The wire will be buried underground the average temp in my area in the summer is 100 degrees. What size wire should I use. I will be welding with a welder that...

Voltage Drop [ 3 Answers ]

I am trying to illuminate a tunnel about 3000' long temporarily with 9- 400 Watt Metal Halide fixtures spaced about 320' apart. I have a 120/240 generator single phase that I will use to back feed a 240/480 volt transformer to deliver 480 volts, single phase to the tunnel lights. At 480 volts I...

Voltage drop [ 1 Answers ]

The Voltage will drop after 150 meter wire ,how to sole the problem . Thanks to all

Voltage drop [ 4 Answers ]

A 300sq mm cable is to be laid for 600mtr. Distance. As the distance is large so there are considerable voltage drop at the receiving side. How can we cope up with this voltage drop at the receiving end? We want a constant voltage ofd 415 V at receiving end irrespective of input voltage? ...

Voltage drop [ 2 Answers ]

How far can you run an electrical cord, that is plugged into a 20 amp circuit, and still run a circular saw? If the saw starts slowly, will that harm the saw?


View more questions Search