    Beckett AFG Burner with R7184A Primary Contrl
    I have a Beckett AFG burner with a Beckett R7184A Interrupted Ignition Oil Primary Control. The fuel line filter was clogged so I replaced it with a new one. When I turned power back on the burner tried to ignite but after 10 seconds or so it shut down. Now the burner will not start and the green light flashes (1/2 second on) which according to the R7184A dianostic table this means it is in lockout. I press the red button but nothing happens.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jan 4, 2008, 08:35 PM
    Shut off all power. Wait then turn back on. Did you bleed the pump?
    shocktron123's Avatar
    shocktron123 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 5, 2008, 07:45 AM
    I attempted the process of bleeding. Not sure if I got all of the air out but the burner did fire up and run for approximately 5 minutes then all of a sudden you could hear the flame kicking in and out and then finally out...
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Jan 5, 2008, 08:29 AM
    Sound like you still have air getting in the line or the filter housing/flare nut connections are leaking allowing air to get into the system. I am sure you have checked to make sure you have oil?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Beckett model AFG burner flame-out [ 14 Answers ]

This season is the first time ever that this has happened. The furnace starts, gets a flame, runs for a while, then it flames-out. It sounds like the oil pump is still running (I hear like a spraying sound). Nothing shuts off. Then the flame will come on again, but may continue flaming-out...

Vent plug for Beckett model AFG [ 1 Answers ]

I need to bleed the line... but I can not find the vent plug to do this. I have a one line and have to bleed line. Please help me locate this plug. Thanks for your help in advance.

Beckett oil burner for forced air furnace [ 1 Answers ]

Why does the oil burner make a high pitched noise when firing?

Beckett oil furnace [ 3 Answers ]

I have an oil furnace... recently, I had a contractor come out to take a look at it. The furnace is tied into my central air conditioning system and the contractor told me that I had a blown computer box on the base of the unit and that it would need to be replaced (for $290 not including labor)....

Beckett oil furnace [ 2 Answers ]

I recently switched from oil to gas in the house, and rather then get rid of the oil system, I decided to install in the garage. The system used to be a 2 line feed but have only one to it now the other being closed. The furnace will fire up, however fuel is spraying out from the inside near the...


View more questions Search