    Thermostat Calling for Heat but Furnace Shuts Off
    I have a gas forced-air furnace 3-5yrs old. Honeywell setback type thermostat (set to "HOLDTEMP")

    My problem is the furnace seems to shut off before it reaches set point (ussually 4-6 degrees below set point)

    I changed the thermostat and still the same issue. If I turn the power off to the furnace and turn it back on the furnace starts up and runs fine for 15, 20 maybe 25 minutes, but eventually shuts off again short of set point. Doesn't seem to be any pattern as to how long it runs or how near set point it is.

    I might be saving gas cost but the bride is putting on too many sweaters and a man can only wear some many pairs of socks.

    Any help?
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Feb 21, 2008, 03:57 PM
    Exact model number of thermostat.
    willift's Avatar
    willift Posts: 4, Reputation: 1
    New Member
     
    #3

    Feb 21, 2008, 06:59 PM
    Honeywell RTH6300B
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #4

    Feb 21, 2008, 07:21 PM
    If your furnace is faulting out it should have a flashing light you can see.-- lower door on the furnace with a small glass window count the blinks it will give you a code telling you what's wrong.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #5

    Feb 22, 2008, 06:00 AM
    Read under settings. If not set properly the unit will cycle off early. You might have yours set to hot water instead of forced air. Read and follow directions exactly. Link below for your stat.

    http://customer.honeywell.com/techli...0s/69-1717.pdf
    willift's Avatar
    willift Posts: 4, Reputation: 1
    New Member
     
    #6

    Feb 25, 2008, 08:00 AM
    Quote Originally Posted by T-Top
    If your furnace is faulting out it should have a flashing light you can see.-- lower door on the furnace with a small glass window count the blinks it will give you a code telling you whats wrong.
    All right, the fault code tells me it's one of 3 limits (2 ROL & 1 Limit). I've physically inspected the 2 ROL can't tell anything and the limit switch seems stuck to the unit. I removed the screws but one side of the plastic circuit board like switch is stuck to unit. That switch must be normally closed because when I disconnected it the fan started running but I thought I'd better not run it that way.

    I'm not sure if this limit switch has some type of mech tab holding it to the wall of the furnace or is it just stuck something else, I'm fearful of breaking it and having no heat.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #7

    Feb 25, 2008, 08:50 AM
    I've physically inspected the 2 ROL can't tell anything and the limit switch seems stuck to the unit.

    You have to test these with a meter.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Furnace Thermostat Near Heat Duct [ 2 Answers ]

I live in an older home (1928). The furnace thermostat is mounted to a wall which also carries a heat duct to the second floor. The wall surface is warm during the heating season and I think this radiant heat is affecting the thermostat. Is there a way to shield the stat to minimize the heat...

New thermostat, Furnace ignites fire but no heat [ 3 Answers ]

Hi My furnace and thermostat was working fine until two weeks ago. So I replaced the thermostat and the heat started working for the first day then it stopped. I tried to turn up the degrees on the thermostat and I checked the furnace. The electric ignitor was working fine and there was fire...

Heil Furnace - No response when calling for heat [ 3 Answers ]

I have a 5 year old 90% efficient Heil Furnace. I get no response when I call for heat. (the "blower only" setting works fine.) I have confirmed that it is not the thermostat and that the fan control board has power. The gas valve light pulsates to indicate that it is OK. The lead that goes to the...

Honeywell Thermostat Furnace heat not on [ 2 Answers ]

Hi, We installed a new Honeywell Deluxe 5-2 Programmable Thermostat (RTH6300B) last week. We have a Carrier Furnace that is 15 years old, I believe. We've noticed that the temperature of our house doesn't seem to be reaching the temperature it's set for but have been so busy and out so much...

Honeywell thermostat heat/cool in Rheem 2 stage furnace? [ 1 Answers ]

I have a Honeywell 1 Heat/1Cool thermostat (TH6110D1013) that I would like to use with a Rheem 2 stage gas heat furnace. I think it is possible but would I get the same benefits as having a thermostat with 2 heat/1 cool? Would I just connect the W terminal on the Thermostat to the W2 on the...


View more questions Search