    Thought I had it Fixed.but no. Burners won't start now
    Hi All,

    1) In my previous question (https://www.askmehelpdesk.com/heatin...ld-155440.html) I received help on trouble shooting my furnace problems and found a bad inducer motor to be the culprit (Thanks!).

    2) After replacing the motor today, I'm finding the burners won't ingite at all.

    3) The inducer motor is running great and the pilot is lit just fine... I think

    4) Point of interest: I'm noticing that the pilot light does not seem to be hitting the same area it hit before I changed out the motor, though I have made sure the pilot orafice is clean and clear.

    Q: Is the difference in the pilot light I notice because before, I didn't really have the inducer motor running very well to notice an effect on the pilot?

    Q: Does the inducer motor affect the pilot flame?

    Q: Why won't the main gas burners kick in?

    Thanks again! Thankfully, the weather warmed up a bit today...
    hixton's Avatar
    hixton Posts: 146, Reputation: 5
    Junior Member
     
    #2

    Nov 27, 2007, 05:16 PM
    First if you opened up the pilot orifice with a wire gauge you might have made the orifice to big try a new orifice also you might have a bad bi-metal pilot assembly which comes with a new orifice. Do you hear any clicks or clunks from the firing valve after the pilots been lit for about minute ?
    Whistleboy's Avatar
    Whistleboy Posts: 12, Reputation: 1
    New Member
     
    #3

    Nov 27, 2007, 06:04 PM
    Thanks for your reply hixton. The wire went through the orafice quite easily and is much softer than the orafice material, so I'm pretty sure no damage was done to the orafice. Also, when I was able to get the old motor working for a few hours longer, the pilot and main burner had no problems. Also, no clicks. I know what you are talking about, but all seems fine... really consistent pilot flame.. weird.
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #4

    Nov 28, 2007, 05:22 AM
    Brand of furnace and model number? If the inducer fan is having a effect on the pilot you may have larger problems than you think. A defective heat exchanger is a possibality. Pleas provide model and brand.
    Whistleboy's Avatar
    Whistleboy Posts: 12, Reputation: 1
    New Member
     
    #5

    Nov 28, 2007, 08:03 AM
    Hi hvac1000,

    My furnace is a Carrier 58DH060-CC (Made in the 80's). The inducer motor seems to stay on all the time, as does the pilot. Every once in a while the burners will kick in and work, then either stay on for several minutes or only 5 seconds. Not liking the sound of having something bigger wrong 'gulp'.
    Whistleboy's Avatar
    Whistleboy Posts: 12, Reputation: 1
    New Member
     
    #6

    Nov 28, 2007, 07:38 PM
    Ah ha! I just learned how to adujst the pilot flame and now everything works great... well, I won't get excited too quick since my success was short lived last time. I just gave it a little more gas, so to speak. Finding the service manual online at http://www.carrier-commercial.com under "Literature > Maintenance" was VERY helpful for reading how everything should work and how to troubleshoot my particular furnace.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Burners come on, go off, come on, then they go away [ 3 Answers ]

Hi folks. I've got a problem with a Goodman GPG13 gas pack unit. When a call to heat is given all seems to work fine but the burners come on for a short time then some go off and come back on but after a while (a couple minutes) they all go off. And they stay off for the lock out time ~ I'm...

Burners do not stay lit. [ 3 Answers ]

Burners do not stay lit. I have a brand new Goodman GPG13 package unit with a 138,000 BTU natural gas furnace. The furnace has six (6) burners and an electronic spark ignition. All burners light, then (after about one (1) minute) the bottom burner or bottom two burners sputter or just go out may...

Burners won't ignite--no gas? [ 1 Answers ]

Lennox model GMP075-3. Installed in '95. I've tried resetting according to instructions on access cover panel (turn heat to 'off', turn off power to furnace, turn gas valve to 'off' for 5 minutes, etc.) When I call for heat, small (induction?) fan runs for a few seconds, the igniter unit glows...

2 internal dvd burners [ 2 Answers ]

I want to know can you have 2 internal dvd burners in your computer and both of them working if so how do u set it up

Burners won't... Follow up info [ 3 Answers ]

Burners light for couple seconds, then go out Weather King --- ICECO --- 80 PJ --- forced air --- Honeywell valve (on/off switch) Burners try to light on 1'st attempt, lights for couple seconds then out on2'nd attempt. Brand new furnace. Looked in installation manual -- says stuff...


View more questions Search