    gaclements's Avatar
    gaclements Posts: 4, Reputation: 1
    New Member
     
    #1

    Jan 15, 2008, 09:16 PM
    Reversing valve not reversing
    I have a Goodman package heat pump model PHJ030-1A. I found a leak in the condenser coil, in the "U" shape joint. I made some checks, reversing valve coil: the resistance was 17. Something ohms, found 24 volts going to the coil, but didn't check for amps. O.K. Would low freon stop the reversing valve from switching to heat mode? O.K. Let say that the leak was fix, what would stop the valve from working.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 15, 2008, 11:02 PM
    Reversing valves do go bad and not just the coil part. The internal parts of the valve go bad also. This work is usually left to a professional due to the refrigerant recovery laws and the brazing needed to fix or replace any part of the sealed system.
    gaclements's Avatar
    gaclements Posts: 4, Reputation: 1
    New Member
     
    #3

    Jan 16, 2008, 05:22 AM
    Quote Originally Posted by hvac1000
    Reversing valves do go bad and not just the coil part. The internal parts of the valve go bad also. This work is usually left to a professional due to the refrigerant recovery laws and the brazing needed to fix or replace any part of the sealed system.
    The question is if low freon would stop the reversing valve from working. I know the system has to be pump to a recovery system, for the atmosphere, cause of the freon. When I do call HVAC. I want to know what is wrong with my unit, so I want get rip off. If I do need a reversing valve I would let HVAC do the work for the warranty.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jan 16, 2008, 07:53 AM
    The valve has pressure on different sides depending upon if it is in the heat pump mode or A/C. Some valves have a balance cap tube and some do not. To check for a bad valve put your gauges on the unit and cycle to see if the valve is working. In many cases you can hear it kick in also.

    (((I want to know what is wrong with my unit, so I want get rip off. If I do need a reversing valve I would let HVAC do the work for the warranty.))

    Good luck getting the valve replaced under warranty unless the company that sold and installed the unit is doing the work and then you will still have to pay for ancillary charges.
    gaclements's Avatar
    gaclements Posts: 4, Reputation: 1
    New Member
     
    #5

    Jan 16, 2008, 04:29 PM
    Quote Originally Posted by hvac1000
    The valve has pressure on different sides depending upon if it is in the heat pump mode or A/C. Some valves have a balance cap tube and some do not. To check for a bad valve put your gauges on the unit and cycle to see if the valve is working. In many cases you can hear it kick in also.

    (((I want to know what is wrong with my unit, so I want get rip off. If I do need a reversing valve I would let HVAC do the work for the warranty.))

    Good luck getting the valve replaced under warranty unless the company that sold and installed the unit is doing the work and then you will still have to pay for ancillary charges.
    What is the pressure of the system in heat mode if the outside temp. is in the 20's-30's. Reversing valve part #is B1227316S, does this valve have the balance cap tube? When you turn the unit on it go to cool mode and will not cycle to heat. The valve does not make any noise.
    gaclements's Avatar
    gaclements Posts: 4, Reputation: 1
    New Member
     
    #6

    Jul 19, 2008, 11:47 PM
    Had to add freon. Low freon will stop a reversing from switching from cool to heat or heat to cool. According to which unit you have. Just by adding freon can save you hundreds of dollars in repair cost. G.A. Clements

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Reversing valve [ 3 Answers ]

Trying to start up a water to air heat pump. The high side r-22 kicks out at 400psi within 3 seconds whether in cooling mode or heating mode. The reversing valve (alco 401RD-10F57) clicks but seems to be the only obstruction that would prevent refrig. Flow. There seems to be no suction side change....

Jantirol heatpump reversing valve hums constantly [ 2 Answers ]

My jantirol heat pump when the thermostat is in the off position the reversing valve in the heat pump hums and is hot. If I turn the breaker off in the handler space then it stops. That circuit breaker is the only thing that stops it. The cutoff next to the heat pump will not stop the hum and...

Reversing valve or Compressor? [ 1 Answers ]

Stuck on this: Unit has equal pressures when it starts up... compressor does not sweat even from common suction... the reversing valve selenoid clicks but does not switch... I know pressures along with 24v switch the reversing valve... but it seems valves are bad in compressor? Any help would be...

Reversing entries [ 2 Answers ]

I have a problem that says to reversing entries by the previous year's adjusting entries. It want me to reverse Interest income $307.50 Salaries expense That give me Sales salaries $1306, Office Salaries $607 I will add them together and get $1913 for Salaries payable. Interest Expense $1,755. How...


View more questions Search