    Trane Air Handler/Heat Problems
    Hi,

    I have a Trane airhandler system in my house with an oil burner furnace that feeds hot water to the heat exchanger inline with the air handler and the ducting. We suspect our system has ver poor efficiency overall, as it appears to run the hot water often through the heat exchanger, and ofen the fan goes on/off frequently, and even blows cool air sometimes. The house has 2 very similar air handler systems (both Tranes; 1 just smaller than the other) and both run in conjunction with the main oil burner/hot water system. We have basic Honeywell thermostats that we believe are working properly (we've even swapped them between the 2 systems as they are exactly the same units). We're looking for general description of how the system works, and basic troubleshooting to help isolate where the problem(s) may be.

    Here's some very basic info:
    Thermostats: basic Honeywell, round, thermostats. 4 wire(s) that control either heat (winter) or AC (summer). Fans set to "Auto"; mode currently (winter) set to "Heat"

    AirHandlers: Trane

    Oil burner, with forced hot water through heat exchangers at air handlers; the water temp exiting the burner seems to be set at approx 180deg F.

    There are also some sort of Honeywell controllers on the heat exchangers that seem to also control, override, or limit the running of system above or below a set temperature (not sure if these are set at the right temparatures - both currently set to 160deg F)

    Is there any way to know if our system is wired correctly? We can't seem to find a GOOD general wiring diagram containing all of the system components.

    What temperatures should the Honeywell heat controllers at the heat exchangers be set to? We've tried 10deg lower and 10deg higher, and it doesn't seem to change anything.

    Any advise or good resources to learn about about this type of system?

    Thanks!

    \\
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Dec 25, 2007, 11:13 PM
    You have a water to air heat system.
    Most of those systems are design/build and are wired in many different ways.
    180 degree water temp out is good for a fan coil system
    The controls on the heat exchanger/hot water coils are probably minimum set or fan lock off controllers to prevent blowing cold air. They could also be used for many other things.

    A reputable company should have left a wiring diagram because since it is field built and installed no one really knows exactly what you have except for some part numbers and name brands.

    Leave your heat controllers set as they were when you found them till you find the problem.

    You need to test your control system to find the offending part for your fan problem. This can be done by finding the control for the fan. Those could be the controls next to the hot water coil air handlers.

    Here is a link to Honeywells site. Just type your control number in the lower box on the right side. You can look up the controls yourself and see how they work and what they are for. Since we are not on site all we can do is guess at what you problem is but you will have the advantage now with the Honeywell site. Good luck.


    Default - Honeywell Environmental And Combustion Controls

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Trane Air Handler won't come one [ 15 Answers ]

Hello, My air is not working. The thermostat is set to 77 degrees and it is 80 degrees in the house. I have turned the breaker off and back on. The fan on the unit outside the house is running, but cool air is coming out, not warm as I expected. I turned everything off for 2 hours to see...

Trane XL16i, Variable Speed Air Handler, 803 thermostat [ 3 Answers ]

We purchased this unit about 8 weeks ago and it's been nothing but a headache. Trane's field rep came out Friday with the installer and they gave the unit a complete going over. Checked duct work, everything. Even replaced the thermostat. Was assured everything was mechanically correct. The...

Trane Air Handler [ 1 Answers ]

We recently purchased a Trane 16Xi with a Trane 4TEE variable speed air handler. The air handler has been installed upside down. Is this right? At 75 degrees the compressor is coming on for 10 minutes. shutting down for 20 minutes. The humidity in the house is running 57% to 61%. Outside...

Replacement motor for Trane air handler [ 1 Answers ]

The motor in one of my 35-year old Trane air handlers recently Blew. It looked quite old. I figured it would be easy to replace It just by matching the specs. Unfortunately the new Motor runs for 10-15 minutes, then it stops for 15 minutes, Then it starts again. I suspect the thermal...

Trane A/C Handler [ 2 Answers ]

The blower makes a slight noise, almost rattling. I looked at the blower unit and it has the part number M412TB31V. Now I'm not sure if that's just the wheel, motor or both the motor and wheel. I would like to replace the motor and wheel, as I can't determine exactly where the noise is coming...


View more questions Search