Too much on a 200 amp panel?
Well this is the first time I've been here so thanks for your time. My question is about a 200 amp
Panel, I want to add a 220 for a hot tub but I am worried to ad this it would trip the main breaker. Here are the breakers that are now in the panel. Every spot in this panel is taken up so I would have to add a few more double breakers. Let me know if it is any good for me to try this out or if I would be setting up my main to flip. Thank you
40-------------------------------------15
40- dryer ------------------------------15- vac
40--------------------------------------60
40-oven---------------------------------60- furnace
40------------------------------------- 60
40-hot water ---------------------------60- furnacd
15--------------------------------------40
15--------------------------------------40- burner on oven top
20--------------------------------------15
20--------------------------------------15
20- this is a double 20 breaker----------20- this is also a double 20
40-------------------------------------20
40-ac----------------------------------15
40--------------------------------------15
40ac-----------------------------------15
|
|
 |
Uber Member
|
|
Oct 22, 2007, 03:30 PM
|
|
Would need Square footage of living area, Plus Name plate ratings.
Furnass and AC's won't be used at the same time.
Dryer on a 40 amp is a little odd, would check nameplate, Most are 30 Amp.
I would Check the Water Heater name plate(Watts)40 Amps??
InstaHeats can Draw 40 and way beyond. Most Regular? Are 20-30 Amps?
|
|
 |
New Member
|
|
Oct 24, 2007, 06:11 PM
|
|
OK I will get this info to you by tomorrow thanks again for your time
|
|
 |
New Member
|
|
Oct 28, 2007, 02:55 PM
|
|
OK here is what I have
Kw----5.6 oven
--------11 cook top
-------9.6 furnace
-------9.6 furnace
-------4.4 ac
-------7.2 ac
I could not figure out the dryer I called the manufacture and asked them and they didn't know what the kw was so I figure its around 4.4 or 5
Also on the w/h it says total kw is 4.5 but it also says on the w/h that it has a upper and lower that both have 4.5 kw so I figured id tell you.
The jacuzzi that were installing is 5.5 kw
Total sq is 3800
Anything else let me know
|
|
 |
Junior Member
|
|
Oct 28, 2007, 07:48 PM
|
|
Need to know which are 2 pole (220-240V) for calculating load. All of 'em?
|
|
 |
Uber Member
|
|
Oct 29, 2007, 02:50 AM
|
|
Gentlemen, there is enough information given to calculate the service load, hint, use Optional Heat larger than AC method .
|
|
 |
New Member
|
|
Oct 29, 2007, 06:39 AM
|
|
Yeah all of them are two pole I'm going to install the wire today hopefully its enough load.
|
|
 |
Uber Member
|
|
Oct 29, 2007, 03:47 PM
|
|
I guess no one else wants to answer.
I arrive at a total connected load of 137 amps, without the hot tub.
The service should not be loaded more than 80%, leaving 160 available amps.
Assuming a 40 amp load (9600 watt) from the hot tub, adds up to 177 amps.
Depending on the lifestyle of the home, and how many appliances and heat are used, you may have problems.
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
200 amp panel feeding a 100 amp panel roughly 130' away
[ 7 Answers ]
Hi all,
We are building a apartment above the garage,my question is what size wire do I need to run from the 200 amp panel to the 100 amp panel roughly 130' away?
I want to use aluminum wire as I think copper would be to costly.
Thanks for your help in advance,
Dude
:eek:
200 AMP Service panel to 200Amp Sub Panel
[ 1 Answers ]
I getting new 200Amp service to surface mount service panel. I want to run 2oo cable to bring it sub panel in my Garage which is approx 120Ft Run through ceiling.
2 Questions
1. Is there any ristriction on running a 200AMP inside house to garage ?
2. I got a dirt cheap subpanel that has...
100 Amp Subpanel from 200 Amp main panel
[ 2 Answers ]
I want to install a subpanel to be used to supply branch circuits to a new kitchen, laundry, garage, and some additional lighting and receptacles. The 200 amp main panel is about 50 ft away but because of the obstructions, we'll need about 85 feet of cable to connect the 100 amp subpanel. Since...
Using 100 amp panel on 200 amp service
[ 5 Answers ]
I am building new camp at a site that already has 200 amp service. My power requirements are small and 100 amp will be more than sufficient. Is there any reason I cannot hookup a 100 amp panel to the 200 amp meter socket? Not sure is code allows this. I want to use a small 100 amp panel vs the...
200 Amp Service Panel with 60 Amp Main Breakers
[ 26 Answers ]
I was told when we purchased our house that it had 200 Amp service which it appears to be; however, the top of each bus bars only has 60 Amp breakers for the Main shut offs. Is this normal? Each bus bar is connected to a hot wire (one red and one black) and then the two 60 amp breakers are...
View more questions
Search
|