    15 amp switch and plugs on 20 amp service
    Hi
    The electrical contractor on our house put in all 20 amp circuits which I like but while replacing a switch in one noticed he put in all 15 amp rated plugs and switches which I don't like. Is this OK and according to code , I live in SC.
    Thanks
    Mike
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Sep 9, 2007, 08:30 AM
    15 amp receptacles on a 20 amp circuit is fine and allowed the national code. The nature of the blasde configurtaion of a 15 receptacle will onlu allow a 15 amp device to be plugged in, thereby limiting the amount of curent to 15 amps on the 20 amp circuit.

    The issue is with the switches. A 20 amp load can easily be applied to the circuit and not have any limiting means. So a 15 amp switch may have more load on it that it can safely handle.

    What does the local inspector say about this? Has a Certificate of Occupancy Inspection been done yet?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Running two 100 amp main panels from a 200 amp service [ 27 Answers ]

Greetings! I live in a rural country area. The electric company will be installing a pole, meter, and 200amp service with disconnect at pole. (It will require 50 foot run of service cable from pole to main load center in mobile). Currently the double wide has a General Electric 100amp Main...

400 amp service, 2 200 amp panels, 320 amp meter socket [ 10 Answers ]

Hi, this is my first post here, but I have been reading a lot and have already learned a bunch. I want to thank TK already and hope you reply to this. I am in the process of designing my electrical system for my new home. I have some electrical experience, but am by no means a pro. I am...

400 amp service with 2-200 amp panels & 320 amp socket [ 6 Answers ]

Hi TK. I am running 400 amp service into my new contruction home. The electric compnay is running a single 400 amp line to the meter. I have to split it to the two panels at that point. You had told me once before that I need a 320 amp meter socket and then run 2-200 amp lines to the separate...

200 Amp Service Panel with 60 Amp Main Breakers [ 26 Answers ]

I was told when we purchased our house that it had 200 Amp service which it appears to be; however, the top of each bus bars only has 60 Amp breakers for the Main shut offs. Is this normal? Each bus bar is connected to a hot wire (one red and one black) and then the two 60 amp breakers are...

100 amp service vs. 200 amp service [ 5 Answers ]

The house I just bought was built in 1952. It's a 3 bedroom, 1 bathroom with the standard screw in fuses (total amps unknown). Presently I'm doing a remodel. Adding a third bedroom & extra bathroom, washer & dryer, dishwasher, newer & larger refrigerator, bigger microwwave, probably 3 window air...


View more questions Search